Exclamation Lenox G40DF Furnace

Hello,

My home inspector has reffered me to this site.

I recently purchased a home and have noticed potential furnace problems after the move in. When the temperature is set at for 70 degress, the furnace seems to run for about 8 minutes, then shuts down for 2 minutes, and then restarts for 8 minutes. If I decrease the temperature the amount of time the furnace is off increases and the time the furnace is on decreases for during the cycle. It seems to be running fine, but the shut down and start up does not appear to be normal. I can imagine it being major since the furnace is about 4 years old. It is a Lenox G40DF.

Any information you can provide would be much appreciated, especially during this cold time of year!
Reply With Quote
  #2  
Old 2/15/07, 9:47 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Lenox G40DF Furnace

Albert.

Make sure you check your air filter first.

It sounds like the furnace may be short cycling.
Reply With Quote
  #3  
Old 2/15/07, 10:55 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Lenox G40DF Furnace

Albert,
There are several possible causes for the short cycling you describe. The unit could be oversized, there could be a problem with the controller or the high limit switch may be sensing high heat and shutting the unit down.
As mentioned, check your filter first. If it is clean, then you should call for service. Also, make sure your returns are not obstructed.

Anatol
Reply With Quote
  #4  
Old 2/16/07, 6:15 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,926
Default Re: Lenox G40DF Furnace

If you have a thermostat with a heat anticipator it may not be set properly or damaged.
This would be the first place to start as the cycling changes when you change the thermostat setting.
There will not be changes in cycle time if it were one of the other many possibilities.
Gas furnaces are quite complex and it is unlikely that you will be able to make the evaluation yourself.
Reply With Quote
  #5  
Old 2/18/07, 2:25 PM
Albert Detorre Albert Detorre is offline
New User
 
Join Date: Feb 2007
Posts: 3
Please Note: Albert Detorre is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thumbs up Re: Lenox G40DF Furnace

Thank you for all of your responses, it has been very helpful!

I've checked the filters and it looks like the previous owner did not change them for years (a single women used to live here)....

After changing the filters, I've noticed an improvement in the cycling. Also, I found the heat anticipator located under the thermostat. The thermostat is not digital and is an older model from "White-Rodgers". I've adjusted the heat anticipator to the 'longer' setting which has increased the cycles. So far, it seems to be ok. If there are any other problems, I may try a new thermostat.
Reply With Quote
  #6  
Old 2/19/07, 4:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Lenox G40DF Furnace

Quote:
Originally Posted by Albert Detorre
Thank you for all of your responses, it has been very helpful!

I've checked the filters and it looks like the previous owner did not change them for years (a single women used to live here)....

After changing the filters, I've noticed an improvement in the cycling. Also, I found the heat anticipator located under the thermostat. The thermostat is not digital and is an older model from "White-Rodgers". I've adjusted the heat anticipator to the 'longer' setting which has increased the cycles. So far, it seems to be ok. If there are any other problems, I may try a new thermostat.
Albert: if what you stated is true about the filter not being changed you can rest assured that the furnace A-Coil is also matted over and you are severely restricting air flow which can also cause the furnace to cycle. I would caution you about adjusting the heat anticipator as this anticipator has a graduated scale setting that is suppose to be set to match the amp draw of the furnace control gas valve.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Problem Comments Welcome rfrost Inspecting HVAC Systems 28 10/21/07 6:26 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph Inspecting HVAC Systems 2 6/6/07 2:56 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer Inspecting HVAC Systems 19 4/9/07 8:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
Pvc For Furnace Venting? dtaylor Inspecting HVAC Systems 8 8/10/06 11:11 PM


All times are GMT -4. The time now is 11:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts