  #1  
Old 4/8/07, 12:24 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 188
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Level condensers

I see quite a few home inspection reports where the inspector calls out the condenser isn't level (I'm referring to split systems). I would think you would want it to be sloping a bit toward the drain. Is there I reason that would require it to be exactly level?
Reply With Quote
  #2  
Old 4/8/07, 12:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Level condensers

A condensing unit normally doesn't have a drain.

Hermetic compressors in condensing units are "splash oiled" and having the unit level is important to the proper functionality of the splash oiler pickup.
Reply With Quote
  #3  
Old 4/8/07, 12:31 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 188
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Re: Level condensers

Marc, what about a heat pump?
Reply With Quote
  #4  
Old 4/8/07, 12:32 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hellertown, Pa
Posts: 1,852
Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information Thomas H. Dietrich is very trusted source of information
Send a message via Yahoo to tdietrich1
Default Re: Level condensers

Quote:
Originally Posted by gheller
Marc, what about a heat pump?
Same thing, just the direction of heat flow is reversed.

As for level, yes, Marc was correct. A compressor's major root cause of premature failure is lack of lubrication. This comes from two sources. 1. A leak in the system, carrying away oils/cooling of oils. 2. Unleveled condensers, causing low areas in the sump.

tom



Hellertown, Pa 18055 NACHI ID: NACHI06101299
Northampton County Home Inspector, Monroe County Home Inspector


Help Me Save Money For My Kids' Education.

"Might as well stick a fork in it, the real estate industry is done for now."
- Tom Dietrich November 4th 2008

Ayers: Obama was 'family friend'
Reply With Quote
  #5  
Old 4/8/07, 12:44 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Level condensers

Quote:
Originally Posted by gheller
I see quite a few home inspection reports where the inspector calls out the condenser isn't level (I'm referring to split systems). I would think you would want it to be sloping a bit toward the drain. Is there I reason that would require it to be exactly level?
Gary;

There generally are more than one drain hole in the bottom of the condensing unit. I do not run around with a level in my pocket and have never called out a unit as being unlevel not to say that I wouldn't if it was grossly unlevel. I see some units that slant with the conture of the landscape slightly but would consider this as cosmetically un-pleasing has nothing to do with the proper operation of the unit. I don't nit-pick



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 4/8/07, 1:04 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 188
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Re: Level condensers

In our climate we get quite a few winter days when a heat pump will ice up and then have to go through a defrost cycle. On the older houses where the unit is on the roof I often see water dripping off the roof due to plugged drains.

I agree that it should not be grossly out of level for a variety of reasons.
Reply With Quote
  #7  
Old 4/8/07, 1:08 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 3,174
Michael R. Boyett .
Default Re: Level condensers

I've only called out one or two grossly out of level condensing units in the last couple of years. I use an "approximately 10°" out of level rule:
AC Level.JPG
Reply With Quote
  #8  
Old 4/8/07, 1:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Level condensers

Some of the packaged outdoor air conditioning units (aka - trailer unit) have the condensate drain run in such a way that it undermines and washes out the unit's pad. In time, the unit will start to sink right where the condensate line drips off if the line isn't run away from the pad a bit.
Reply With Quote
  #9  
Old 4/8/07, 1:10 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Level condensers

Quote:
Originally Posted by tdietrich1
Same thing, just the direction of heat flow is reversed.

As for level, yes, Marc was correct. A compressor's major root cause of premature failure is lack of lubrication. This comes from two sources. 1. A leak in the system, carrying away oils/cooling of oils. 2. Unleveled condensers, causing low areas in the sump.

tom
Compressors are cooled by the temperature of the returning freon thru the windings thus keeping the oil at a cooler temp. After having changed out hundreds and hundreds of compressors in my opinion the #1 cause of failure would have to be a dirty condenser not oil failure. The larger% of freon leaks do not have the volume of oil with the freon that would deplete the compressor of oil and cause failure. And I say again you would have to have the unit grossly unlevel to create a lack of lubrication. A Lack of lubrication is most often a result of a washout simply stated liquid freon returning to the compressor and washing the oil from its sump.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #10  
Old 4/8/07, 1:19 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Level condensers

Quote:
Originally Posted by gheller
In our climate we get quite a few winter days when a heat pump will ice up and then have to go through a defrost cycle. On the older houses where the unit is on the roof I often see water dripping off the roof due to plugged drains.

I agree that it should not be grossly out of level for a variety of reasons.
Gary:

Most heat pumps have a preforated bottom that allows for drainage and any installing contractor worth their salt will elevate a heat pump from a flatsurface to allow for proper drainage as this water if allowed to stand in the bottom will freeze every time after a defrost and over time will coat and block the condenser of air flow.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #11  
Old 4/8/07, 2:27 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,832
David A. Andersen .
Default Re: Level condensers

I second Charlie's posts.

Heat Pumps require proper drainage when they defrost. This is more about "away from the unit" rather than level.

Oil problems occur more from improperly installed line sets with big dips in the run that cause the oil to pool out under low ambient conditions where there is low suction pressures/differential.

That 10 degree picture; I'd be jumping out of my skin over the drainage / foundation issues, rather than an unlevel condenser. If you fix the drainage, the condenser would be leveled.
Reply With Quote
  #12  
Old 4/8/07, 10:41 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,331
William E. Siegel is often very helpful William E. Siegel is often very helpful
Default Re: Level condensers

Compressors which are badly out of level may fail to function properly and need adjustment. Tipping and moving compressors can also cause can cause leaks in refrigerant lines.
Reply With Quote
  #13  
Old 4/9/07, 3:58 AM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
dchew hasn't had much positive or negative feedback
Default Re: Level condensers

A non-level AC condensor will experience more wear and tear on its bearings. At what point does it become a real factor is hard to determine.

I always check to see if the condensor is attached to the pad. If it's not and the condensor is not level, the condensor can start to "walk" away from the pad and start to put stress on the hoses, etc.
Reply With Quote
  #14  
Old 4/9/07, 4:42 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,858
Russel Ray .
Default Re: Level condensers

Quote:
Originally Posted by gheller
I see quite a few home inspection reports where the inspector calls out the condenser isn't level (I'm referring to split systems). I would think you would want it to be sloping a bit toward the drain. Is there I reason that would require it to be exactly level?
Definitely: The manufacturer installation instructions state that the unit must be level. If it's not, damage can result. That's good enough for me.



  • Need a positive networking site? Click here to join Active Rain, a networking community of 125,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #15  
Old 4/9/07, 11:34 AM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,370
Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information
Default Re: Level condensers

The reason that I've called out unlevel units was because of what I assumed could be undue stress on the fan blade bearing. A defensible idea?



InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI

Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
2 questions staylor5 Electrical 9 3/23/07 11:40 PM
Torpedo Level thejnicki Structural 11 2/21/07 11:57 PM
Gas Logs........ pabernathy HVAC 11 12/25/06 9:58 PM
Condenser unit not level loconnor HVAC 5 6/5/06 2:36 PM
chimney crack rcantrell Exterior 7 4/4/06 8:10 PM


All times are GMT -4. The time now is 12:39 AM.