I see quite a few home inspection reports where the inspector calls out the condenser isn't level (I'm referring to split systems). I would think you would want it to be sloping a bit toward the drain. Is there I reason that would require it to be exactly level?
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
A condensing unit normally doesn't have a drain.
Hermetic compressors in condensing units are "splash oiled" and having the unit level is important to the proper functionality of the splash oiler pickup. |
|
#3
|
||||
|
||||
|
Marc, what about a heat pump?
|
|
#4
|
||||
|
||||
|
Quote:
As for level, yes, Marc was correct. A compressor's major root cause of premature failure is lack of lubrication. This comes from two sources. 1. A leak in the system, carrying away oils/cooling of oils. 2. Unleveled condensers, causing low areas in the sump. tom Hellertown, Pa 18055 NACHI ID: NACHI06101299 Northampton County Home Inspector, Monroe County Home Inspector Help Me Save Money For My Kids' Education. "Might as well stick a fork in it, the real estate industry is done for now." - Tom Dietrich November 4th 2008 Ayers: Obama was 'family friend' |
|
#5
|
||||
|
||||
|
Quote:
There generally are more than one drain hole in the bottom of the condensing unit. I do not run around with a level in my pocket and have never called out a unit as being unlevel not to say that I wouldn't if it was grossly unlevel. I see some units that slant with the conture of the landscape slightly but would consider this as cosmetically un-pleasing has nothing to do with the proper operation of the unit. I don't nit-pick Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#6
|
||||
|
||||
|
In our climate we get quite a few winter days when a heat pump will ice up and then have to go through a defrost cycle. On the older houses where the unit is on the roof I often see water dripping off the roof due to plugged drains.
I agree that it should not be grossly out of level for a variety of reasons. |
|
#7
|
||||
|
||||
|
I've only called out one or two grossly out of level condensing units in the last couple of years. I use an "approximately 10°" out of level rule:
AC Level.JPG |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Some of the packaged outdoor air conditioning units (aka - trailer unit) have the condensate drain run in such a way that it undermines and washes out the unit's pad. In time, the unit will start to sink right where the condensate line drips off if the line isn't run away from the pad a bit.
|
|
#9
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#10
|
||||
|
||||
|
Quote:
Most heat pumps have a preforated bottom that allows for drainage and any installing contractor worth their salt will elevate a heat pump from a flatsurface to allow for proper drainage as this water if allowed to stand in the bottom will freeze every time after a defrost and over time will coat and block the condenser of air flow. Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#11
|
||||
|
||||
|
I second Charlie's posts.
Heat Pumps require proper drainage when they defrost. This is more about "away from the unit" rather than level. Oil problems occur more from improperly installed line sets with big dips in the run that cause the oil to pool out under low ambient conditions where there is low suction pressures/differential. That 10 degree picture; I'd be jumping out of my skin over the drainage / foundation issues, rather than an unlevel condenser. If you fix the drainage, the condenser would be leveled. |
|
#12
|
|||
|
|||
|
Compressors which are badly out of level may fail to function properly and need adjustment. Tipping and moving compressors can also cause can cause leaks in refrigerant lines.
|
|
#13
|
|||
|
|||
|
A non-level AC condensor will experience more wear and tear on its bearings. At what point does it become a real factor is hard to determine.
I always check to see if the condensor is attached to the pad. If it's not and the condensor is not level, the condensor can start to "walk" away from the pad and start to put stress on the hoses, etc. |
|
#14
|
||||
|
||||
|
Quote:
|
|
#15
|
|||
|
|||
|
The reason that I've called out unlevel units was because of what I assumed could be undue stress on the fan blade bearing. A defensible idea?
InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI Author of Manual For a Happy Home & Inspect & Protect |
![]() |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 2 questions | staylor5 | Electrical | 9 | 3/23/07 11:40 PM |
| Torpedo Level | thejnicki | Structural | 11 | 2/21/07 11:57 PM |
| Gas Logs........ | pabernathy | HVAC | 11 | 12/25/06 9:58 PM |
| Condenser unit not level | loconnor | HVAC | 5 | 6/5/06 2:36 PM |
| chimney crack | rcantrell | Exterior | 7 | 4/4/06 8:10 PM |