Default A loaded question # 2

Ok lets do another simple question how many test a heat pump in the normal heat mode with an outside ambient at 90 degrees yes or no is sufficient



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/3/11, 4:10 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: A loaded question # 2

Well, it depends Red Top, I've never run across a heat pump here.
Reply With Quote
  #3  
Old 10/3/11, 4:16 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A loaded question # 2

Quote:
Originally Posted by ldapkus1 View Post
Well, it depends Red Top, I've never run across a heat pump here.
Well you should get out more and do a few inspections prolly would see one



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 10/3/11, 4:34 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: A loaded question # 2

Quote:
Originally Posted by cbottger View Post
Ok lets do another simple question how many test a heat pump in the normal heat mode with an outside ambient at 90 degrees yes or no is sufficient
I will answer this way, and it applies to all appliances in a home...

"Can the occupant of a home operate an appliance, using normal controls and at any given condition, whether proper or not?" ???

Or...

"Is there a sign on the thermostat with instructions to not turn on the heat when too hot, or to not turn on the A/C when too cool" ???
Reply With Quote
  #5  
Old 10/3/11, 4:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: A loaded question # 2

Should I?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 10/3/11, 4:37 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: A loaded question # 2

Quote:
Originally Posted by ccurrins View Post
Should I?
Yes!
Reply With Quote
  #7  
Old 10/3/11, 4:38 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: A loaded question # 2

Quote:
Originally Posted by cbottger View Post
Well you should get out more and do a few inspections prolly would see one
I'm done for the day, just came here to help out and working on my Aerial IR Website
Reply With Quote
  #8  
Old 10/3/11, 5:00 PM
Ken Ruppert Ken Ruppert is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Merritt Island, FL
Posts: 79
Default Re: A loaded question # 2

No I don't. Because it a heat pump and it 90 outside, I won't get an accurate reading so I tell them I did not test it in the heat mode.




Ken Ruppert
NACHI # 08081129
Florida Lic # HI162

www.happyhomeinspection.com
Reply With Quote
  #9  
Old 10/3/11, 5:45 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A loaded question # 2

Quote:
Originally Posted by ldapkus1 View Post
I'm done for the day, just came here to help out and working on my Aerial IR Website
Looking good Bud yous need to go up and take a aerial shot for your Web page or borrow one of mine until yous get one of your own



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 10/3/11, 5:47 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: A loaded question # 2

Quote:
Originally Posted by cbottger View Post
Looking good Bud yous need to go up and take a aerial shot for your Web page or borrow one of mine until yous get one of your own
I'm going up soon, maybe this week.
Reply With Quote
  #11  
Old 10/3/11, 6:02 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A loaded question # 2

Quote:
Originally Posted by kruppert View Post
No I don't. Because it a heat pump and it 90 outside, I won't get an accurate reading so I tell them I did not test it in the heat mode.
I can appreciate you saying it would not be an accurate reading because it would not but you also don't know if the reversing valve works, is that the only reason you do not test



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 10/3/11, 7:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A loaded question # 2

Ok no one is doing much talking hiding in the bushes I guess so here is the reason I made these two loaded questions.

There is no difference in operating the A/C unit with a indoor ambient of 90 degrees and operating a heat pump in the heat mode with an outdoor ambient of 90 degrees you get the same results. So when someone tells me they don't operate a heat pump in the summer time in the heat mode even for just a test they basically don't understand the refrigerant cycle



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 10/3/11, 7:22 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: A loaded question # 2

Quote:
Originally Posted by jjonas View Post
Yes!
Ya got it bubba



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/3/11, 8:06 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,926
Default Re: A loaded question # 2

Is there enough pressure differential for the reversing valve to operate in those conditions?!

I'd guess so.

Now someone mentioned tripping the head pressure safety and you'd have to figure out hot to re-set it!

"Push the big red button"!

If it don't got one, it's auto-reset...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A loaded question cbottger Inspecting HVAC Systems 35 10/6/11 9:59 AM
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 7:43 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM


All times are GMT -4. The time now is 11:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts