I am running across a lot of new homes that have the fresh air make up vent terminating in the attic space. While at first glance I would agree that it is bring fresh air into the HVAC system. The question is. Is this correctly installed?
Seems to me to be a real bad idea to bring 120+ degree fresh air into the house during colling season as the AC needs to now cool all that hot air.
I cannot seem to find an answer to this question so I though I would post it here and see what all you experts think.
Attached Thumbnails
make-up-air-ducting-question-100_5165.jpg  
Reply With Quote
  #2  
Old 1/29/06, 1:34 PM
ekartal5 ekartal5 is offline
Active Poster
 
Join Date: Dec 2005
Location: Schaumburg, Il
Posts: 273
Please Note: ekartal5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Make up air ducting question

Hi John,
A well ventilated attic can be used as a source of combustion air. Check 2003 IRC section R806 for more detail. I don't have the book with me, I just know it's in there.

Erol Kartal
ProInspect
Reply With Quote
  #3  
Old 1/30/06, 12:50 AM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Make up air ducting question

i'd question the lack of filter. plus any little tree rat could just jump in and cause all kinds of havok.
Reply With Quote
  #4  
Old 1/30/06, 4:39 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Make up air ducting question

Would it be any different from the furnace sitting in the utility closet with a screened ceiling to the attic?

Yes, I would put a screen over it, though.
Reply With Quote
  #5  
Old 1/30/06, 6:36 PM
rarmstrong1 rarmstrong1 is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Sandy Springs, GA
Posts: 33
Default Re: Make up air ducting question

When combustion air is taken from an attic the duct must extend a min. of 6 inches into the attic above the ceiling joist and insulation and the attic must be well ventilated. NO SCREENS to be used on the duct ends. IRC M 1703.3
Reply With Quote
  #6  
Old 1/30/06, 6:47 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Make up air ducting question

It's a good thing we don't use the IRC here. I'm putting a screen on mine.
Reply With Quote
  #7  
Old 1/30/06, 6:55 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 270
Default Re: Make up air ducting question

I don't think John is referring to combustion air in this case. I think he is referring to a system that requires a certain amount of fresh air to be blended with the conditioned air as part of an air exchange.

tg
Reply With Quote
  #8  
Old 1/30/06, 7:00 PM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: Make up air ducting question

That was my take as well. I can't imagine using flex duct for combustion air. That is if it was connected to a 90+ furnace.

Last edited by JLilly; 1/30/06 at 7:26 PM..
Reply With Quote
  #9  
Old 1/30/06, 7:13 PM
rarmstrong1 rarmstrong1 is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Sandy Springs, GA
Posts: 33
Default Re: Make up air ducting question

The other end of the duct should terminate in the room with the furnace within 12 inches of the ceiling. I could not find a reason for no screen. The CODE is not too hot on why's. If the duct extends 6" into the attic and less than 12" through the ceiling it should remain clear at all times. A screen could get blocked with insulation and prevent flow of required air.
Reply With Quote
  #10  
Old 1/30/06, 10:50 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Make up air ducting question

true, but with no protection at all, it could get clogged with haycorns, pine cones, wallnuts, chestnets, and it will drive them nuts. dead squrells swell up when stuck in a slick sheet metal tube that there little claws can't climb. i'd screen it and make it a point to check and clean everytime they replace the fresh air filter. yeah they'll likely forget both of those, but i'd pick the lesser of 2 evils.
Reply With Quote
  #11  
Old 2/3/06, 7:38 AM
John M. Nelson John M. Nelson is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Manassas, VA
Posts: 3
Default Re: Make up air ducting question

The end of the flex duct terminates into the return side of the system. It connects directly to the return duct. This is not combustion air supply. It's fresh air being added to the house. My problem with it is the extra work the AC system will have to do to cool all that hot air in the summenr time.
I agree that at the very least a screen needs to be added.
Reply With Quote
  #12  
Old 2/5/06, 1:08 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Make up air ducting question, WE LIVE IN A LITIGIOUS SOCIETY!

Hi John & Jay!

Here is the information that you were looking for. I ask that you use caution in your inspections.

As a "generalist" YOU ARE NOT PERFORMING A CODE INSPECTION.

Only a Code Compliance Inspector can conduct a “Code Compliant Inspection.”

If you start “quoting code” to a client during the physical inspection, and especially in your written report this is an implication that the ENTIRE HVAC system to include duct works, size, type, placement, spacing, support & fastening, vents, the size and placement of the vents, as well as the condenser, compressor, coils, etc. not only meet code but are the correct size to provide sufficient cooling and or heating for the ENTIRE house.


WE LIVE IN A LITIGIOUS SOCIETY!


Even the slightest mistake could lead to a lawsuit, and could lead you to “upgrading / replacing” a unit that is too “small” for the home in question.


Once again please be careful about quoting code.

PS:
IN ORDER TO PROTECT YOURSELF, Just state that you recommend that a HVAC trained and certified specialist should come and look at the open-ended duct. He / she will see that it should terminate in a "vent".
This way you have identified a situation that you as a “generalist” feel should be brought to the attention of a “HVAC trained & certified specialist”.



Respectfully, Frank Carrio
Certified Inspector & Consultant
President, New Hampshire Chapter
The National Association of Certified Home Inspectors {NACHI}

CONTACT INFORMATION:
{603} 483-5282

Frank Carrio
P.O. Box 188
Chester, New Hampshire 03036
www.americascertifiedinspectioncompanyllc.com


MEMBERSHIPS, AFFILIATIONS, AND CERTIFICATIONS
· CERTIFIED By: The Examination Board of Professional Home Inspectors
{EBPHI # FC-660614}

CODE COMPLIANCE INSPECTOR: {#0502}
United States Government, The Department of Veterans Affairs

· CERTIFIED MEMBER: {ICC-5159435}
International Code Council

CERTIFIED INSPECTOR {NACHI-04010246}
The National Association of Certified Home Inspectors {NACHI}

PRESIDENT, NEW HAMPSHIRE CHAPTER

The National Association of Certified Home Inspectors


SUSTAINING MEMBER: {BOCA-101251}
Building Official Code Administrators {BOCA / ICC}

CERTIFIED MEMBER: From 1994-2004
{ASTM / ISO-000131040}
American Standards & Testing Materials Society {ASTM / ISO}

COMMITTEE MEMBER: From 1994-2004
{ASTM / ISO-000131040}
ASTM F:06 & D:07 {ASTM / ISO}

CERTIFIED MOLD & RADON INSPECTOR
ESA, PRO-LAB, ACCU-STAR

E-Mail:FMCarriosr@aol.com

CELL: {603} 498-2753,
Phone: {603} 483-5282

Fax: {603} 483-5280


R806
ROOF VENTILATION
806.1 Ventilation required.
Enclosed attics and enclosed rafter spaces formed where ceilings are applied directly to the underside of roof rafters shall have cross ventilation for each separate space by ventilating openings protected against the entrance of rain or snow. Ventilating openings shall be provided with corrosion-resistant wire mesh, with 1/8 inch (3.2 mm) minimum to 1/4 inch (6.4 mm) maximum openings.
806.2 Minimum area.
The total net free ventilating area shall not be less than 1 to 150 of the area of the space ventilated except that the total area is permitted to be reduced to 1 to 300, provided at least 50 percent and not more than 80 percent of the required ventilating area is provided by ventilators located in the upper portion of the space to be ventilated at least 3 feet (914 mm) above eave or cornice vents with the balance of the required ventilation provided by eave or cornice vents. As an alternative, the net free cross-ventilation area may be reduced to 1 to 300 when a vapor barrier having a transmission rate not exceeding 1 perm (57.4 mg/s · m2Pa) is installed on the warm side of the ceiling.
806.3 Vent clearance.
Where eave or cornice vents are installed, insulation shall not block the free flow of air. A minimum of a 1-inch (25.4 mm) space shall be provided between the insulation and the roof sheathing at the location of the vent.
Reply With Quote
  #13  
Old 2/5/06, 10:29 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Make up air ducting question

Hi Frank, good to hear back from you the other day. however, if you look at the pic in the beginning of the post you'll see that this thread is in concern of a screen on the vent duct to the furnace of this house which either begins or terminates in the attic. i don't know as if any mention of the attic venting was in question at all. but hay, thanx for the info. it's alway good to be firmiliar with the code. i personaly never quote code either in my report or communicating with my client. at least if we know the code we can translate that into the ammo we need to call out those deficiencies without actualy mentioning that it is or isn't code. thanx again Frank, and i'll be trying to make it up to Concord on the 14th at 10:00.
Reply With Quote
  #14  
Old 2/5/06, 11:24 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,098
Default Re: Make up air ducting question

Must be a northern thing. I've never seen make-up air on residential a/c in this area before. I've seen plenty on commercial though, usually adjustable from 15% to 40% or so and either manual or automatic and always pulling from the exterior.
Reply With Quote
  #15  
Old 2/6/06, 7:57 PM
jrupert jrupert is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Grove City, OH
Posts: 47
Default Re: Make up air ducting question

If this is connecting to the return side of the system it must be a house make up air duct, it can not by code take the air from the attic it must be from out side unless the local code allows different.

No screens are allowed for make up air or combustion air due to clogging, this does not present an issue that is dangerous for the make up air but it can be very dangerous for combustion air, if blocked the conditions for carbon monoxide then exists.

Here in Ohio make up air is to off set the tighter homes, normally a single 4 inch round pipe is called for, but then its really up to the local code and it can be flex duct. Combustion air is always metal duct by code

An additional note on screens, combustion air pipe size is based on what’s called FREE SPACE or FREE AREA which is the sq inches of unrestricted pipe, a 4 inch round pipe for example has the free space of 13 square inches, when a grill is added it will effectively reduce the free area so it must be taken into account by the designer or a dangerous situation may occur from the reduced free area caused by the grill or screen.

I agree, use caution about code, and always refer to a qualified professional HVAC company



John Rupert
Accurate Property Inspections
Solitaire Heating & Cooling
CSG Training (HVAC Training & Consulting)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Foundation w/return air ducting through slab? lfoster Structural 5 7/17/06 11:40 AM
Rule of Thumb A/C sizing question from Practice Exam gliebig HVAC 9 5/25/06 2:38 AM
Answer to a common question about GFCI's jtedesco1 Electrical 4 1/12/06 10:29 PM


All times are GMT -4. The time now is 4:57 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts