Re: Make up air ducting question
Quote:
|
Originally Posted by rarmstrong1
The other end of the duct should terminate in the room with the furnace within 12 inches of the ceiling. I could not find a reason for no screen. The CODE is not too hot on why's. If the duct extends 6" into the attic and less than 12" through the ceiling it should remain clear at all times. A screen could get blocked with insulation and prevent flow of required air.
|
I know this is what the code says but all of the old diagrams for static combustion air that I have seen requires one high and one low. If you have only one high and the mechanical room/closet is hot and the attic is cold there is going to have to be one huge negative pressure developed in the room to reverse the flow of air that is going into the attic.