Default Metalized Flexible Vent for Bathroom

Gentlemen,

I wonder if you could help me out with this one. I have been advised that flexible plastic vent ducting is not allowed from bathroom vents. It could allow a fire to escape into the attic. Please see the attached photos.

In this case, metal ducting was used almost to the wall, but metalized flex duct, the slinky kind, was used between the solid ductwork and the wall, as well as from the fan unit to the solid duct work. In addition they used aluminum tape to seal all the joints in the solid ducting, but used "Duct Tape" to finish the connections.

What say you?
Attached Thumbnails
metalized-flexible-vent-bathroom-100_2969.jpg   metalized-flexible-vent-bathroom-100_2970.jpg   metalized-flexible-vent-bathroom-100_2971.jpg   metalized-flexible-vent-bathroom-100_2972.jpg  
Reply With Quote
  #2  
Old 9/21/07, 8:54 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Metalized Flexible Vent for Bathroom

My response would be depends on your local AHJ mine allows flex to be used.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 9/25/07, 10:06 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Metalized Flexible Vent for Bathroom

Standard in my area as well. Basically uninsulated flexduct liner. Plastic or mylar type flexduct liners are not acceptable in our area.
Also, gray "fabric" duct tape is not acceptable, as used in your pic. Only smacna "foil" tape or rated Mastic is allowed.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 4 10/12/07 6:38 PM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM


All times are GMT -4. The time now is 12:43 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts