Default mid-level efficiency?

It had a sealed combustion chamber but a metal vent. Is this an acceptable installation? I called clearance to combustibles.
Attached Thumbnails
mid-level-efficiency-boiler-1.jpg   mid-level-efficiency-boiler-2.jpg   mid-level-efficiency-boiler-3.jpg  




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/15/10, 7:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: mid-level efficiency?

Quote:
Originally Posted by kshepard View Post
It had a sealed combustion chamber but a metal vent. Is this an acceptable installation? I called clearance to combustibles.
It may be OK Kenton.

See page 6

http://www.slantfin.com/documents/305.pdf (PDF)



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 5/15/10, 7:49 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: mid-level efficiency?

Too freaky for me with that manifold contraption.
They just love tempting fate that it will not leak into the air intake.
Reminds me of those concentric vents.

Anyway the first thing I noticed was the slope on the exhaust.
Does not look like 1/4" per foot to me.
Reply With Quote
  #4  
Old 5/15/10, 9:20 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: mid-level efficiency?

I don't like the negative slope of the combustion air intake nor the foil type dryer's vent pipe.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #5  
Old 5/15/10, 9:25 PM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: mid-level efficiency?

It looks like they have the connections reversed according to the pdf drawings that Michael provided. The exhaust should be in the center not the outside.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #6  
Old 5/15/10, 10:25 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: mid-level efficiency?

Quote:
Originally Posted by dhays View Post
It looks like they have the connections reversed according to the pdf drawings that Michael provided. The exhaust should be in the center not the outside.
I think you are right. Direct vent type usually sends the exhaust through the center and combustion air in the outer ring.

Most of the concentric direct vent exhausts, I believe, are zero clearance and UL listed. That's a lot of stainless steel vent pipe they have there $$$.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #7  
Old 5/15/10, 10:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: mid-level efficiency?

The exhaust does go through the middle.
It is the schedule 40.
Reply With Quote
  #8  
Old 5/16/10, 1:41 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: mid-level efficiency?

Also... there's plastic pipe meeting that manifold fairly close to where the metal exhaust vent meets it. It looks like heat transfer might melt the PVC.
This vent terminated within a foot of an operable window, which says to me that the installer was not qualified or didn't care about proper installation.

Thanks Mike, that diagram makes it appear to be a sort of HRV, which seems like a good idea, but I'm not sure about the PVC, plus, to act as an HRV, the vent pipe would have needed to make a 90-degree turn just inside the manifold.

Too much guesswork here. Time for a specialist evaluation.
Attached Thumbnails
mid-level-efficiency-termination.jpg  




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 5/16/10 at 1:49 AM..
Reply With Quote
  #9  
Old 5/16/10, 1:48 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: mid-level efficiency?

Quote:
Originally Posted by dhays View Post
It looks like they have the connections reversed according to the pdf drawings that Michael provided. The exhaust should be in the center not the outside.
Looks that way to me too.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #10  
Old 5/16/10, 1:50 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: mid-level efficiency?

Quote:
Originally Posted by belliott View Post
The exhaust does go through the middle.
It is the schedule 40.
That doesn't make any sense to me, Bob. Why install a PVC exhaust and a metal intake?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #11  
Old 5/16/10, 3:07 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: mid-level efficiency?

Quote:
Originally Posted by belliott View Post
The exhaust does go through the middle.
It is the schedule 40.
They wouldn't spend all that money for a 3 inch stainless steel "intake" vent. The condensation tap and drain line is another clue that the stainless pipe is the exhaust vent. This boiler does specify stainless steel for the exhaust (I guess gas temps are still too high for PVC on this unit). PVC is specified as OK for the intake. They have definitely made the connection to the concentric terminal inside/out on this. Also should be minimum of 4 feet from the window.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #12  
Old 5/16/10, 5:52 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: mid-level efficiency?

If it needs a metal exhaust ,then it makes no sense to use a PVC air intake either.
The exhaust must get awfully hot if it must be metal.
Why would you surround plastic with hot metal and poisonous gas.?
Reply With Quote
  #13  
Old 5/16/10, 8:14 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: mid-level efficiency?

Quote:
Originally Posted by dhays View Post
It looks like they have the connections reversed according to the pdf drawings that Michael provided. The exhaust should be in the center not the outside.
Good catch. Sometimes you just have to be there.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/16/10, 9:45 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: mid-level efficiency?

Quote:
Originally Posted by kshepard View Post
Natgas has been in our area for only 8-10 years with not much showing up in inspections. Have not yet seen a concentric terminal for gas but have seen many for oil boilers/furnaces. They have been in use for 10-12 years and are known as sealed combustion / direct vent systems. They work well if properly located and installed. There's a list of 12 "shall nots" for the vent outlet. Here's a few:

A vent shall not terminate:

- under a veranda, deck or porch

- less than 3 ft from an inside corner of an L-shaped structure

- within 6 ft of an operable window, door, or mechanical air supply to any building including soffit openings

- within 6 ft of any combustion air inlet, unless the appliance is otherwise certified

BTW, the direct vent condensing units are considered "high efficiency".

Last edited by Brian A. MacNeish; 5/16/10 at 1:32 PM.. Reason: additional info
Reply With Quote
  #15  
Old 5/17/10, 1:13 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: mid-level efficiency?

Quote:
Originally Posted by belliott View Post
If it needs a metal exhaust ,then it makes no sense to use a PVC air intake either.
The exhaust must get awfully hot if it must be metal.
Why would you surround plastic with hot metal and poisonous gas.?
Because the manufacturer of the UL listed device said it needs a stainless steel vent and specifically not to use plastic for the vent. It was stated pretty clearly in the installation guide.

Properly installed, the intake air will pass through the outer ring of the concentric, not through the center - this one is configured inside out.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 5/17/10 at 1:18 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fluke Ti32 / Fluke TiR32 & Level X Infrared Certification Package jkaylor Thermal Imaging, Infrared Cameras & Energy Audits 6 9/10/09 7:37 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM
Level 1 Certification dvalley Thermal Imaging, Infrared Cameras & Energy Audits 73 1/21/08 3:00 PM