Default Minimum slope for water heater exhaust flue?

1. gas-fired water heater 1/4" per foot. Right?
2. Oil-fired WH?
3. Gas-fired furnace?
4. Oil-fired funace?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #2  
Old 6/7/08, 9:11 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Minimum slope for water heater exhaust flue?

Kenton is this another version of 20 questions????



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 6/7/08, 9:39 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Minimum slope for water heater exhaust flue?

James, do you always answer a question with a question?

Seriously, no, these are very simple questions. I went through the IRC, couldn't find the answers on the first pass. I suspect they're there, but I'm runnin' outa' time. I've got a deadline and would appreciate any help. Don't know why I don't know this already but at this point I just need to be accurate. There's always more to learn... sit down to write a library of narratives and that will become obvious really fast.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 6/7/08 at 9:57 PM..
Reply With Quote
  #4  
Old 6/7/08, 10:20 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Minimum slope for water heater exhaust flue?

wish I could help you Kenton...I'll back away now and give the experts a chance....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 6/7/08, 10:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,469
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by kshepard
1. gas-fired water heater 1/4" per foot. Right?
2. Oil-fired WH?
3. Gas-fired furnace?
4. Oil-fired funace?
Kenton, all the installation instructions, for any of the above, that I've ever seen were a minimum of 1/4" per foot but I don't have a code reference handy.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 6/7/08, 10:46 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Minimum slope for water heater exhaust flue?

James and Larry, thanks for answering, I was embarrased to admit I don't know, can't find it in the IRC, now I feel a little better but would like to get at the real answer.
Does it vary by jurisdiction? Is it established by the IRC but a little hard to find?

Anyone got an answer for this?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #7  
Old 6/7/08, 10:53 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by kshepard
James and Larry, thanks for answering, I was embarrased to admit I don't know, can't find it in the IRC, now I feel a little better but would like to get at the real answer.
Does it vary by jurisdiction? Is it established by the IRC but a little hard to find?

Anyone got an answer for this?
Kent,

Manufacturers installation instructions for all listed appliances.
Reply With Quote
  #8  
Old 6/7/08, 11:00 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,469
Default Re: Minimum slope for water heater exhaust flue?

I can't imagine it would vary by jurisdiction and the manufacturer's installation instructions would prevail.

Heck, just the other day I had a Burnham power vented boiler that required the vent pipe to fall 1/4" per foot toward the termination.

Sorry I can't help more.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 6/7/08, 11:03 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by lkage
I can't imagine it would vary by jurisdiction and the manufacturer's installation instructions would prevail.

Heck, just the other day I had a Burnham power vented boiler that required the vent pipe to fall 1/4" per foot toward the termination.

Sorry I can't help more.
Too drain condensation----

Ahhh...What is a Boiler by the way Larry?....
Reply With Quote
  #10  
Old 6/7/08, 11:10 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,469
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by dduffy
Too drain condensation----
Yes, but most often we see them drain back to the furnace to a condensate pump.



Quote:
Originally Posted by dduffy
Ahhh...What is a Boiler by the way Larry?....

Ah, you should feel fortunate you don't need to know.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 6/7/08, 11:13 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by dduffy
Too drain condensation----

Ahhh...What is a Boiler by the way Larry?....

just a big or small hot water tank used to heat a house or building Dale.....it's not warm all the time everywhere....some of us need heat from time to time....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #12  
Old 6/8/08, 10:10 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by kshepard
James and Larry, thanks for answering, I was embarrased to admit I don't know, can't find it in the IRC, now I feel a little better but would like to get at the real answer.
Does it vary by jurisdiction? Is it established by the IRC but a little hard to find?

Anyone got an answer for this?
Page 312 IRC M1803.3



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 6/11/08, 6:43 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Minimum slope for water heater exhaust flue?

Quote:
Originally Posted by cbottger
Page 312 IRC M1803.3
Ah, but IRC M1801.1 states those requirements only apply to fuel burning equipment other than gas, which needs to be vented in accordance with IRC Chapter 24. The plot thickens ...

For Category-I gas equipment (basically natural draft, standard efficiency), G2427.10.8 requires the 1/4" per foot slope upwards towards the chimney.

For other types of gas equipment, the IRC requires the installation to meet the equipment manufacturer's requirements.

[P.S. The IRC requirements above apply to water heaters, furnaces, and boilers]



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 6/12/08 at 4:43 PM..
Reply With Quote
  #14  
Old 6/13/08, 2:12 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Minimum slope for water heater exhaust flue?

Kenton

Good question, but a little open ended.
The problem with "your" question is that there are variables that we probably all see in the field, that weren't mentioned in "your" question.
1- Is the vent H & V run in a totally open area or is part of the venting material passing through combustible materials or encapsulated in chases of combustible material.
2- What type of material are we talking about (ex.- Metal Ridgid Double-Wall/ B'vent type pipe & fittings, Metal Ridgid Single-wall/pipe & fittings, Metal Flexible rated pipe & fittings, PVC Pipe & fittings, etc.).
3- Local codes in our area typically exceed minimum standards set be the Manuf. of the venting materials and/or the Equipment/Appliance Manuf's. recommendations.
If I see what I think is a problem I always check local code dept's. when I go outside my local jurisdiction, just in case.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 7:11 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
HVAC / Water Heater Flue abishop Inspecting HVAC Systems 5 2/22/06 12:30 PM
Exhaust fan in room with gas water heater and furnace jweinberg Inspecting HVAC Systems 7 2/18/06 2:23 PM


All times are GMT -4. The time now is 4:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts