Default My furnace short cycling

The glow plug comes on, the burners start and about 15 seconds later the burners quit. It just keeps repeating this way. There is a button size limit switch by the 4th burner at the opposite end of the glow plug and I bought a new one but it is still short cycling...

There is a rod about an 1/8" by 4" long that hangs down into the 4th burner. What is it? Could that be the problem? Then above all the burners in the middle I see another button size limit switch, what is that for?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 1/2/07, 11:24 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 53,147
Default Re: My furnace short cycling

Mark, most systems have some type of flame proving device. If the flame is not "sensed within the set time the gas valve will shut down to a safe condition.

What you describe sounds like there is no signal from this device. The rod you describe could be a cappillary tube that funtions as this device. Does that rod have a tube going all the wy back to the gas valve?

A photo or two might help to troublehoot you rproblem. Good luck.

Last edited by mlarson; 1/2/07 at 11:35 AM..
Reply With Quote
  #3  
Old 1/2/07, 11:29 AM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 7,022
Default Re: My furnace short cycling

Mark,
Same thing happened to me this winter. I called my HVAC guy.....$75. He took steel wool to some components???? and it fixed the problem. I get fliers from him every spring and fall reminding me of his preventative maintenance services he offers to avoid these problems.



Linas Dapkus, CMI
Infraspection Institute Certified Infrared Thermographer Level III # 8510
Dapkus Home Inspections
Dapkus Home Inspections Inc. - No Gimmicks, No Kickbacks, Your personal contact information will not be sold to third parties. For 8 years & counting, quality home inspections is all we sell.
Reply With Quote
  #4  
Old 1/2/07, 11:55 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 840
Default Re: My furnace short cycling

Quote:
Originally Posted by ldapkus
Mark,
Same thing happened to me this winter. I called my HVAC guy.....$75. He took steel wool to some components???? and it fixed the problem. I get fliers from him every spring and fall reminding me of his preventative maintenance services he offers to avoid these problems.
Same here last year.

We tell everyone else to have regular maintenance, why don't we follow our own advice?



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #5  
Old 1/2/07, 1:40 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 8,093
Default Re: My furnace short cycling

This can be associated with gas pressure regulation, as well as component failure.

There are so many sensors to insure things are safe, they must systematically diagnosed. Your HVAC Tech is likely the only one that is qualified for this and it is well worth the money spent. Let them do the parts changing if they can't figure it out the first time around.

That limit switch you are describing has to do with flame roll out. You can see this happen if it is the case.

There are limit devices, proving devices, sequential devices, and safety devices. You must understand each one and how to test them (without replacing them).

It is about as probable to diagnose the issue from here as it would be to inspect the house from the Internet. You are an expert, let the experts do their job.
Reply With Quote
  #6  
Old 1/3/07, 2:06 AM
rsummers rsummers is offline
New User
 
Join Date: Oct 2003
Location: 13302 Cabin Hollow Court Suite 110 Chico, CA 95973
Posts: 39
Please Note: rsummers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: My furnace short cycling

Is the unit have a board with a fault indicator on it? It sounds like the Flame sensor is not picking up the ground. Ive seen equipment that operated properly when 1st fired up only to fail later on due to a poor ground. Also check the polarity on the cord most units wont operate on heat if this is wrong.
Reply With Quote
  #7  
Old 1/3/07, 2:40 AM
dhadler's Avatar
dhadler dhadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 377
Default Re: My furnace short cycling

Mark, I've had several instances like yours. My heating tech guy did the same thing....he took a plumbers fitting cleaner(little wire brush) or like another suggested, emery sandpaper, and cleaned that sensor rod. Worked perfectly. He said it was usually due to washer/dryer cleaners and additives building up on the sensor. He also said if they are in the same general area its likely to occur more often?

Might as well give it shot...cheap fix...not much to lose.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #8  
Old 1/3/07, 10:09 AM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,118
Default Re: My furnace short cycling

Home inspectors should take their own advise. We would recommend an item like this to a professional tradesman but when it comes to doing it ourselves we become reluctant to follow that same sage advise. As Dave A. stated there are numerous devices installed to perform safety functions and someone may correct one thing by fixing it themselves, allowing the furnace to function and completely miss another problem by not doing the full system analysis the tech would do to insure the system is operating correctly. Recommend you call the HVAC man.
Reply With Quote
  #9  
Old 1/3/07, 11:08 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,686
Default Re: My furnace short cycling

Thanks guys. Darrell, I will give it a try . Thanks...




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #10  
Old 1/16/07, 10:24 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,686
Default Re: My furnace short cycling

Thanks guys. Darrell it worked!!! Saved me some cash!!




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #11  
Old 1/16/07, 1:07 PM
dhadler's Avatar
dhadler dhadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 377
Default Re: My furnace short cycling

That's great Mark...it's always nice to save a few bucks especially when its something simple like that and they have to charge you 1 hrs. labor just to come and clean off a little sensor. </IMG>



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


LinkBacks (?)
LinkBack to this Thread: http://www.nachi.org/forum/f20/my-furnace-short-cycling-11747/
Posted By For Type Date
Problem with Burnham Oil Furnace short cycling - DIY Chatroom - DIY Home Improvement Forum This thread Refback 9/10/08 10:05 PM

Similar Threads
Thread Thread Starter Forum Replies Last Post
Short Cycling twheeler Inspecting HVAC Systems 21 11/21/10 4:12 AM
Short cycling of furnace lagudo Inspecting HVAC Systems 12 10/17/07 9:47 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph Inspecting HVAC Systems 2 6/6/07 3:56 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer Inspecting HVAC Systems 19 4/9/07 9:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 9:17 PM

All times are GMT -4. The time now is 10:25 AM.
no new posts