Default Need AC input.

House #1
AC unit calls for min. 15.6/max. 25 amps. AC fuses are 25 amp. AC breaker in panel box is 30 amp. All #10 wire.

House #2
AC unit calls for min. 19.3/max. 25 amps. AC fuses are 20 amp. AC breaker in panel box is 30 amp. All #10 wire.

Neither seems right.

Thanks in advance.
Reply With Quote
  #2  
Old 9/7/07, 6:20 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,896
Default Re: Need AC input.

They both seem right to me. House #1 calls for a max of 25 amp, which you have at the unit. House #2 calls for a minimum of 19.3, and you have a 20 amp fuse at teh unit. Both witll work fine. The 'oversized' breaker in the box does not matter, as both units will shut off from the fuses if there is a problem.
Reply With Quote
  #3  
Old 9/7/07, 6:26 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,661
Default Re: Need AC input.

Ya, what William said.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #4  
Old 9/7/07, 6:38 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,527
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need AC input.

The 30 amp breakers match the #10 wire.

The first unit should be alright wth the 25 amp fuses.......the higher rating is usually written as the "locked rotor" or starting current.

Definition:
LOCKED ROTOR CURRENT
Steady state current taken from the line with the rotor at standstill (at rated voltage and frequency). This is the current seen when starting the motor and load.

The 20 amp fuses may be "time delay" fuses that allow a higher start-up current momentarily and then allows it to return to the lower running current. Did you run the second unit and it had no problems? See:
http://elpaso.apogee.net/foe/fsgotdf.asp
Reply With Quote
  #5  
Old 9/7/07, 11:31 AM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Need AC input.

The weakest link should always be the circuit breaker (or fuses in this case). The circuit breaker basically function as a disconnect switch.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need some input... dlawrence General Inspection Discussion 24 9/14/07 11:47 AM
Input please.... rhumphries Misc. Discussion 0 2/16/07 9:24 AM


All times are GMT -4. The time now is 5:29 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts