Default Need Assistance on A/C Unit

Did an inspection on pre-manufactured (double-wide) home late yesterday. The A/C unit did not have a manufacturer specified on Unit or Mfg tag. The furnace was a coleman. The model # on A/C Unit is BRCO0481BD with a S/N of 010322259. Also need to find tonnage of A/C. The home was manufacturered by Hart Housing Group of Indiana in August of 2001.

Does anybody have any idea who the A/C Unit was manufacturered by. I ran it through Preston with no luck. The people at HArt did'nt know. Your help would be appreciated. Thank you in advance.
Reply With Quote
  #2  
Old 6/20/06, 11:45 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need Assistance on A/C Unit

Patrick,

I believe that you wrote the model # down incorrectly, I think you are looking at an Airpro BRCQ0481BD which is a 2001 4 ton unit

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 6/20/06, 11:48 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: Need Assistance on A/C Unit

By the model number, it looks like a four ton unit. Must've been a big mobile!

The manufacturer company is probably listed at the bottom of the tag in very small print. Usually a trick of Inter City products, or Goodman/Janitrol, which would not necessarily be the brand name on the unit.
Reply With Quote
  #4  
Old 6/20/06, 1:20 PM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: Need Assistance on A/C Unit

Blaine is right about that. Intercity is bad for no name units. You bought a Mc Unit No brand tag at all.
Reply With Quote
  #5  
Old 6/20/06, 2:30 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need Assistance on A/C Unit

Patrick,

You may know this already, but the 48 in the model number gives the tonnage away. Most manufacturers use this system.

Look for multiples of 12 in the model number for tonnage
48 / 12 = 4 tons

54 / 12 = 4.5 tons

etc..
Reply With Quote
  #6  
Old 6/20/06, 3:43 PM
Patrick Carter's Avatar
Patrick Carter Patrick Carter is offline
Active Poster
 
Join Date: Oct 2004
Posts: 427
Please Note: pcarter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need Assistance on A/C Unit

Everybody thanks for the help. No mfg was on that tag which really surprised me some, usually thaey give some good clues as who put the unit together but not in this case. Yep, Gerry, you are probaly right about the O being a Q, since all the other numbers matched up, I will go with the mfg you listed. The unit requires servicing anyway and I am telling them to have it serviced because of crimp in the supply line and noisy fan (bearing going bad sound). So the HVAC Tech can have a go at it as well. The tonnage is a bit much for a 1680 sq. ft. double wide.
Reply With Quote
  #7  
Old 6/20/06, 8:31 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,759
Default Re: Need Assistance on A/C Unit

On your typical 1600-1700 sf house in this area a 4 ton would be overkill. On top of that because it was so big - it would have a tendency to come on, cool the space off very quickly then cycle off.

Because of that you could have more humidity and be less comfortable.
Reply With Quote
  #8  
Old 6/20/06, 8:46 PM
Patrick Carter's Avatar
Patrick Carter Patrick Carter is offline
Active Poster
 
Join Date: Oct 2004
Posts: 427
Please Note: pcarter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need Assistance on A/C Unit

Very short cycles in fact, you should have seen the water coming out of the condensate pan drain hose, a very steady stream. I could see the "A" coils and that were sweating badly, water just dripping off of them.
Reply With Quote
  #9  
Old 6/21/06, 1:45 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,759
Default Re: Need Assistance on A/C Unit

The longer it runs the more humidity removed OR vice versa.
Reply With Quote
  #10  
Old 6/21/06, 8:23 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Need Assistance on A/C Unit

Coleman is a major manufacturer, and York is a major distributor of the Coleman brand.
www.colemanac.com
They either specialize in mobile/manufactured homes, or they have a really nice contract with the manufacturers of such homes.
They seem to be to mobile/manufactured homes what In-Sink-Erator is to disposals.
In fact, I don't think I've ever seen anything other than a Coleman (or York) in the mobile/manufactured homes around here.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year

Last edited by rray; 6/21/06 at 8:27 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Geo unit neat system cbottger HVAC 14 4/14/08 3:48 PM
Illinois: Carbon Monoxide Alarm Detector Act rcramer Legislation, Licensing & Legal Issues 2 2/9/07 8:52 AM
Help with unit size rcarter HVAC 4 2/1/07 5:55 PM


All times are GMT -4. The time now is 7:07 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts