Default Need HVAC pro's for question

Shouldn't there be a trap on this setup, before the vertical vent. This set up is blowing conditioned air out the vent.
Attached Thumbnails
need-heating-venting-air-conditioning-pros-question-trap-400-x-266-.jpg.jpg
Views:	59
Size:	47.8 KB
ID:	13599  
Reply With Quote
  #2  
Old 8/1/07, 6:10 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: Need HVAC pro's for question

From what I see in the picture, yes a trap should be installed. As far as they system blowing conditioned air into the space, I don't see how that would be possible. The condensate pan is below the evaporator coils which are below the blower. I could see the possibility of it sucking air through the blowout in the picture, but not blowing air out. If it really is blowing air out, I would check the rotation of of the blower motor and it's orientation.

Just read another thread and completely forgot about blow through set-ups. I don't run across any where I'm at because most HVAC contractors install draw through systems from what I see around here. If it is a blow through system, then yes you definately need a trap and there neds to be a cap on that blow-out fitting.

Last edited by sgilligan1; 8/1/07 at 6:20 PM..
Reply With Quote
  #3  
Old 8/1/07, 7:06 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need HVAC pro's for question

Quote:
Originally Posted by sgilligan1
From what I see in the picture, yes a trap should be installed. As far as they system blowing conditioned air into the space, I don't see how that would be possible. The condensate pan is below the evaporator coils which are below the blower. I could see the possibility of it sucking air through the blowout in the picture, but not blowing air out. If it really is blowing air out, I would check the rotation of of the blower motor and it's orientation.

Just read another thread and completely forgot about blow through set-ups. I don't run across any where I'm at because most HVAC contractors install draw through systems from what I see around here. If it is a blow through system, then yes you definately need a trap and there neds to be a cap on that blow-out fitting.
Thanks Scott...

I wish furnace and heat pump manufacturers put installation documents on the web like other appliances do (water heater,etc...). You know, something to refer to....
Reply With Quote
  #4  
Old 8/1/07, 7:06 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need HVAC pro's for question

This pages may help.

They used to be on the Trane site, but have disappeared.

I retrieved them form the Wayback Machine Net Archives, and combined them into a single document:
Attached Files
File Type: pdf Trane - Trapping Design Flaws.pdf (173.3 KB, 3368 views)
Reply With Quote
  #5  
Old 8/1/07, 7:12 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need HVAC pro's for question

Quote:
Originally Posted by mthomas2
This pages may help.

They used to be on the Trane site, but have disappeared.

I retrieved them form the Wayback Machine Net Archives, and combined them into a single document:
Great, thanks for the pdf, that is exactly what I was looking for.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HVAC in unvented, spray foam insulated attic? lfreeze Inspecting HVAC Systems 17 6/20/07 9:58 AM
Room size requirement for HVAC supply kweiss Inspecting HVAC Systems 3 6/9/07 6:58 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 10 5/21/07 3:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM


All times are GMT -4. The time now is 6:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts