Hey all you HVAC guru's...can someone cite the IRC section about using walls as a plenum for return vents between the basement to the 2nd floor? Had a pre-drywall inspection today on a 2500 sq.ft. new construction and found that the builder is leaving the cavities in the walls open for the return vents from the second floor. I know there have been issues/concerns about mold ...not to mention the lack of any fire boundary in these spaces, but my client has the walkthrough with the builder tomorrow and I'd like to give him some additional ammo for when he asks the builder to do it, as I am sure it up to code for the area, but I feel it is in my clients best interests to have this done the right way. Thanks for any help...</IMG>



James A. Honaker
In and Out Home Inspection
www.inandoutinspections.com
info@inandoutinspections.com
(847) 877-0417
Serving Chicago and surrounding suburbs
Reply With Quote
  #2  
Old 7/20/06, 12:48 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Need some HVAC help

This help you James?


SECTION 602

PLENUMS


602.1 General.
Supply, return, exhaust, relief and ventilation
air plenums shall be limited to uninhabited crawl spaces, areas
above a ceiling or below the floor, attic spaces and mechanical
equipment rooms. Plenums shall be limited to one fire area.
Fuel-fired appliances shall not be installed within a plenum.



602.2 Construction.
Plenum enclosures shall be constructed
of materials permitted for the type of construction classification
of the building.
The use of gypsum boards to form plenums shall be limited
to systems where the air temperatures do not exceed 125ºF
(52ºC) and the building and mechanical system design conditions
are such that the gypsum board surface temperature will
be maintained above the airstream dew-point temperature. Air
plenums formed by gypsum boards shall not be incorporated in
air-handling systems utilizing evaporative coolers.


Reply With Quote
  #3  
Old 7/20/06, 1:28 AM
jhonaker jhonaker is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Zion, IL
Posts: 279
Default Re: Need some HVAC help

Thanks Dale. Now in sec. 602.2, it mentions "materials permitted for the type of construction classification"...This is a residential and the plenums are the raw, untreated, stud quality 2x's on 2 sides and the gypsum on the others. They are in the interior walls, which I do not foresee hitting 125 deg., but condensation can form at much lower temps. I guess this would be where the dew point part of it would come into play though...correct? Also, if I am reading correctly, in .1 it mentions to be limited to 1 fire area...If it were running in openings from the basement, through the first floor and into the 2nd floor, wouldn't this be in violation of breaking fire boundaries? Please correct me if I am reading wrong, as I want to make sure I am fully understanding it.



James A. Honaker
In and Out Home Inspection
www.inandoutinspections.com
info@inandoutinspections.com
(847) 877-0417
Serving Chicago and surrounding suburbs

Last edited by jhonaker; 7/20/06 at 1:32 AM..
Reply With Quote
  #4  
Old 7/20/06, 8:36 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Need some HVAC help

Here is the IRC section on the issue from Part V - Mechanical ...
Quote:
(IRC) M1601.1.1 Above-ground duct systems.
Above-ground duct systems shall conform to the following:
1. Equipment connected to duct systems shall be designed to limit discharge air temperature to a maximum of 250°F (121°C).
2. Factory-made air ducts shall be constructed of Class 0 or Class 1 materials as designated in Table M1601.1.1(1).
3. Fibrous duct construction shall conform to the SMACNA "Fibrous Glass Duct Construction Standards" or NAIMA "Fibrous Glass Duct Construction Standards."
4. Minimum thicknesses of metal duct material shall be as listed in Table M1601.1.1(2). Galvanized steel shall conform to ASTM A 525.
5. Gypsum products are permitted to be used to construct return air ducts or plenums, provided that the air temperature does not exceed 125°F(52°C) and exposed surfaces are not subject to condensation.
6. Duct systems shall be constructed of materials having a flame-spread index not greater than 200.
7. Stud wall cavities and the spaces between solid floor joists to be utilized as air plenums shall comply with the following conditions:
7.1. Such cavities or spaces shall not be utilized as a plenum for supply air.
7.2. Such cavities or spaces shall not be part of a required fire-resistance-rated assembly.
7.3. Stud wall cavities shall not convey air from more than one floor level.
7.4. Stud wall cavities and joist space plenums shall be isolated from adjacent concealed spaces by tight-fitting fire blocking in accordance with Section R602.8.
The biggest issue is the floor-to-floor wall plenum due to the spread of fire (Par. 7.3), and condensation on the outside can be an issue if the plenum walls are in any unconditioned spaces (Par. 5)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #5  
Old 7/20/06, 12:32 PM
jhonaker jhonaker is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Zion, IL
Posts: 279
Default Re: Need some HVAC help

Thanks Robert. I advised my client to use the M60101.1.1 7.3 quote as well as the 602.1, concerning only 1 fire area.

Thanks to both of you for the help.



James A. Honaker
In and Out Home Inspection
www.inandoutinspections.com
info@inandoutinspections.com
(847) 877-0417
Serving Chicago and surrounding suburbs
Reply With Quote
  #6  
Old 7/21/06, 2:49 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Need some HVAC help

I would stay away from quoting specific model code sections, and just use things like the IRC (Dale's quote appears to be from another code) as a general guide for providing general recommendations. It may not be the locally adopted code, and could put you on a slippery slope (e.g. does everything else comply with the IRC even though it may not be adopted or the standard used for code inspections).

Any questions about code compliance should be directed to the local building department, and ya may have a fight on your hands if it does indeed comply with the legally adopted building code and the issue gets pushed.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #7  
Old 7/21/06, 7:24 AM
jhonaker jhonaker is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Zion, IL
Posts: 279
Default Re: Need some HVAC help

Quote:
Originally Posted by roconnor
I would stay away from quoting specific model code sections, and just use things like the IRC (Dale's quote appears to be from another code) as a general guide for providing general recommendations. It may not be the locally adopted code, and could put you on a slippery slope (e.g. does everything else comply with the IRC even though it may not be adopted or the standard used for code inspections).

Any questions about code compliance should be directed to the local building department, and ya may have a fight on your hands if it does indeed comply with the legally adopted building code and the issue gets pushed.

JMO & 2-nickels ...
I did advise my client that there is the chance that it does meet the local code, but I could not say for sure. I also advised that I tend to stick to the national codes, as these stick as the minimums with some additional adjustments by local municipalaties normally, but also said that I use my own best judgement concerning safety. Not sure if I made it sound like I advised the client to fight tooth and nail for it to be done, as I did not, but I advised him to bring it up to the builder and have the additional information on-hand in case the builder wanted to know where the information came from. I also advised that it would hurt to ask for it (not demand, as I know what kind of trouble this could lead to) and see how the builder reacted to it and then take it from there once you get a feel for what he may/may not want to do...but I did write it up as a fire hazard 1st and foremost. Thanks again.



James A. Honaker
In and Out Home Inspection
www.inandoutinspections.com
info@inandoutinspections.com
(847) 877-0417
Serving Chicago and surrounding suburbs
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Room size requirement for HVAC supply kweiss Inspecting HVAC Systems 3 6/9/07 6:58 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 10 5/21/07 3:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
HVAC..definitely my weakness..any help? tneumann Inspecting HVAC Systems 3 1/30/06 5:37 PM


All times are GMT -4. The time now is 10:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts