Hey all you HVAC guru's...can someone cite the IRC section about using walls as a plenum for return vents between the basement to the 2nd floor? Had a pre-drywall inspection today on a 2500 sq.ft. new construction and found that the builder is leaving the cavities in the walls open for the return vents from the second floor. I know there have been issues/concerns about mold
James A. Honaker In and Out Home Inspection www.inandoutinspections.com info@inandoutinspections.com (847) 877-0417 Serving Chicago and surrounding suburbs |
|
#2
|
||||
|
||||
|
This help you James?
SECTION 602 PLENUMS 602.1 General. Supply, return, exhaust, relief and ventilation air plenums shall be limited to uninhabited crawl spaces, areas above a ceiling or below the floor, attic spaces and mechanical equipment rooms. Plenums shall be limited to one fire area. Fuel-fired appliances shall not be installed within a plenum. 602.2 Construction. Plenum enclosures shall be constructed of materials permitted for the type of construction classification of the building. The use of gypsum boards to form plenums shall be limited to systems where the air temperatures do not exceed 125ºF (52ºC) and the building and mechanical system design conditions are such that the gypsum board surface temperature will be maintained above the airstream dew-point temperature. Air plenums formed by gypsum boards shall not be incorporated in air-handling systems utilizing evaporative coolers. Dale Duffy Inspect Arizona Companies, Inc. Phoenix Commercial Building Inspectors, Inc. Phoenix Thermal Imaging, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#3
|
|||
|
|||
|
Thanks Dale. Now in sec. 602.2, it mentions "materials permitted for the type of construction classification"...This is a residential and the plenums are the raw, untreated, stud quality 2x's on 2 sides and the gypsum on the others. They are in the interior walls, which I do not foresee hitting 125 deg., but condensation can form at much lower temps. I guess this would be where the dew point part of it would come into play though...correct? Also, if I am reading correctly, in .1 it mentions to be limited to 1 fire area...If it were running in openings from the basement, through the first floor and into the 2nd floor, wouldn't this be in violation of breaking fire boundaries? Please correct me if I am reading wrong, as I want to make sure I am fully understanding it.
James A. Honaker In and Out Home Inspection www.inandoutinspections.com info@inandoutinspections.com (847) 877-0417 Serving Chicago and surrounding suburbs Last edited by jhonaker; 7/20/06 at 1:32 AM.. |
|
#4
|
||||
|
||||
|
Here is the IRC section on the issue from Part V - Mechanical ...
Quote:
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#5
|
|||
|
|||
|
Thanks Robert. I advised my client to use the M60101.1.1 7.3 quote as well as the 602.1, concerning only 1 fire area.
Thanks to both of you for the help. James A. Honaker In and Out Home Inspection www.inandoutinspections.com info@inandoutinspections.com (847) 877-0417 Serving Chicago and surrounding suburbs |
|
#6
|
||||
|
||||
|
I would stay away from quoting specific model code sections, and just use things like the IRC (Dale's quote appears to be from another code) as a general guide for providing general recommendations. It may not be the locally adopted code, and could put you on a slippery slope (e.g. does everything else comply with the IRC even though it may not be adopted or the standard used for code inspections).
Any questions about code compliance should be directed to the local building department, and ya may have a fight on your hands if it does indeed comply with the legally adopted building code and the issue gets pushed. JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#7
|
|||
|
|||
|
Quote:
James A. Honaker In and Out Home Inspection www.inandoutinspections.com info@inandoutinspections.com (847) 877-0417 Serving Chicago and surrounding suburbs |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Room size requirement for HVAC supply | kweiss | Inspecting HVAC Systems | 3 | 6/9/07 6:58 PM |
| Access to Electrical Panel in Ontario by HVAC Contractors | Nalliah Thayabharan | Canadian Inspectors | 10 | 5/21/07 3:01 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |
| HVAC..definitely my weakness..any help? | tneumann | Inspecting HVAC Systems | 3 | 1/30/06 5:37 PM |