Default Never had this...

I typically test the Delta T of the A/C at the return and just past the plenum. Today, I got a difference of 29F which is way higher than anything I've gotten before.

The unit is 3 years old, outside temp was 75F, overcast, RH about 40-50%. I let it run for about 20 minutes after running the heat for about 15 before I measured the temp. The temp past the A-coil was 41F. I'm sure there are many factors to this and I don't look at Delta T as the end-all of indicators, but I figured it's worth discussing.

Is this high of a Delta T a concern? It seems odd to ask this question, but it's just so out of the ordinary.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector
www.aaintegrityhomeinspection.com
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/3/13, 6:41 AM
Rick A. Harrington's Avatar
Rick A. Harrington Rick A. Harrington is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Westerville, Oh
Posts: 198
Default Re: Never had this...

Cameron,

When I get a high Delta T during the AC test, I ask what can cause this?

1) air speed. is the fan set at the right speed? I can't test this
2) Is the filter dirty? This can slow air speed through the unit allowing the air to become colder as it moves past the A-Coil more slowly
3) As I have seen this happen before -- If there is a humidifier on the HVAC system --- the damper that is used to control air flow from the humidifier is open or missing and that is allowing colder air to flow directly back into the cold air return to join with the air coming from the living space and really cause a high Delta T. (this situation also caused some condensation as the duct was not insulated through a garage ceiling and water was dripping on the garage ceiling drywall). Once we blocked the air from the humidifier duct, the Delta T returned to normal.

Since this Delta T may be out of the ordinary (you didn't say what the AC unit capacity is) then something may be amiss.

Hope this helps



Rick A. Harrington

Patch Independent Home Inspections, LLC
Serving Columbus and Central Ohio
Certified Specialist - Infrared Residential Inspections Advanced
Certified Level 1 Thermographer
Certified Mold Inspector
State of Ohio Licensed Radon Tester


http://www.patchhomeinspections.com
http://www.centralohiohomeinspector.com
http://www.columbusohiohomeinspector.com
http://www.thermalimagescanning.com

Last edited by rharrington; 7/3/13 at 6:43 AM.. Reason: adding info to answer the question more completely.
Reply With Quote
  #3  
Old 7/3/13, 6:51 AM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: My house
Posts: 9,742
Default Re: Never had this...

My guess is they went from a R22 system to a R410 system, in addition to the great ideas above I would add overcharged system, or/and the air return is much smaller than what is needed, significantly decreasing the air intake.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.


Reply With Quote
  #4  
Old 7/3/13, 7:29 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,965
Default Re: Never had this...

Quote:
Originally Posted by rhensel View Post
My guess is they went from a R22 system to a R410 system, in addition to the great ideas above I would add overcharged system, or/and the air return is much smaller than what is needed, significantly decreasing the air intake.
Can not happen an over charge creates higher pressure which in turn creates higher temp suction and head pressure

Super heat temp needs adjusted unit does not run the proper time between cycles to remove humidity



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #5  
Old 7/3/13, 7:37 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 12,468
Default Re: Never had this...

Cameron in this case I would this write up temperature differentials were not normal recommend a license heat and air contractor to to review and repair as necessary. It is not our job to analyze as you said many factors could be in play for this one. Overcharging would not cause this is Charlie stated



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 7/3/13, 8:11 AM
Cameron Anderson's Avatar
Cameron Anderson Cameron Anderson is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 6,844
Default Re: Never had this...

Thanks guys. That really helps, I appreciate you taking time to answer.



Cameron Anderson
Integrity Home Inspection
Truth. In Real Estate.
Since 2004
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector
www.aaintegrityhomeinspection.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -4. The time now is 6:06 PM.
no new posts