InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > HVAC

HVAC Topics include heating, venting, and air conditioning.

Reply
 
LinkBack Thread Tools Display Modes
  #1  
Old 4/26/07, 10:40 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default New Geo unit neat system

I inspected a 4 year old home this week that had a Geo unit installed unlike any I have inspected before.

It was a two story one system unit with supply and returns from the ceiling.

Both levels had their own thermostats that could activate the cooling or heating mode separate of each other or both call for A/C or heat at the same time. Needless to say one stat could not be in heat and the other stat in cool both stats have to be in the same mode. There were 24 volt controlled dampers in the supply duct that would open and close according to what stat was calling. If the down stairs was calling for cooling the upstairs dampers would go closed and VS if the upstairs was calling and not the down stairs and both would open if both stats were calling at the same time.

This unit had two vertical loops one for each level of the home that were drilled to 200 feet in depth. This was all controlled with an electronic logic board. I liked this system. I was just wondering how many inspectors have ran into this type of system any comments.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #2  
Old 4/27/07, 1:21 AM
Joseph B. Kormos's Avatar
Joseph B. Kormos Joseph B. Kormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 640
Joseph B. Kormos .
Default Re: New Geo unit neat system

Monticello had form of geothermal AC back in the day. A few contractors are starting to advertise these types of system in my area. I have yet to see one, I have seen Earth homes built into the ground. I would imagine that these unites are still rather pricey.
http://www.geoexchange.org/incentives/incentives.htm
http://en.wikipedia.org/wiki/Geothermal_heating
http://www.eere.energy.gov/consumer/.../mytopic=12670



Joe Kormos
A-1st Look Home Inspectors Inc.
630-201-0933
Your 1st Choice in Property Inspection Professionals
www.a-1stlookhomeinspectors.com
www.a-1stlook.com
Let us look before you buy...for peace of mind
“Thinking is the hardest work there is, that’s why so few engage in it. ” Henry Ford
Reply With Quote
  #3  
Old 4/27/07, 9:16 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: New Geo unit neat system

Quote:
Originally Posted by jkormos
Monticello had form of geothermal AC back in the day. A few contractors are starting to advertise these types of system in my area. I have yet to see one, I have seen Earth homes built into the ground. I would imagine that these unites are still rather pricey.
http://www.geoexchange.org/incentives/incentives.htm
http://en.wikipedia.org/wiki/Geothermal_heating
http://www.eere.energy.gov/consumer/.../mytopic=12670
The seller was present during the inspection and he asked me if I knew what these system cost, my guess was 12K to 15 K and he stated the price was right in the middle as he had the home custom built.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #4  
Old 4/28/07, 12:15 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
jbreazeale is generally well trusted
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Geo unit neat system

That's not a bad price, considering the long-term savings. I've yet to see one, but I've studied them in whatever info I could find on the web and elsewhere. I wonder...did that price include the whole installation, or just the equipment? How prevalent are they out where you are?
Reply With Quote
  #5  
Old 4/28/07, 9:05 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: New Geo unit neat system

Quote:
Originally Posted by jbreazeale
That's not a bad price, considering the long-term savings. I've yet to see one, but I've studied them in whatever info I could find on the web and elsewhere. I wonder...did that price include the whole installation, or just the equipment? How prevalent are they out where you are?
Jimmy;
I would think the price quoted was turn key and no they are not real common but are starting to catch on for those country locations that can afford the price.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 4/28/07, 11:09 AM
bbenjamin bbenjamin is offline
New User
 
Join Date: Feb 2007
Location: Round O, SC
Posts: 45
bbenjamin hasn't had much positive or negative feedback
Please Note: bbenjamin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Geo unit neat system

Charley,

I have been installing these types of systems for about 10 years in Hilton Head, South Carolina. Every 2 story house that I installed over that period of time has this type of design. I use Honeywell Zone boards and T-stats.
Reply With Quote
  #7  
Old 5/2/07, 12:24 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
jbreazeale is generally well trusted
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Geo unit neat system

Bruce, I'm no expert on the subject, but I'm thinking that ductwork design and static pressure are paramount considerations when installing this type of system. Am I correct? I'd like to hear your thoughts on that.
Reply With Quote
  #8  
Old 5/5/07, 5:22 PM
bbenjamin bbenjamin is offline
New User
 
Join Date: Feb 2007
Location: Round O, SC
Posts: 45
bbenjamin hasn't had much positive or negative feedback
Please Note: bbenjamin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Geo unit neat system

Jimmy,

You are correct. The design of the systems ductwork is always a big consideration. The more efficient the system is the most cost effective it will be for the consumer. Most air conditioning equipment has to be at least a 14 seer rating to be considered engery efficent. The higher the seer rating the more efficent the system is suppose to be.
Reply With Quote
  #9  
Old 4/14/08, 7:26 AM
Charles J. Yezza Charles J. Yezza is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: Concord, Oh
Posts: 314
Charles J. Yezza is generally well trusted
Default Re: New Geo unit neat system

Quote:
Originally Posted by cbottger
I inspected a 4 year old home this week that had a Geo unit installed unlike any I have inspected before.

It was a two story one system unit with supply and returns from the ceiling.

Both levels had their own thermostats that could activate the cooling or heating mode separate of each other or both call for A/C or heat at the same time. Needless to say one stat could not be in heat and the other stat in cool both stats have to be in the same mode. There were 24 volt controlled dampers in the supply duct that would open and close according to what stat was calling. If the down stairs was calling for cooling the upstairs dampers would go closed and VS if the upstairs was calling and not the down stairs and both would open if both stats were calling at the same time.

This unit had two vertical loops one for each level of the home that were drilled to 200 feet in depth. This was all controlled with an electronic logic board. I liked this system. I was just wondering how many inspectors have ran into this type of system any comments.
How did you determine whether it was a vertical loop?



Chuck Yezza, President
1st Choice Property Inspectors Inc.
NACHI #05012083
Concord, Ohio

440-6678458
cyezza@roadrunner.com

www.1stcpi.com
Reply With Quote
  #10  
Old 4/14/08, 8:20 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,157
Barry Adair .
Default Re: New Geo unit neat system

This is a good site for beginners studying these systems, like me



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
  #11  
Old 4/14/08, 9:32 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: New Geo unit neat system

Quote:
Originally Posted by cyezza
How did you determine whether it was a vertical loop?
Geez old thread had forgot about it. Very easy to determine I could see the well head plus the seller was present and we were discussing the cost of drilling the water well.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #12  
Old 4/14/08, 9:38 AM
GARY L. RUSK GARY L. RUSK is online now
InterNACHI Member
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 117
GARY L. RUSK .
Default Re: New Geo unit neat system

Thanks Barry
I am also a beginner on geothermal systems.

Gary
http://www.hsspropertyinspection.com/
Reply With Quote
  #13  
Old 4/14/08, 9:43 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,360
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: New Geo unit neat system

Quote:
Originally Posted by cbottger
Geez old thread had forgot about it. Very easy to determine I could see the well head plus the seller was present and we were discussing the cost of drilling the water well.
Charlie,

I did a new construction inspection that had a Geo Thermal system. When I talked to the owner he was telling me that the vertical loop systems often have problems after a few years because they get "clogged up" and That's why he chose a buried field loop system.

Is it possible that he was talking about a twin well type that was not closed closed loop?

I wasn't sure what he meant by "clogged up."

Have you heard of any problems with the vertical loop systems?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #14  
Old 4/14/08, 3:45 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: New Geo unit neat system

Quote:
Originally Posted by mlarson
Charlie,

I did a new construction inspection that had a Geo Thermal system. When I talked to the owner he was telling me that the vertical loop systems often have problems after a few years because they get "clogged up" and That's why he chose a buried field loop system.

Is it possible that he was talking about a twin well type that was not closed closed loop?

I wasn't sure what he meant by "clogged up."

Have you heard of any problems with the vertical loop systems?
I have not seen a twin well type here we take the suction and discharge from the same well head. The only problem with clogging that I could see would be if some knuckle head installed the discharge and suction to close to the bottom and stirred up the debris in the bottom of the well casing.

BTW I like the ground loop myself fill with glycol and forget it



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.

Last edited by cbottger; 4/14/08 at 3:49 PM.
Reply With Quote
  #15  
Old 4/14/08, 3:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,360
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: New Geo unit neat system

Didn't make sense to me either.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues 293 2/10/08 2:20 AM
THE "GROUNDING "TRUTH- Article To Read pabernathy Electrical 1 1/1/07 2:14 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues 0 2/14/06 4:38 AM


All times are GMT -4. The time now is 11:52 PM.