Default No ductwork??

I recently inspected a very intricately designed 1980 home with Geo Thermal. The house has a main floor and a full basement built with engineered floor trusses. (high tec for 1980?) I pulled up a floor register on a hardwood floor to discover no duct work. I at first I thought it was a cold air return. I found out that this is the heat source. The owner/designer has charged the entire floor cavity with warm air. (Keep in mind this is geo thermal, so no risk of overheating, fire or even carbon monoxide) Where ever he wanted heat, he simply cut a register into the floor or ceiling. He says this works well, and keeps his floors warm too.

This is the first time running into this configuration, and it took me a minute to wrap my head around it. Have anyone else seen this or have anything to add?
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/6/12, 10:25 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: No ductwork??

Quote:
Originally Posted by mroberson View Post
I recently inspected a very intricately designed 1980 home with Geo Thermal. The house has a main floor and a full basement built with engineered floor trusses. (high tec for 1980?) I pulled up a floor register on a hardwood floor to discover no duct work. I at first I thought it was a cold air return. I found out that this is the heat source. The owner/designer has charged the entire floor cavity with warm air. (Keep in mind this is geo thermal, so no risk of overheating, fire or even carbon monoxide) Where ever he wanted heat, he simply cut a register into the floor or ceiling. He says this works well, and keeps his floors warm too.

This is the first time running into this configuration, and it took me a minute to wrap my head around it. Have anyone else seen this or have anything to add?
"Geothermal" simply explains the heat source and has nothing to do with heat distribution.

What would be your thoughts if this were a standard air source heat pump supplying heat to the air handler with this configuration?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 2/6/12, 10:28 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: No ductwork??

Sounds pretty inefficient to me, but I've never actually seen a geothermal system. Was there a heat pump incorporated into the system, or was it simply a radiant transfer of the earths heat to the residence?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 2/6/12, 10:31 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: No ductwork??

Quote:
What would be your thoughts if this were a standard air source heat pump supplying heat to the air handler with this configuration?
I would call this out IF this had a standard gas fired forced air system. I would think this would be less efficient. Also anytime you remove part of the ceiling, you will basically depressurize the heat system.
I cant see any reason why this is dangerous, Im curious what YOU have to say about it Jim.
Reply With Quote
  #5  
Old 2/6/12, 10:34 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: No ductwork??

Jeff: This was a "Pump and Dump" style geothermal, that looked like a large stainless furnace. It has a internal heat "Extractor" and a forced air blower. It used about 10 gallons per minute.
Reply With Quote
  #6  
Old 2/6/12, 10:37 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: No ductwork??

With that type of distribution, ducts would certainly be more efficient and I would likely recommend that as an upgrade to the system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 2/6/12, 10:37 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: No ductwork??

Houses years ago had a big old wood stove and that heated the first floor and opening let the air get to the second .
With this system the floors would always be warm and warm floors make MOMMA happy with her warm feet .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #8  
Old 2/6/12, 10:51 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: No ductwork??

Quote:
Originally Posted by jpope View Post
With that type of distribution, ducts would certainly be more efficient and I would likely recommend that as an upgrade to the system.
The blower simply blew into the floor cavity, roughly 125 degree air (I didn't actually measure the air temp, but the plenum above the furnace was nice and warm) It had a natural cold air return through the stairwell and open balcony. Almost all the doors an the house were Louvered to improve air flow.

This was very quiet, (and once the floors are warm) I would think a very even heat. I could also see moisture as less of an issue in the floor cavity.

I guess Sunny Southern CA don't install these much Jeff?
Reply With Quote
  #9  
Old 2/6/12, 12:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: No ductwork??

Quote:
Originally Posted by mroberson View Post
I guess Sunny Southern CA don't install these much Jeff?
No, we don't. The only thing I've seen that might be similar, was a "solar room."

This hillside home had a dedicated room with rounded glass (1/4 round essentially) running the length of the home facing south. The room was roughly 10'WX10'HX40'L. At the top of the interior wall, there were thermostatically controlled dampers, which allowed heated air to flow beneath the house through an 18" (non-partitioned) finished crawl space. The solar room had two blowers, one at each end of the room. Throughout the house, there were floor registers that opened directly into the crawlspace.

The biggest "issue," according to the homeowner, was the temperature difference of the conditioned air by the time it reached the opposite end of the home. I imagine a ducted system would have helped solve (or at least reduce) that problem.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 2/6/12, 1:09 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: No ductwork??

Hows's this for a description? Comments?

No ducting present. Furnace blows warm air into the Floor cavity, and then subsequently out of the registers. Cold air return is natural though the louvered doors, stairwell, and balcony. This is an irregular but not necessarily an unsafe method of heat distribution considering the heat is geo-thermal. Installing ductwork would help improve the efficiency of the air flow system, but would change the "warm floor" feeling.
Reply With Quote
  #11  
Old 2/6/12, 1:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: No ductwork??

Again, I am not familiar with these systems, but that sounds like what I would suggest. I would change "irregular" to "unconventional."

Was there a return air duct at least, or does the system draw air from the outdoors?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 2/6/12, 3:40 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: No ductwork??

How does he get the heat to travel across the joist bays? I guess any heat that is loss downward enters the basement. The rim should be sealed and insulated well to prevent heat loss that way. Also any wire or pipe homes would need sealing to prevent the air blowing up the wall cavity and into the attic. It's a interesting to say the least.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #13  
Old 2/6/12, 4:00 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: No ductwork??

Quote:
Originally Posted by rernst1 View Post
How does he get the heat to travel across the joist bays? I guess any heat that is loss downward enters the basement. The rim should be sealed and insulated well to prevent heat loss that way. Also any wire or pipe homes would need sealing to prevent the air blowing up the wall cavity and into the attic. It's a interesting to say the least.
Very good point Robert, I obviously couldn't see all the rim joists, but they were insulated where I could see. These were engineered floor joists, about 24" thick and made of criss-crossing 2x4's. Heat would flow just fine sideways.
A shot from below the floor through a heat duct.
Attached Thumbnails
no-ductwork-dscf0473.jpg  
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/6/12, 4:03 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: No ductwork??

Quote:
Was there a return air duct at least, or does the system draw air from the outdoors?
The Cold air return system was a natural flow, through the Louvered doors, down the stairwell or balcony, and into the utility room.
Reply With Quote
  #15  
Old 2/6/12, 4:06 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: No ductwork??

A very similar and grossly inefficient system is commonly found in mobile homes. I can't believe somebody would put this in a real house. What an incredible waste.

Is this an exceptionally small home ... 1000 sf or less?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is this on the Ductwork? iniquette Inspecting HVAC Systems 5 10/9/09 7:38 AM
Client states loud banging in ductwork? crichiii Inspecting HVAC Systems 7 2/9/09 9:47 PM
Oxidation on Ductwork mnahrgang Inspecting HVAC Systems 10 11/9/07 8:54 AM


All times are GMT -4. The time now is 10:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts