Default No return duct reporting ?

i inspected a (side-by-side) double yesterday and found the same condition in both units. the furnaces had no return ducts and were just drawing air from the basement. this was in an 1890's house that had new supply ducts, but they didnt buck up for the returns.

how do you all report these? i just note the lack of them and explain the 'possible' hazards. at least you can see when the filter needs a changing

ALSO, while im on the subject, this house had a couple ducts that ive seen a few times where there what appears to be a return duct connected to a floor grate on an exterior wall, but the duct runs straight down and terminates about 6" from the floor. its not connected to anything?? ive seen these in a couple old homes. what were these? wish i had a pic.

Bob

Last edited by bmargiotti; 5/26/06 at 8:30 AM..
Reply With Quote
  #2  
Old 5/26/06, 8:58 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: No return duct reporting ?

Quote:
Originally Posted by bmargiotti
i inspected a (side-by-side) double yesterday and found the same condition in both units. the furnaces had no return ducts and were just drawing air from the basement. this was in an 1890's house that had new supply ducts, but they didnt buck up for the returns.

how do you all report these? i just note the lack of them and explain the 'possible' hazards. at least you can see when the filter needs a changing

ALSO, while im on the subject, this house had a couple ducts that ive seen a few times where there what appears to be a return duct connected to a floor grate on an exterior wall, but the duct runs straight down and terminates about 6" from the floor. its not connected to anything?? ive seen these in a couple old homes. what were these? wish i had a pic.

Bob
Bob, I have seen very many older furnace installations where return air is drawn from the basement. While this eems to work ok on some older and "leakier" buildings I have always recomended that a return air duct be installed somewhere in the conditioned space.

As for the duct to the outside, this is a combustion air supply.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 5/26/06, 12:08 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: No return duct reporting ?

I'll second Gerry comments,

This most likely is natural draft, cat 1 ,negative pressure furnace. Now the part about the return air ducts missing is defeating the effectiveness of the heating system.
You want a return air duct in the living space. Not within 10 feet of the FAU in the same room!

Negative room pressure , cold air volume, duct sizing ( cold air requires a larger duct) all plays a major role on how the living space is going to be heated effectively. Since cold air is at the floor level , you want that to be "pulled" back into the FAU to be heated and "pushed" out the supply register. (pressure in smaller ducts) Not having a return air duct in the living spaces "works" but the efficiency and effectiveness of the system is not there.

The other open ducts are to supply combustion air to the FAU, 1 square inch for every 1000 BTU's is the general rule. These ducts are installed in several different ways. Some take it from the attic (one high duct , one low duct) never just one duct!! One is at least open 12" above the floor where the FAU is located and the other is within 12" from the ceiling of the FAU room. Some ducts are routed to the outside walls, some are installed to pull from the crawl space and attic, some are louvers to adjacent rooms that are much larger to fulfill the combustion air requirements.

This allows for proper movement of combustion air so the FAU has enough O2 to burn clean and have the Natural draft hood dilution air so the flue can "draw" that product of combustion outside ..

When you see an old natural draft FAU in a closet and it's tight...It's a death machine.
If the current H/O remodeled a basement and "hide the old beast" it's a possible death machine. People don't realize a FAU can be a killer.
Keep em safe ..

Last edited by pbolliger; 5/26/06 at 12:15 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Critter in the return air duct... swaskewicz Inspecting HVAC Systems 11 11/28/07 3:49 PM
furnace return air duct vwood Inspecting HVAC Systems 5 6/19/07 1:18 PM
Reduced return air duct mmorgan Inspecting HVAC Systems 4 6/6/07 7:39 PM
Gas line in return duct jhugenroth Inspecting HVAC Systems 0 8/10/06 9:01 AM
return air duct? dbucknavich Inspecting HVAC Systems 2 5/17/06 10:53 PM


All times are GMT -4. The time now is 10:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts