Default Is this normal?

Was wondering what might be the cause of the markings at the interior of the hot air furnace. I did not operate the furnace because the AC was running when I arrived. Furnace is approximately 21 years old.
Attached Thumbnails
normal-img_8877.jpg  
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/3/10, 2:48 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Is this normal?

Why would the AC running stop you from testing the furnace?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 8/3/10, 3:25 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Is this normal?

Agree with Jim that you should have ran it.
Corrosion is usually from moisture but do you have a wider shot ? (How did the flue and hood area look?) and also I notice a paint bucket with water in it.
Is that where they are draining condensation?
Reply With Quote
  #4  
Old 8/3/10, 3:26 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Is this normal?

The change in temperature between heat and cool mode can cause damage to the evaporator coil.
Reply With Quote
  #5  
Old 8/3/10, 3:38 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is this normal?

Quote:
Originally Posted by jgromkoski View Post
The change in temperature between heat and cool mode can cause damage to the evaporator coil.
How do you account for the hot heat exchanger in the winter?



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #6  
Old 8/3/10, 3:39 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Is this normal?

There is a condensation pump attached to the side of the furnace, the bucket may have been there to catch any leakage from the pump though I did not see any leaking when I was there. The slight corrosion on the furnace casing is likely a result of a past leak from the condensation pump or pvc drain pipe. There was no leaking or corrosion above the area in the picture. I was more concerned with the high temperature marks on the exterior casing of the heat exchanger.
Reply With Quote
  #7  
Old 8/3/10, 3:41 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Is this normal?

Quote:
Originally Posted by jgromkoski View Post
The change in temperature between heat and cool mode can cause damage to the evaporator coil.
Then thousands of Inspectors are wrong.
Please provide proof that we should not test furnaces in the summer.
Seriously there is no harm if you wait for a short time.
I assume you were there at least a few hours so the reasoning is not valid.

Got a wider shot?
Reply With Quote
  #8  
Old 8/3/10, 5:08 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Is this normal?

I do not disagree with the idea that waiting a short time (perhaps inspecting the heat or cool at the beginning of the inspection, and testing the other mode closer to the end) would likely not harm the coil. I was told by my licensing course instructor 3 years ago that it was not required to test both aspects during a single inspection because of the potential damage. I believed it to be completely accurate as most inspectors around here test only one or the other.
Reply With Quote
  #9  
Old 8/3/10, 5:14 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Is this normal?

Quote:
Originally Posted by jgromkoski View Post
Was wondering what might be the cause of the markings at the interior of the hot air furnace. I did not operate the furnace because the AC was running when I arrived. Furnace is approximately 21 years old.

Its slap worn out and not safe anymore since it was never intended to function for that long. Any HVAC tech will recommend replacing it on the next service call whether it runs or not.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #10  
Old 8/3/10, 5:25 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Is this normal?

Quote:
Originally Posted by jgromkoski View Post
I was told by my licensing course instructor 3 years ago that it was not required to test both aspects during a single inspection because of the potential damage. I believed it to be completely accurate as most inspectors around here test only one or the other.
That is insane.

If you are having people sign an inspection agreement and, on that agreement, if you are publishing that your inspections are being done in accordance with the NACHI SOP....you are violating that contract and can be subject to replacing a furnace that doesn't work if ever called on it.

One of the interesting things about being in business for yourself is...when someone has you by the balls....you can't get out of it by saying "My instructor told me....."

If you don't have some hard, legitimate and credible material to base your deviation from this universally accepted industry standard....you are providing a disservice to your client and are creating the potential for some very bad relations between you, our industry, and your clients.

Please follow the SOP.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #11  
Old 8/3/10, 5:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Is this normal?

Quote:
Originally Posted by jgromkoski View Post
I do not disagree with the idea that waiting a short time (perhaps inspecting the heat or cool at the beginning of the inspection, and testing the other mode closer to the end) would likely not harm the coil. I was told by my licensing course instructor 3 years ago that it was not required to test both aspects during a single inspection because of the potential damage. I believed it to be completely accurate as most inspectors around here test only one or the other.
I believe your instructor was referring to heat pumps.

An inspector who doesn't test a gas furnace during a home inspection is providing an incomplete inspection.

I turn off the AC at the end of the inspection. As soon as the blower comes to a stop, on comes the heat. As soon as I verify the heat functions (about 10 minutes), I turn it off. Once the blower comes to a stop, on comes the AC again.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 8/3/10, 5:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Is this normal?

By the way, do you know what the "AUTO" setting on a thermostat does?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 8/3/10, 5:28 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Is this normal?

Quote:
Originally Posted by bking View Post
Its slap worn out and not safe anymore since it was never intended to function for that long. Any HVAC tech will recommend replacing it on the next service call whether it runs or not.
Bruce what does "slap worn out" mean?
I am not familiar with the new rap lingo you kids have now in days.

Also age is not a reason to call it not safe as far as I know.
At what age does a furnace become not safe?
I want to know so I can stop testing all those over the safe age limit, and just insist it needs "automatic replacement".
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/3/10, 5:37 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Is this normal?

Joe, I'm not sure I understand what your "AUTO" comment is meant to be? Please explain the purpose of your question so I know where you are coming from.
Reply With Quote
  #15  
Old 8/3/10, 6:17 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Is this normal?

Just for the record.

Every person who attends a NY Home Inspector Licensing Course is given an inspection book titled The Home Inspection Book, A Guide For Professionals by Marcia Darvin Spada. The NY licensing exam is based on the information in this book. Under the Section titled Inspecting the Furnace on page 193 it states Check the location of the thermostat and make sure that it is registering. Inspectors can use the thermostat to check the operation of the heating system. This operation should not be performed in warm weather, however, in a dual heating-air conditioning hot air system. It also should not be performed when a separate air-conditioning unit is on because the excess heat can damage the conditioner's evaporator coils.

In that case, the instructor was not wrong in advising students not to test both systems and inspectors in NY are not wrong if they only test one or the other. To the contrary if damage is cause the inspector has made himself liable.

In my report I make it abundantly clear that I have not tested the Heat mode of the system and state the reason for it. I recommend that the system be tested prior to close of escrow and after the AC has been off for several hours.

Whenever possible, if none of the systems are running at the start of the inspection, I recommend testing the heat mode of the system over the AC, but I let my client make the call. In the report I make it clear that "at the client's request" only one aspect of the heat/ac was tested.

Please don't get me wrong that I am trying to short cut any inspection as my reputation locally is one of being extremely thorough - not a RE agent's most welcomed face at an inspection. I am only following the State guidelines which supersede the NACHI SOP.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New frugality is the new normal, by necessity jburkeson1 Miscellaneous Discussion for Inspectors 4 9/21/09 11:26 AM
Normal Life Expectancy jmckenna1 Miscellaneous Discussion for Inspectors 6 1/29/07 9:57 PM
Normal Stuff We See.... pabernathy Electrical Inspections 8 1/28/06 12:51 PM


All times are GMT -4. The time now is 10:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts