Default How not to install a return air

This was one nasty mess the closet itself was part of the return chamber filter grill located at the top of the closet they tried to block off the door but air was bypassing filter at the bottom of the door. The closet was open into the wall allowing bypass from the attic and the crawl space both. the A-coil was more than likely matted with lint. I did not bother looking just wrote it up.
Attached Thumbnails
not-install-return-air-151-magnolia-kaw-city-5-16-11-006.jpg   not-install-return-air-151-magnolia-kaw-city-5-16-11-007.jpg   not-install-return-air-151-magnolia-kaw-city-5-16-11-008.jpg   not-install-return-air-151-magnolia-kaw-city-5-16-11-009.jpg   not-install-return-air-151-magnolia-kaw-city-5-16-11-010.jpg  




Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/17/11, 12:19 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: How not to install a return air

Thought that was an outhouse .
Reply With Quote
  #3  
Old 5/17/11, 8:08 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: How not to install a return air

Quote:
Originally Posted by belliott View Post
Thought that was an outhouse .
Most outhouses are two holers



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 5/17/11, 8:14 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: How not to install a return air

Quote:
Originally Posted by cbottger View Post
Most outhouses are two holers
This has two holes. The urinal is in the upper left hand corner, 1st photo.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #5  
Old 5/17/11, 9:10 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How not to install a return air

Quote:
Originally Posted by cbottger View Post
This was one nasty mess the closet itself was part of the return chamber filter grill located at the top of the closet they tried to block off the door but air was bypassing filter at the bottom of the door. The closet was open into the wall allowing bypass from the attic and the crawl space both. the A-coil was more than likely matted with lint. I did not bother looking just wrote it up.
Good example of what research from the 1990's showed as reported in HOME ENERGY magazine:

"20 to 40% of air moving through the air handler did not go to or return from the rooms it was designed/intended for"

This is a big inefficiency not addressed in many house energy retrofits.
Reply With Quote
  #6  
Old 5/17/11, 10:47 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: How not to install a return air

Quote:
Originally Posted by Brian A. MacNeish View Post
Good example of what research from the 1990's showed as reported in HOME ENERGY magazine:

"20 to 40% of air moving through the air handler did not go to or return from the rooms it was designed/intended for"

This is a big inefficiency not addressed in many house energy retrofits.
I have inspected new out of the box furnaces that were installed on existing duct work the return air plenum on the upflow furnace was touching soil in the crawl and the bottom was missing or big holes installer did not bother to look. Same with downflow with the supply plenum in the crawl. Usually more problems found with the duct work than the units themselves



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 5/17/11, 12:14 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How not to install a return air

Quote:
Originally Posted by cbottger View Post
I have inspected new out of the box furnaces that were installed on existing duct work the return air plenum on the upflow furnace was touching soil in the crawl and the bottom was missing or big holes installer did not bother to look. Same with downflow with the supply plenum in the crawl. Usually more problems found with the duct work than the units themselves
As I have mentioned before, in Dec/1989, I started and headed a new subsidiary corp for a mechanical design firm. It's initial focus was IAQ and small commercial/industrial/institutional TAB (Test/Adjust/Balancing) of HVAC systems.

I bought a duct leakage tester from England through Davis Equipment/Instruments in Philadelphia (I believe). It's barrel resembled a small cannon with a series of finely machined nozzles of declining diameter with exterior pressure taps......they could measure down to 1-2 cfm flow!! In one situation (seniors managed care home with newly installed windows) I used the smallest nozzle to do window air leakage testing after complaints from the old folks!!

Some of the better engineers were specing main trunk air leakage rates of 3-5% of total design flows...kept the subs on their toes doing good work!!

Some companies selling blower doors now have duct air leakage testers:

http://www.retrotec.com/residential/.../ModelQ32.aspx

http://www.energyconservatory.com/ap...lications1.htm
Reply With Quote
  #8  
Old 5/17/11, 2:01 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: How not to install a return air

People are to trusting when it comes to things they know nothing about. Automatically assuming that the contractor will do a perfect install. Even if a permit is pulled and a inspection by the AHJ was performed contractors know that AHJ's do not enter crawl spaces and inspect duct on a retro fit. Some of the duct jobs I have observed are simply shameful.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 5/17/11, 2:34 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: How not to install a return air

Quote:
Originally Posted by cbottger View Post
People are to trusting when it comes to things they know nothing about. Automatically assuming that the contractor will do a perfect install. Even if a permit is pulled and a inspection by the AHJ was performed contractors know that AHJ's do not enter crawl spaces and inspect duct on a retro fit. Some of the duct jobs I have observed are simply shameful.
That is why Handymen make a good living.
Reply With Quote
  #10  
Old 5/17/11, 2:56 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: How not to install a return air

What a nice way to share the odor of wet coats with the rest of the house.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #11  
Old 5/17/11, 6:50 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: How not to install a return air

Quote:
Originally Posted by belliott View Post
That is why Handymen make a good living.
Not handymen I was talking about, licensed contractors doing this kind of crap ya know the ones that we refer to



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 5/17/11, 6:53 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: How not to install a return air

Quote:
Originally Posted by sstanczyk View Post
What a nice way to share the odor of wet coats with the rest of the house.
Probably more like a drying rack smell goes away after the moisture evaporates



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 5/21/11, 11:39 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How not to install a return air

What about the unplugged gas valve?
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/21/11, 7:00 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: How not to install a return air

Quote:
Originally Posted by Gary Reecher View Post
What about the unplugged gas valve?
Gary that was on my repair list also no gas lines allowed in the return unplugged or not. I was waiting for someone to comment no mention until now thanks



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 5/21/11, 7:14 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How not to install a return air

Let me take a guess at this install. Furnace was installed in the closet at some time in the past and some enterprising person decided it would be a great idea to move the furnace into the crawl space. And they shortly went out of business.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cold air return mthiltgen Inspecting HVAC Systems 13 3/27/09 4:20 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM