Default Not a very good design

This was a "down-flow" unit, where the return air compartment is on top of the furnace, which was on top of the evaporator coil.

Typically, I see these types of units with the vent pipe routed around the return air compartment, but not this time.

The vent runs directly through the return, and out of the closet from there. Notice the soot at the inside of the cabinet.

Not a very good design. . .
Attached Thumbnails
not-very-good-design-pc110010.jpg   not-very-good-design-pc110011.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #2  
Old 12/11/06, 8:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Not a very good design

Quote:
Originally Posted by jpope
This was a "down-flow" unit, where the return air compartment is on top of the furnace, which was on top of the evaporator coil.

Typically, I see these types of units with the vent pipe routed around the return air compartment, but not this time.

The vent runs directly through the return, and out of the closet from there. Notice the soot at the inside of the cabinet.

Not a very good design. . .
Not allowed in this state flue can not pass thru any supply or return air.
Reply With Quote
  #3  
Old 12/11/06, 11:11 PM
kmcmahon kmcmahon is offline
Active Poster
 
Join Date: Apr 2004
Location: Stevens Point, WI
Posts: 224
Please Note: kmcmahon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Not a very good design

ditto here..
Reply With Quote
  #4  
Old 12/12/06, 11:00 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Not a very good design

Quote:
Originally Posted by cbottger
Not allowed in this state flue can not pass thru any supply or return air.
That is probably true in most jurisdictions, and model codes address it as "constructed components" - plenums and such. In this case however, this is how the FAU was manufactured, in other words, this is (was) a listed system.

This entire complex had these units installed (34 years ago) and I inspected three of them yesterday. The fact that two, out of three, of these units showed evidence that the vents were "leaking" into the return air compartments, was a bit alarming.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 12/12/06, 9:14 PM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: Not a very good design

It make changeing the blower motor a real pain, been there



James R Lilly, CMIA
www.lhiservices.com
jamesrlilly@lhiservices.com
Home and Mold Inspections Radon Testing
Based in Parkersburg, WV
Serving West Virginia and Ohio
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM
Extractd from the archives, Thanks Paul for this list! jtedesco1 Electrical Inspections 4 1/2/07 7:51 PM
Grounding -V- Bonding Article (Good Read) pdoane Electrical Inspections 0 10/12/06 4:31 PM


All times are GMT -4. The time now is 10:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts