Should a heat pump be tested if the unit as not been on for over 12 or more hours? Doesn't the heater in the crankcase need to be on to prevent damage to the compressor?

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #2  
Old 1/23/08, 11:00 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,730
Default Re: On or Off?

Here where it is warm probably no problem, where you are in the cold NO it should not be tested.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 1/23/08, 11:37 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: On or Off?

What if it is a heat pump with a Scroll compressor instead of a Reciprocating Compressor and does not have crankcase heaters?
Reply With Quote
  #4  
Old 1/23/08, 11:56 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,730
Default Re: On or Off?

Educate me Doug.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #5  
Old 1/24/08, 7:44 AM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: On or Off?

One other question to the group. When temps. outside are below a certain range
do not run the AC, correct, this is for a heat pump. Also, running in heat mode, when temps are below a certain range, run in normal cycle or em/aux for testing? All this is within SOP.

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #6  
Old 1/24/08, 11:59 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: On or Off?

Quote:
Should a heat pump be tested if the unit as not been on for over 12 or more hours?
What do you mean by "not on"? Only if the power has been turned off to the unit is there a problem.

Quote:
What if it is a heat pump with a Scroll compressor instead of a Reciprocating Compressor and does not have crankcase heaters?
A scroll compressor can handle just about anything passing through it and should not be affected by the cold. It will make one heck of a noise when it starts up from the oil passing through the scroll though.

Quote:
Also, running in heat mode, when temps are below a certain range, run in normal cycle or em/aux for testing? All this is within SOP.
You should test the heat pump in both the heat pump mode in the auxiliary/EM heat load separately. When you test the heat pump you should be sure that the auxiliary/EM he is not on. You may need to turn off the breaker, or make sure you don't turn the thermostat up more than 2° from an achieved setpoint (unit being off).

Running a heat pump in cold weather is never a problem as it is designed to operate in both heating and cooling (which it does every 45 minutes or so for defrost) in the winter. There is an accumulator in a pump that collects oil and returns it to the compressor at a slower rate to prevent potential damage to a reciprocating type compressor.
Reply With Quote
  #7  
Old 1/24/08, 11:24 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,730
Default Re: On or Off?

Well I am kinda up to speed on scroll pumps now, thanks David.
I made the assumption that Gary meant that the power was completely off to the unit, I see that that may not be the case.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #8  
Old 1/25/08, 12:40 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: On or Off?

I assumed that too, but then wasn't sure.

It should be noted that there is always a potential to wash out the compressor oil on startup of a cold compressor. It will all come back so long as there is not a problem with the refrigerant lineset (split system only). We may not know of this potential problem as it is not something we normally look at and evaluate.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:58 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts