  #1  
Old 6/10/09, 2:20 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Is it ok...

Is it ok to have a larger duct on a water heater? Here's one that has the same size duct as the furnace. (You can't tell from the picture but it enters the pipe "behind" the furnace duct.)
Attached Thumbnails
ok-dscn0903.jpg  
Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #2  
Old 6/10/09, 2:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Is it ok...

Mark, best I can tell the water heater is 4" and the furnace is 5"

http://www2.iccsafe.org/states/seatt...pendix%20B.pdf



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 6/10/09 at 3:58 PM..
Reply With Quote
  #3  
Old 6/10/09, 2:42 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: Is it ok...

Is this an accurate comment?

1.The water heater duct is entering the flue behind the location where the furnace flue enters. The larger (furnace) BTU appliance should be closer to the stack than the smaller one (water heater). In this case they are reversed. This could cause “back drafting” of the furnace exhaust gasses down the water heater flue and into the home. Major Concern. Recommend repair.
Reply With Quote
  #4  
Old 6/10/09, 2:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Is it ok...

Mark, are you sure about the diameters of the two flues?

A side shot by any chance?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 6/10/09, 3:03 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,525
Default Re: Is it ok...

Quote:
Originally Posted by mnahrgang View Post
Is this an accurate comment?

1.The water heater duct is entering the flue behind the location where the furnace flue enters. The larger (furnace) BTU appliance should be closer to the stack than the smaller one (water heater). In this case they are reversed. This could cause “back drafting” of the furnace exhaust gasses down the water heater flue and into the home. Major Concern. Recommend repair.
No it's not accurate. WH does not have a duct, it has a vent.


As a side note; How many levels of concern do you use? You have "Major concern" here, curious as to what other verbiage you use there. TIA



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #6  
Old 6/10/09, 4:01 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Is it ok...

Quote:
Originally Posted by mnahrgang View Post
Is this an accurate comment?

1.The water heater duct is entering the flue behind the location where the furnace flue enters. The larger (furnace) BTU appliance should be closer to the stack than the smaller one (water heater). In this case they are reversed. This could cause “back drafting” of the furnace exhaust gasses down the water heater flue and into the home. Major Concern. Recommend repair.
See this document.

I think I had it bassackwards in my original post so I removed that comment.

I can't tell from the photo but they need to be offset(not entering the flue at the same place).

Read this document and note the examples:

http://www2.iccsafe.org/states/seatt...pendix%20B.pdf



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #7  
Old 6/10/09, 4:47 PM
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 2,620
Default Re: Is it ok...

Louvers are awful high on the furnace door. Does this furnace has a inducer draft/power vent?
Reply With Quote
  #8  
Old 6/10/09, 5:57 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: Is it ok...

Quote:
Originally Posted by mlarson View Post
See this document.

I think I had it bassackwards in my original post so I removed that comment.

I can't tell from the photo but they need to be offset(not entering the flue at the same place).

Read this document and note the examples:

http://www2.iccsafe.org/states/seatt...pendix%20B.pdf
According to your pdf, what I have pictured is fine. I'm still not sure about the "vent " sizing. I'll be back at the house tomorrow, but just at quick glance I thought they were the same size, and had always seen smaller vent pipes for WH's.
Reply With Quote
  #9  
Old 6/10/09, 7:12 PM
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 2,620
Default Re: Is it ok...

It looks like a 5 inch to me. Being a little big should not matter.
Reply With Quote
  #10  
Old 6/10/09, 7:30 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Is it ok...

Quote:
Originally Posted by jbraun View Post
It looks like a 5 inch to me. Being a little big should not matter.
The flue on the water heater must be the same size as the collar supplied with the appliance.

As James hinted at things may change if the furnace is a fan assisted draft.

My concern is that when the furnace runs the fan assisted exhaust will blow fumes out the water heater collar because of the lack of a wye fitting.

A better pic and more info would certainly help.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #11  
Old 6/11/09, 1:01 AM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 495
Default Re: Is it ok...

looks like 6" ducting



Need a Link Exchange? Inspector Links


Seattle,WA Commercial Inspectors

Reply With Quote
  #12  
Old 6/11/09, 9:24 AM
Matthew M. Berman Matthew M. Berman is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 84
Smile Re: Is it ok...

Remove the T fitting add a Y fitting connect the water heater to the strait end and the furnace to the Y and your good no chance of back draft
Reply With Quote
  #13  
Old 6/11/09, 6:34 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: Is it ok...

Ok, heres some more pictures from today...

The first picture is looking at the duct as it enters the chimney on the right.

The second is "caddy corner" to it so you get perspective.

The next three are the HW flue, the Furnace flue, and the combined double walled flue entering the chimney.
Attached Thumbnails
ok-dscn1519.jpg   ok-dscn1518.jpg   ok-dscn1521.jpg   ok-dscn1522.jpg   ok-dscn1523.jpg  

Reply With Quote
Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America)
  #14  
Old 6/11/09, 6:37 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: Is it ok...

Here the picture on the left is a close up of the single flue entering the chimney. (The washed out white area of the picture is bad photograpy. That is the cinder block chimney.) Note there is no fitting here, which was "tagged" by our local gas company. If you look closely though, the flue connects to a flexible metal flue inside the masonry chimney. This is the exact same material I found in a closet that was being used as ductwork (of course with duck tape.)

Comments?
Attached Thumbnails
ok-dscn1524.jpg   ok-dscn1483.jpg  
Reply With Quote
  #15  
Old 6/11/09, 7:31 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: Is it ok...

Mark,

Pics show the situation much better.

This is my opinion.

I think I would consider it OK as long as the water heater does not back draft when the furnace is running.

There probably should have been a wye instead of a tee for the water heater connection and 12" vertical above the water heater draft hood would be better as well.
Some manufactures specify the minimum vertical section above the draft hood before a change in direction.

This one specifies 6" of straight before the next fitting. See Figure 11

hth



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:59 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts