  #1  
Old 8/9/11, 10:42 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Older Bard AC condenser

Unit was "sucking" air on fan side and blowing out on fin side, this can't be right, can it? Not familiar with this type & unit is 30 years old.

Thanks in advance.
Attached Thumbnails
older-bard-ac-condenser-dscn0019.jpg   older-bard-ac-condenser-dscn0087.jpg  
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/9/11, 11:43 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Older Bard AC condenser

Quote:
Originally Posted by jfrederick View Post
Unit was "sucking" air on fan side and blowing out on fin side, this can't be right, can it? Not familiar with this type & unit is 30 years old.
Doesn't really matter how old it is ... the fan should be drawing air in thru the coil side/fins and blowing it out thru the fan side/grille.

For a unit that old it's likely a replacement fan that wasn't wired correctly. A pretty easy fix for a service tech who knows what they are doing ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #3  
Old 8/9/11, 12:03 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Older Bard AC condenser

Quote:
Originally Posted by roconnor View Post
Doesn't really matter how old it is ... the fan should be drawing air in thru the coil side/fins and blowing it out thru the fan side/grille.

For a unit that old it's likely a replacement fan that wasn't wired correctly. A pretty easy fix for a service tech who knows what they are doing ...
Thank you Sir, just wanted to double check.
Reply With Quote
  #4  
Old 8/9/11, 3:27 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Older Bard AC condenser

Seen some of those old units that did discharge through the condenser might need to check that out



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 8/9/11, 9:11 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Older Bard AC condenser

No, No, damn no!

Can't you guys leave this crap alone?!

Nothing wrong with that...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 8/10/11, 2:30 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Older Bard AC condenser

I have never come across an AC condenser that draws air in from the fan side/grille that didn't have the fan wired incorrectly. Plus it just seems wrong that ya could be drawing in debris that could be blown on the coil or wiring. Checked with a buddy who is an old time service tech and he said that Bard units aren't that common in my neck of the woods, but thats just how Bard did it. Ya learn something new every day.

In any event I would still call out that a condenser thats 30 yrs old needs to be serviced and checed out by a specialist, and that they budget for replacement.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/10/11 at 3:41 PM..
Reply With Quote
  #7  
Old 8/10/11, 3:22 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Older Bard AC condenser

Quote:
Originally Posted by roconnor View Post
I havent never come across an AC condenser that draws air in from the fan side/grille that didn't have the fan wired incorrectly. Plus it just seems wrong that ya could be drawing in debris that could be blown on the coil or wiring. Checked with a buddy who is an old time service tech and he said that Bard units aren't that common in my neck of the woods, but thats just how Bard did it. Ya learn something new every day.

In any event I would still call out that a condenser thats 30 yrs old needs to be serviced and checed out by a specialist, and that they budget for replacement.
See us old farts are good for something I have worked on Bards many times had enclosed electrical sub-stations with Bard package units hung on the exterior wall for cooling never did like them hard to work on some PE designed the unit and never worked on them some Bards had reverse air flow on the condenser some did not and If memory serves me there was an old york unit the same way



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 8/10/11 at 3:26 PM..
Reply With Quote
  #8  
Old 8/10/11, 4:33 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Older Bard AC condenser

Just goes to show ya that even after 25 years you can run across unusual situations ...

And I see mechanical designs from guys with no practical experience all the time. Last one was 14 forced air heat/cool systems for a commercial building with everything looking good on paper ... only problem was the furnace drives were not big enough for the cooling coils ... ... Just looking at the equipment schedule it looked wrong, but nobody bothered to check it. All the ductwork was then wrong too ...

Probably the same guy who designed the older Bard units. I'm thinking mostly about debris being blown on the coil fins and damaging it. You could change the fan/direction, but if thats the way they are designed it's probably better to just leave it alone and service it more regularly.

And your dating yourself again Charlie ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/10/11 at 8:23 PM..
Reply With Quote
  #9  
Old 8/10/11, 11:04 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Older Bard AC condenser

I didn't say I liked it...

Carrier also has blow through design (new ones).

See them all the time, and I hate them...

Yes crap does get sucked in, and they are a bear to clean (if anyone was so inclined to do so) :-0



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
I'm older than DIRT... jwilliams4 Miscellaneous Discussion for Inspectors 41 11/9/10 4:12 PM
older homes with Mario Kyriacou, rcooke Canadian Inspectors 45 5/9/08 5:30 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 9 9/9/07 7:02 PM
Older wiring dmacy Electrical Inspections 1 5/11/07 2:40 PM


All times are GMT -4. The time now is 10:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts