Default Outside condenser A/C no wires

I inspected a A/C system back a ways that had no 24 volt thermostat wires traveling to the outside unit. How can that be and it was operating.
Reply With Quote
  #2  
Old 12/10/06, 9:22 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,319
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: Outside condenser A/C no wires

There are several remote control units to make this work.



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 12/10/06, 9:27 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by bgraham
There are several remote control units to make this work.
Are they like a garage door opener.
Reply With Quote
  #4  
Old 12/10/06, 10:07 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by cbottger
Are they like a garage door opener.
I bought a thermostat at walmart $15;00 completly wire less and it tell me the outside temp and the green house temp . I have a wirless unit that I can turn on more heat in the green house again Walmart $15;00. yes just like the car door opener.
Roy
Reply With Quote
  #5  
Old 12/10/06, 10:22 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by rcooke
I bought a thermostat at walmart $15;00 completly wire less and it tell me the outside temp and the green house temp . I have a wirless unit that I can turn on more heat in the green house again Walmart $15;00. yes just like the car door opener.
Roy
But guys this A/C unit had a indoor thermostat conventional mounted on the wall regular heat and cool position with auto/ on fan switch just no wires to the outside unit?????
Reply With Quote
  #6  
Old 12/10/06, 10:24 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 3,174
Michael R. Boyett .
Default Re: Outside condenser A/C no wires

How was the 220 run to the condensing unit? Sealtight? Could the LV t-stat wires been there? Not right, but nothing physically stopping them from being there.
Reply With Quote
  #7  
Old 12/10/06, 10:25 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 1,581
Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information
Default Re: Outside condenser A/C no wires

I have seen the low voltage wires inside the electrical conduit.
Reply With Quote
  #8  
Old 12/10/06, 10:27 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by mboyett
How was the 220 run to the condensing unit? Sealtight? Could the LV t-stat wires been there? Not right, but nothing physically stopping them from being there.
No I checked the seal tight where the 220-volt entered the unit. No 24 volt wires there either.
Reply With Quote
  #9  
Old 12/10/06, 10:27 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by cbottger
But guys this A/C unit had a indoor thermostat conventional mounted on the wall regular heat and cool position with auto/ on fan switch just no wires to the outside unit?????
I have seen I think they are called Scott packs mounted high on the wall like this I have seen gas fire places same thing . This is the new age .
Reported here, Colarado has gone wirless with phone and Computer in one part .
Roy
Reply With Quote
  #10  
Old 12/10/06, 10:28 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,816
Dale Duffy .
Default Re: Outside condenser A/C no wires

Charley,

I find thermostat wire wrapped (hidden) in the insulation around the refrigerant line.
Reply With Quote
  #11  
Old 12/10/06, 10:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by dduffy
Charley,

I find thermostat wire wrapped (hidden) in the insulation around the refrigerant line.
Guys this unit had no 24 volt wires anywhere inside conduit, inside insulation or anywhere????
Reply With Quote
  #12  
Old 12/10/06, 10:36 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,816
Dale Duffy .
Default Re: Outside condenser A/C no wires

Charley,

Did you take the top/sides off the condenser and actually look inside?

If so, and no T wires, I don't know what to tell you.
Reply With Quote
  #13  
Old 12/10/06, 10:41 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 1,581
Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information
Default Re: Outside condenser A/C no wires

Was it like one I saw once?
The ice truck loads a big block of ice on a rack and a big fan blows across it towards the duct to the house. No thermostat needed, the size of the ice block is engineered to cool the house to the desired temperature.
Reply With Quote
  #14  
Old 12/10/06, 10:44 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information rcooke is very trusted source of information
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by bking
Was it like one I saw once?
The ice truck loads a big block of ice on a rack and a big fan blows across it towards the duct to the house. No thermostat needed, the size of the ice block is engineered to cool the house to the desired temperature.
Years ago they used to cut the Ice like that on Grenadier pond in the west end of Toronto .
That was for Bellewart Ice Company.

I used to be the guy on the lower end of the saw but could not stand the cold so looked for another job .
Roy
Reply With Quote
  #15  
Old 12/10/06, 10:59 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,447
Charley L. Bottger .
Default Re: Outside condenser A/C no wires

Quote:
Originally Posted by dduffy
Charley,

Did you take the top/sides off the condenser and actually look inside?

If so, and no T wires, I don't know what to tell you.
Sorry guys I have been messing with your minds.
They call me the tricksters I get answers.

An A/C unit that has no 24 wires to the outside unit is called a pump down unit and I do occasional see some in use.
There is a liquid line solenoid valve located on the exterior side of the furnace A-coil that the Yellow wire or cooling wire activates this valve when the stat calls for cooling this valve is a normally closed valve that opens when the stat calls for cooling.
In turn the outside condensing unit has a 220-volt contactor instead of a 24 volt contactor. One leg of the 220 volts is routed thru a low pressure switch back to the contactor.
This low pressure switch is normally open. When the solenoid valve is activated for cooling and opens it allows pressure back to the low pressure switch that closes thus starts the compressor. No low voltage wires required at the unit.
The thermostat operates the solenoid valve and the low pressure switch operates the compressor.
</IMG></IMG>
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Wires ran from lugs to auxilary panels Kevin Luce Electrical 7 9/20/07 10:24 AM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 8 9/9/07 8:02 PM
Loose/terminated wires in main panel csteele Electrical 12 7/19/07 5:39 PM
Ground Wires Inside a Panel mveitenhans Electrical 13 10/29/06 12:39 PM
Painted service wires hcavin Electrical 1 9/27/06 1:47 PM


All times are GMT -4. The time now is 10:58 PM.


Popular Sections