Default Re: Oxidation on Copper Gas Line

Joe, it could be type k which is ok or it could be other types.
type k has a thicker wall.

Its just not visible on most inspections and I would not be concerned with it really because it could be type k.

All types of copper is ok for propane.

I would report the oxidation as being present.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #17  
Old 4/9/06, 4:12 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Oxidation on Copper Gas Line

Quote:
Originally Posted by jfunderburk
Please tell me exactly why that is?
As I stated earlier...

Quote:
You won't see that in my area. 1/4 inch copper tubing (with no joints) is the maximum I see in Massachusetts.
In the hundreds of inspections I've performed, I've never ran into 3/4 copper supply line (esp. with joints) in Massachusetts. We use 1/4 copper tubing (no joints) and black steel.

SC may have different codes relating to gas supply line material.

I simply do not like what I see...
Reply With Quote
  #18  
Old 4/9/06, 9:33 PM
wcottrell wcottrell is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Patrick Springs, VA
Posts: 38
Default Re: Oxidation on Copper Gas Line

Joe,
It appears that the line was soldered as opposed to being brazed. I would call for evaluation as well. I beleive SC requires this line to be brazed for gas service. The 3/4 inch line might be required for the proper gas flow depending on the size and BTUs of the water heater.
Regards Bill
Reply With Quote
  #19  
Old 4/10/06, 12:49 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Oxidation on Copper Gas Line

If this is a gas supply line? (Gas or Water?) 3/4" is too big for residential needs!?

1. Copper can be used in LP.
2. Fitting is not needed. Pipe can be bent.
3. Silver brazing is required.
4. Fittings/splices should not be made in an enclosed space.

The oxide your are asking about is flux as posted above.
Reply With Quote
  #20  
Old 4/10/06, 4:06 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Oxidation on Copper Gas Line

http://www.copper.org/applications/f...-fittings.html


Quote:
NEW YORK - The 2000 Editions of the Uniform Plumbing Code and Uniform Mechanical Code contain provisions for the use of copper tube in natural gas-distribution systems. The revised codes reflect acceptance of copper tube and fittings for gas-distribution applications by the International Association of Plumbing & Mechanical Officials (IAPMO) after review during the code body's annual Education and Business Conference last August


Quote:
Gas installation regulations aim to avoid joints within walls or other inaccessible places where undetected leakage might cause an accumulation of gas. However, joints in these locations may sometimes be unavoidable. Since mechanical joints are prohibited in inaccessible locations, brazed joints should be used, provided they are approved by the authority having jurisdiction. These joints should be inspected and tested prior to enclosure to ensure a leak-free system. Minimization of joints, especially in inaccessible areas, can be easily accomplished using long, flexible lengths of copper tube.

http://www.copper.org/about/pressrel...echanical.html


The oxidation is caused by oxygen, the situation has been exacerbated by improper cleaning of the joints after Brazing.

Last edited by bkelly2; 4/10/06 at 4:11 PM..
Reply With Quote
  #21  
Old 4/10/06, 5:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Oxidation on Copper Gas Line

I don't know how ya'll can tell if it's 3/4 by looking at a picture that has no scale to it. I don't remember it being that big.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #22  
Old 4/10/06, 5:14 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Oxidation on Copper Gas Line

Quote:
Originally Posted by jfunderburk
I don't know how ya'll can tell if it's 3/4 by looking at a picture that has no scale to it. I don't remember it being that big.
They can't with out a scale of reference Joe.

I would have recomended protection from physical damage though, depending on the location of course.
Reply With Quote
  #23  
Old 4/10/06, 10:28 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Oxidation on Copper Gas Line

Baseboard?
PVC pipe 1 1/2, the next size down is 3/4.
Reference? I saw reference.
Reply With Quote
  #24  
Old 4/10/06, 10:41 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Oxidation on Copper Gas Line

judging by the baseboard molding (3 1/2 base with 1/2 cove) i'd say the pipe IS 1/2". fairly confident with that one.
Reply With Quote
  #25  
Old 4/10/06, 11:09 PM
lfoster's Avatar
lfoster lfoster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Oxidation on Copper Gas Line

Natural gas causes the copper tubing to deteriorate. When I smelled gas (for a while), located it at the water heater supply line - copper tubing appx. 30 years old. It was eaten away and easily fell out of the screw connector when it was moved.
Linda
Reply With Quote
  #26  
Old 4/11/06, 1:54 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Oxidation on Copper Gas Line

Quote:
Originally Posted by lfoster
Natural gas causes the copper tubing to deteriorate.
Then why is it allowed? Is there really some scientific evidence that gas causes the metal to deteriorate? I'm not trying to be a wise guy...just trying to learn. As the code cited earlier in this thread shows, it is allowed.

Quote:
...copper tubing appx. 30 years old. It was eaten away...Linda
Lots of things fail at 30 years old. I necessarily wouldn't blame it on the type of metal used in the supply line, unless there is some proof that gas and copper don't mix.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #27  
Old 4/11/06, 7:13 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Oxidation on Copper Gas Line

Quote:
Originally Posted by jfunderburk
I don't know how ya'll can tell if it's 3/4 by looking at a picture that has no scale to it. I don't remember it being that big.
I'll put money on it, that that copper piping is 3/4".
Reply With Quote
  #28  
Old 4/11/06, 4:18 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Question Re: Oxidation on Copper Gas Line

Did you check with your local gas company regarding what there standards are? Maybe a no no with respect to install and or sizing / material.


This could be a another "Saturday" project.. Hmm "Lets" solder this puppy while there is gas in it..."

A side note: I wonder what is the pressure is too.. Figure gas under pressure passing a restriction will get very cold at that point and condensation will occur when ambient exterior temperatures are warmer. Hence sweating will occur.. Improper cleaning after soldering will leave compounds that lead to oxidation and promote further problems.
Reply With Quote
  #29  
Old 4/11/06, 11:08 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Oxidation on Copper Gas Line

Quote:
Originally Posted by dvalley
I'll put money on it, that that copper piping is 3/4".
your geographicly close enough to square up on this one dave, although we may never know for sure, but i'd bet that the p.v.c. it runs threw is 3/4 and the pipe is 1/2''. what do you say,??? do we have a bet??
Reply With Quote
  #30  
Old 4/12/06, 9:12 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Oxidation on Copper Gas Line

By sizing it with the baseboard, I'd say 1/2" copper too.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM
Copper Line Fitting Richard Seay Plumbing Inspections 2 3/27/07 8:25 AM
Bathroom Shut-off Valves - Mineral deposits - Do you note them as leaking in reports? jwatts1 Plumbing Inspections 8 7/29/06 12:50 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 8:59 AM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Inspection Services & Additional Topics 2 2/18/06 12:22 PM


All times are GMT -4. The time now is 11:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts