Default Painting the Gas Log Set vent termination

I don't think it's smart.
It says "Caution gets HOT" right on it, but I could not find it forbidden in the manufacturers installation instructions.

Thoughts?...
Attached Images
File Type: jpg 30 Nov 07 089.jpg (38.3 KB, 36 views)



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #2  
Old 11/30/07, 10:09 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,120
Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information Jack L. Gilleland is very trusted source of information
Default Re: Painting the Gas Log Set vent termination

I saw this same situation 3 days ago. It was done by the building contractor. Haven't done the final for the new construction yet. Could use some input also.

Thanks



Those that have never made a mistake have never done anything.

Jack Gilleland
Home Inspection Services
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #3  
Old 11/30/07, 10:17 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Painting the Gas Log Set vent termination

It's new construction with a CO issued yesterday... supposed to close Monday...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #4  
Old 11/30/07, 10:59 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 6,452
Robert E. Elliott .
Default Re: Painting the Gas Log Set vent termination

There are some high temp paints out there.
I am guessing this was not one of them.
Reply With Quote
  #5  
Old 12/1/07, 1:37 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,361
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: Painting the Gas Log Set vent termination

That would be a baked on finish.
Reply With Quote
  #6  
Old 12/1/07, 8:54 AM
Mark Sylvester's Avatar
Mark Sylvester Mark Sylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 667
Mark Sylvester is often very helpful Mark Sylvester is often very helpful Mark Sylvester is often very helpful
Send a message via AIM to msylvester
Default Re: Painting the Gas Log Set vent termination

I at least have brought it to my clients attention and let them decide what action they would take. As Bob stated there are hi-temp paints.
I will say that the ones I find painted usually get replaced, unless the builder can provide info that the paint is OK for high temp and that the manufacturer allows it.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #7  
Old 12/1/07, 10:31 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Painting the Gas Log Set vent termination

"No definitive answer on painting the vent termination for the gas log set (the manufacturers installation instructions did not say Not
to). I am unable to determine if the paint is an acceptable High Temperature paint which would be suitable for this application. Monitor for any problems while in use as it does get hot"







Sorry, Had to get the report out last night, but this is what I ended up putting in it....












- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #8  
Old 12/1/07, 11:39 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 5,571
William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information William J. Decker is very trusted source of information
Default Re: Painting the Gas Log Set vent termination

Quote:
Originally Posted by msylvester
I at least have brought it to my clients attention and let them decide what action they would take. As Bob stated there are hi-temp paints.
I will say that the ones I find painted usually get replaced, unless the builder can provide info that the paint is OK for high temp and that the manufacturer allows it.
Smart, Mark.

Put the ball back in their court. Have them prove (in writing!!!) that it is right. You have no idea what they did and, frankly, it is not your jib to prove of disprove their work. Make them PROVE it.

That's what I do. I put it in the report and recommend the lawyer (or Realtor, if you are in an area that doesn't use lawyers for closings) do the nagging of the builder.

That's why they get the big comissions.



Will Decker
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 12/2/07, 7:15 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,157
Barry Adair .
Default Re: Painting the Gas Log Set vent termination

Why didn't the inspector fire up this unit during the inspection?

Paint bubbles, peels, scorches, catches the house on fire...FAILED UNDER NORMAL OPERATION

No more ifs, ands or buts...definative info and no further hypothesis or questions. jmo




badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
  #10  
Old 12/2/07, 9:07 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 984
Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted Michael W. Gault is well trusted
Default Re: Painting the Gas Log Set vent termination

Quote:
Originally Posted by badair
Why didn't the inspector fire up this unit during the inspection?

Paint bubbles, peels, scorches, catches the house on fire...FAILED UNDER NORMAL OPERATION

No more ifs, ands or buts...definative info and no further hypothesis or questions. jmo
Like I said, New Construction with a day old CO...

Log Sets are not normally hooked up (though they are provided) by the builder... They let an independent company do the connections and testing.
Attached Images
File Type: jpg 30 Nov 07 121.jpg (37.2 KB, 11 views)



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #11  
Old 12/2/07, 9:40 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,157
Barry Adair .
Default Re: Painting the Gas Log Set vent termination

Quote:
Originally Posted by mgault
Like I said, New Construction with a day old CO...

Log Sets are not normally hooked up (though they are provided) by the builder... They let an independent company do the connections and testing.
Around here the FP/gas logs would have to be finished/fully operational by most munis before calling for final and issuance of CO.

better get



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 6:22 PM
Vent termination thejnicki Plumbing 4 10/1/06 3:27 PM
Dryer Vent termination tneumann Misc. Discussion 8 3/24/06 7:39 PM
vent termination ? bmargiotti Plumbing 7 2/18/06 10:42 AM


All times are GMT -4. The time now is 12:29 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics