Default Partial cold weather A/C check

For those that want to put some extra effort into a cold weather inspection or just use this information for home troubleshooting.

Here is a procedure that will indicate the refrigerant level is not below the "low pressure switch" setting (which indicates very low refrigerant) and some basic control voltage to the condensor contactor is working without actually running the compressor.

It takes two people to do this in most cases:

1. Pull the 220V disconnect at the condensor unit and put your ear near the unit, 2 feet away is close enough.

2. Have someone adjust the t-stat to call for cooling.

3. If you hear the sound of a large contactor energizing then you know the control circuit is allowing the compressor to receive voltage which it will not allow if the refrigerant is really low.

4. If you don't hear the sound, don't assume it is low on refrigerant, it could be many other things wrong, including two or more problems. Now you have a very good reason to recommend a service call on the unit.

5. Set the t-stat back to where you found it (heat mode)

6. Re-install or reset the disconnect.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 2/27/08, 12:41 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Partial cold weather A/C check

Quote:
Originally Posted by bking
For those that want to put some extra effort into a cold weather inspection or just use this information for home troubleshooting.

Here is a procedure that will indicate the refrigerant level is not below the "low pressure switch" setting (which indicates very low refrigerant) and some basic control voltage to the condensor contactor is working without actually running the compressor.

It takes two people to do this in most cases:

1. Pull the 220V disconnect at the condensor unit and put your ear near the unit, 2 feet away is close enough.

2. Have someone adjust the t-stat to call for cooling.

3. If you hear the sound of a large contactor energizing then you know the control circuit is allowing the compressor to receive voltage which it will not allow if the refrigerant is really low.

4. If you don't hear the sound, don't assume it is low on refrigerant, it could be many other things wrong, including two or more problems. Now you have a very good reason to recommend a service call on the unit.

5. Set the t-stat back to where you found it (heat mode)

6. Re-install or reset the disconnect.
Bruce all that will tell you is that the thermostat is indeed pulling in the 24 volt contactor to the closed position provided you have shut down the line voltage.

The low pressure switch does not determine the level of freon as in a liquid state, the LP switch is located on the suction side of the compressor and senses vapor pressure return to the compressor when it is in operation. You could in essences have one lb of freon in a system that requires five for proper operation and still have a closed LP switch in the off position of the unit but would open within the first few seconds that the compressor started to operate.

Your process for checking the contactor is fine but you need to re-think the LP switch. BTW usually only high end units and heat pumps have LP switches installed from the factory.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 8:22 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 11:43 PM