Ok. Guys I am done picking apples for the next four hours. and am going to post two questions graciously supplied by Robert O'Connor and have his answers lurking in the wings
Here Goes. About how many feet of a main supply duct coming off of the furnace plenum should there typically be before any individual supply take-offs are cut in. Should there be any supply take offs in the end head of a furnace supply plenum. |
|
#2
|
||||
|
||||
|
Quote:
Answers posted as/per Robert O,Connor At least 2 feet of main supply plenum without a supply take off is recommended by most MFG. About 3 to 4 feet before a take off is considered a better practice. It is considered as poor practice to have a take off cut into the head of a main supply plenum. I consider this as a defect if installed without a damper and a accessible damper handle to balance the system. |
|
#3
|
||||
|
||||
|
ACCA Manual D requires 12" (or is it 18") at the end of a supply plenum to have no takeoffs.
ACCA - Air Conditioning Contractors Association Kentucky makes that and Manual J part of the building code. -- Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice! |
|
#4
|
||||
|
||||
|
Quote:
Robert will be back on board Monday he can discuss ACCA with you. </IMG> |
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
||||
|
||||
|
Quote:
However plenum head take-offs are found on systems. I consider it at least poor practice, and a defect if there are no accessible dampers with handles to balance the system. I am also very mindful of the flow at registers (feel the air flow with my hand) when I see that, as the registers from the head take-offs are often over supplied (and thus under supplying other registers). JMO & 2-nickels ... Robert O'Connor, PE Eagle Engineering & Inspections Adjunct Professor NACHI Education Committee www.reporthost.com/eagleengineering I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 12/18/06 at 3:10 PM. |
|
#7
|
||||
|
||||
|
Quote:
I have another question for you in particular. I make it a rule to always observe the amount of drops that are attached to a specific trunk line in the attic I do not measure CFM at the registers as an HI. The amount of 8 inch drops attached to a 12 inch trunk line gives me a ball park idea as to the CFM distribution that I will be having when I operate the systems. I prefer 3 drops as excellent CFM, 4 drops as exceptable CFM, 5 drops un-exceptable. I do realize that CFM is calculated by the size and the length of the various ducts but this is not within the scope of a HI. What would your take on this be? </IMG> |
|
#8
|
||||
|
||||
|
Quote:
OK...I'll play your game... What kind of a nut does pick apples in December?? |
|
#9
|
||||
|
||||
|
Quote:
I Raise show horses also and had been cleaning stalls right before I made this post and was thinking you know hay in apples out </IMG></IMG></IMG></IMG></IMG></IMG></IMG></IMG> |
|
#10
|
||||
|
||||
|
Totally forgot about that...
Having been raised in Northern California (and working around horses) I learned there were apples...and then there were apples. |
|
#11
|
||||
|
||||
|
Quote:
Another type of system is called an "Extended Plenum System", where there is a constant size main supply plenum up to about 16 feet long on either side of the air handler (some say 24 feet max), and the system is then balanced with damper handles at the take-off's. In my opinion the Extended Plenum System is an inferior system, but is used by some who don't really know how to calculate out the ductwork. When I see that I am very mindful of balanced register flow, which can easily be roughly checked by just holding you hand up to the registers to get a comparison. It can work fairly well if balanced right (rare), as registers near the end tend to be over-supplied or noisy. Also, some installers make the mistake of locating equipment on one side of a house with a long extended plenum ... almost always problems with these systems in my experience ... and in fact some registers near the equipment can actually be drawing air into the ducts ... And last, and least of all, is the "Radial System" with a very short supply plenum and flex everywhere. Some installers call it a "Spider" system. It's a sign of a real cheap system (lower end builder special) that doesn't work very well in my experience. JMO & 2-nickels ... Robert O'Connor, PE Eagle Engineering & Inspections Adjunct Professor NACHI Education Committee www.reporthost.com/eagleengineering I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 12/20/06 at 12:49 PM. |
![]() |