Yesterday I inspected a house built in in 2005 that had 2900 sq ft, but was much larger in volume than a typical 2900 sq ft house, because about 1/3 the 1st floor area was taken up by a great room.

The furnace was a Carrier ultra-high efficiency model with an output of 112,000 BTU and 3/4 hp motor, and the AC condenser was a Carrier 4 ton unit, which was not run due to cold weather. The latter seemed a bit under optimum size to me.

The furnace did appear to heat the house well enough throughout, and did not have to run for too long in my judgment to do so for an outside temperature about 32 F / 0 C. But the flow at many registers was barely detectable, especially in the 2nd floor and basement, though all were fully open.

The rating / data plates for the units are attached. The AC rating plate was already just about worn off, so I had to really push the contrast to make it readable.

Thoughts, HVAC people?
Attached Thumbnails
poor-air-flow-undersized-system-20080209-furnace-data.jpg   poor-air-flow-undersized-system-20080209-ac-data.jpg  
Reply With Quote
  #2  
Old 2/10/08, 8:05 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Poor air flow -- undersized system?

Frank,

It appears to be adequately sized, but it's not our job to determine the adeqacy of heating and A/C systems.

Quote:
II. The inspector is not required to:
Quote:

C. Determine the uniformity, temperature, flow, balance, distribution, size, capacity, BTU, or supply adequacy of the heating system.




I've got a calculation guide you can give to your clients.....HERE
Reply With Quote
  #3  
Old 2/10/08, 8:20 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Poor air flow -- undersized system?

Thanks, David. I will forward that along to my client.

It often appears that higher efficiency systems tend not to crank out hot air as noticeably as the older, low efficiency units. Is this just "in my mind" or is there some logical explanation for such a perception, such as slower air movement in the heat exchanger being necessary to transfer the radiated heat more effectively?
Reply With Quote
  #4  
Old 2/10/08, 8:28 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Poor air flow -- undersized system?

Quote:
Originally Posted by fbartlo
Thanks, David. I will forward that along to my client.

It often appears that higher efficiency systems tend not to crank out hot air as noticeably as the older, low efficiency units. Is this just "in my mind" or is there some logical explanation for such a perception, such as slower air movement in the heat exchanger being necessary to transfer the radiated heat more effectively?
There too much to consider when sizing a heating system...

Window sizes and quality
Insulation R-Values in walls and ceilings
Seals in/around all wall penetrations
Distance from furnace to registers
Insulated supply ducts
Sizing of supply ducts.
Return air
ETC, etc, etc.....
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 6:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts