Default Poor line sizing?

2008 goodman unit. They must have left the old line set, but figured I would get some feedback about the line sizing..

I wrote it up but whats your opinion??
Attached Thumbnails
poor-line-sizing-1.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/25/11, 9:43 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Poor line sizing?

I would refer it Sean . It should be the same size. CYA



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #3  
Old 1/25/11, 11:01 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Poor line sizing?

Why not tell tell it like it is the MFG requires the same size as the outlet of the unit can not be reduced as it reduces the efficiency of the unit by as much as a 1/2 ton going from 3/8 liquid line to a 1/4 inch



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 1/26/11, 6:41 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Poor line sizing?

See Charley,
I was paying attention.
ON top of the line, it was a 2 1/2 ton for a 2200 sf heated space.
40amp breaker and safety fuses for a max 20 on the compressor, and no drip pan or switch installed under the unit.

I just wrote up that both the sizing and the line set may not be sized properlyand should be evaluated. . The damn thing didn't work anyway so it will have to be looked at to begin with.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #5  
Old 1/26/11, 7:06 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Poor line sizing?

For one reason Charley HI are not refrigeration mechanics . He did very well noticing the the line set. Good catch Sean .



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 1/26/11, 8:24 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Poor line sizing?

Quote:
Originally Posted by wwilson3 View Post
For one reason Charley HI are not refrigeration mechanics . He did very well noticing the the line set. Good catch Sean .
Don't have to be a mechanic just have to be able to use your eyes as much as I have preached that very item over the years. WEll Done Sean



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 1/26/11, 12:18 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Poor line sizing?

Yes Charley your post are great, I Meant most would not know to state the lost of tonnage . It was a good catch by the lad, I have to keep a Eye on this guy. LOL



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #8  
Old 1/26/11, 1:31 PM
Rick Strand's Avatar
Rick Strand Rick Strand is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Calgary, Alberta, Canada
Posts: 266
Default Re: Poor line sizing?

Great post Sean, this is the kind of stuff we can all learn from!



Rick Strand, CPI
CAHPI Associate
Strand Home Inspections Inc.
Calgary, Alberta, Canada
Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
Reply With Quote
  #9  
Old 1/26/11, 2:00 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Poor line sizing?

Quote:
Originally Posted by wwilson3 View Post
Yes Charley your post are great, I Meant most would not know to state the lost of tonnage . It was a good catch by the lad, I have to keep a Eye on this guy. LOL
Yipper be careful or you will be carrying his tools



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 1/26/11, 2:15 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Poor line sizing?

Okay, I am not disputing whether this should be called out or not…

However, I am not seeing the same thing in this picture (which may not be accurate anyway) as the rest of you.

If we start at the top right of the photograph we see what appears to be a 3/8 inch line. When we come out of the tape we see a reduced line size. It goes back into a 3/8 inch line.

The line going into the unit at the flair nut does not appear to be 3/8. I think under the next taped area, it is reduced again.

Don't be surprised if someone gives you some flak on this one. If so, just let it go.

There are calculations to determine line set size beyond what the equipment outlet size happens to be.

You can have an inlet pipe smaller than 3/8 of an inch but are required to install 3/8 inch refrigerant line from the condensing unit to the air handler because of certain circumstances.

You cannot arbitrarily oversize the line because it can be critical to have too much refrigerant in the system. Just as it is critical for it to be too small.

There are numerous adverse effects that may occur from excessive refrigerant. Air conditioners equalize in the off mode. Excessive refrigerant in the system they actually cause flood back to the condensing unit and when the compressor comes on, it will wash out the oil and the compressor.

Liquid refrigerant may end up in the suction line, and if the line is short you may slug the compressor and break something.

If you have a long line set and a high vertical rise, your compressor must work harder.

If your condenser is above your evaporator (not quite as likely in residential, but it does happen frequently) you may overload your compressor on start up.

Additional start capacitors and potential relays may be required. Solenoid valves may need to be installed.…

Another issue is that when we downsize the line and then we upsize the line. Changes in volume may cause a "change of state" of the refrigerant. It may flash off because of the volume differential which equates to pressure differential.

That small section of refrigerant line may actually become the metering device which will cause refrigeration effects to occur outside of the evaporator coil. This is what causes capacity reduction.

There are a lot of considerations. Let the powers that be figure it out.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 1/26/11, 3:29 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Poor line sizing?

All I see is a 3/8 flared line brazed into a 1/4 inch that appears to be the original I see this done occasionally here and it is not allowed by the MFG to decrease the outlet size of the unit. I make those calls and let the contractor dispute if he wants to. One phone call to the MFG is all it takes



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 1/26/11, 8:38 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Poor line sizing?

Quote:
Originally Posted by dandersen View Post
There are a lot of considerations. Let the powers that be figure it out.
I did just that. The unit did not even begin to work for me so it had to be looked at period. I basicaly said that the line and the sizing may not be correct and it could be evaluated when the unit is serviced.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sizing a Service- Weakest Link Method pabernathy Electrical Inspections 7 6/13/10 9:10 AM
Water Heater Sizing charper Plumbing Inspections 13 7/10/07 6:19 PM
Sizing & Neutral Question? thejnicki Electrical Inspections 18 2/15/07 7:00 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM


All times are GMT -4. The time now is 10:32 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts