What do you see wrong with this duct install?????
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. Last edited by cbottger; 5/13/08 at 10:15 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#3
|
||||
|
||||
|
Quote:
Specifically speaking, what is you are looking at in the pictures that leads you to say that? Is it the white insulation visible on the large duct by hanger? Or are you looking at something else? |
|
#4
|
|||
|
|||
|
Outstide of an odd installation technique, I dont see anything wrong.
|
|
#5
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#6
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#7
|
||||
|
||||
|
Not properly supported and the duct laying against the insulation is not straight enough.
|
|
#8
|
|||
|
|||
|
partially supported by a 2X4
|
|
#9
|
||||
|
||||
|
Please Note:
pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Improper duct support. Metal (plumbers tape)
|
|
#10
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
From the IMC:
603.10 Supports. Ducts shall be supported with approved hangers at intervals not exceeding 10 feet (3048 mm) or by other approved duct support systems designed in accordance with the International Building Code. Flexible and other fac - tory-made ducts shall be supported in accordance with the manufacturer’s installation instructions. |
|
#11
|
||||
|
||||
|
Charley,
Is the large trunk line metal snap lock wrapped in insulation? First thing I noticed is; why the hell did they put it so high up into the attic into the hotter area of attic? Next thing I see is it doesn't look like professionally constructed connections where the flex joins the collars; no zip ties, hard cast or for that matter even duct (code) tape. Some of the flex connections are too close together (cause a drop in pressure along the trunk). just to name a few things. Doug Edwards, CMI |
|
#12
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#13
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#14
|
||||
|
||||
|
Quote:
The trunk line is snap lock and yes they did not use wye connections on the two bottom connections and the two bottom connections should come off of the side not the bottom. The ducts were installed in the hottest part of the attic because a upflow was installed in the up right position with the supply plenum on the top. should have used a horizontal or a downflow so the duct could be installed at a lower level. They did use zip ties they were under the insulation as they should be. I did not have a a problem with the spacing of the drops. I did not write up any corrective action on this just very poor craftmanship Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#15
|
|||
|
|||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Thanks Nick I just hate it when I'm wrong | cbottger | Misc. Discussion | 0 | 6/9/07 2:01 PM |
| see anything wrong | jmaisano | Electrical | 16 | 10/31/06 5:23 PM |
| What's Wrong Here? | jtedesco1 | HVAC | 20 | 6/29/06 6:50 PM |
| Anything Wrong Here? | scosta | HVAC | 12 | 6/29/06 9:06 AM |