Default Pretty--But---Wrong

What do you see wrong with this duct install?????



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.

Last edited by cbottger; 5/13/08 at 10:15 PM..
Reply With Quote
  #2  
Old 9/22/07, 4:05 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,527
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by cbottger
What do you see wrong with this duct install?????
Duct vapour barrier not sealed. Can lead to condensation in insulation when A/C is running......especially in very warm/hot humid weather.
Reply With Quote
  #3  
Old 9/22/07, 4:17 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 4,611
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by Brian A. MacNeish
Duct vapour barrier not sealed. Can lead to condensation in insulation when A/C is running......especially in very warm/hot humid weather.
Brian,

Specifically speaking, what is you are looking at in the pictures that leads you to say that? Is it the white insulation visible on the large duct by hanger? Or are you looking at something else?
Reply With Quote
  #4  
Old 9/22/07, 4:25 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,896
Default Re: Pretty--But---Wrong

Outstide of an odd installation technique, I dont see anything wrong.
Reply With Quote
  #5  
Old 9/22/07, 7:24 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by wsiegel
Outstide of an odd installation technique, I dont see anything wrong.
I take it you have never professionally installed duct



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 9/22/07, 7:27 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by Brian A. MacNeish
Duct vapour barrier not sealed. Can lead to condensation in insulation when A/C is running......especially in very warm/hot humid weather.
Plenty of overlap at the seams no condensation going on here.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #7  
Old 9/22/07, 7:44 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 298
Default Re: Pretty--But---Wrong

Not properly supported and the duct laying against the insulation is not straight enough.
Reply With Quote
  #8  
Old 9/22/07, 7:46 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Nashua, NH
Posts: 1,353
Default Re: Pretty--But---Wrong

partially supported by a 2X4
Reply With Quote
  #9  
Old 9/22/07, 8:09 PM
pdoane's Avatar
pdoane pdoane is offline
Active Poster
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,041
Please Note: pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pretty--But---Wrong

Improper duct support. Metal (plumbers tape)
Reply With Quote
  #10  
Old 9/22/07, 8:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Unmoderated Guest
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pretty--But---Wrong

From the IMC:
603.10 Supports. Ducts shall be supported with approved
hangers at intervals not exceeding 10 feet (3048 mm) or by
other approved duct support systems designed in accordance
with the International Building Code. Flexible and other fac -
tory-made ducts shall be supported in accordance with the
manufacturer’s installation instructions.
Reply With Quote
  #11  
Old 9/22/07, 8:24 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: FL panhandle
Posts: 3,744
Default Re: Pretty--But---Wrong

Charley,
Is the large trunk line metal snap lock wrapped in insulation? First thing I noticed is; why the hell did they put it so high up into the attic into the hotter area of attic? Next thing I see is it doesn't look like professionally constructed connections where the flex joins the collars; no zip ties, hard cast or for that matter even duct (code) tape. Some of the flex connections are too close together (cause a drop in pressure along the trunk). just to name a few things.



Doug Edwards, CMI







Reply With Quote
  #12  
Old 9/22/07, 8:26 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by pdoane
Improper duct support. Metal (plumbers tape)
The main trunk line was metal and plumbers strapping is the excepted method for metal duct, for flex duct its not allowed.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #13  
Old 9/22/07, 8:33 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by gheller
Not properly supported and the duct laying against the insulation is not straight enough.
I did not have a problem with any of the supports and as for the small turn in the return air duct lying down on the attic insulation not a problem with me.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #14  
Old 9/22/07, 8:53 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by dedwards
Charley,
Is the large trunk line metal snap lock wrapped in insulation? First thing I noticed is; why the hell did they put it so high up into the attic into the hotter area of attic? Next thing I see is it doesn't look like professionally constructed connections where the flex joins the collars; no zip ties, hard cast or for that matter even duct (code) tape. Some of the flex connections are too close together (cause a drop in pressure along the trunk). just to name a few things.
Master Chief now we are getting some where Thank you.

The trunk line is snap lock and yes they did not use wye connections on the two bottom connections and the two bottom connections should come off of the side not the bottom.

The ducts were installed in the hottest part of the attic because a upflow was installed in the up right position with the supply plenum on the top. should have used a horizontal or a downflow so the duct could be installed at a lower level.
They did use zip ties they were under the insulation as they should be. I did not have a a problem with the spacing of the drops.

I did not write up any corrective action on this just very poor craftmanship



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #15  
Old 9/22/07, 9:13 PM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 354
Default Re: Pretty--But---Wrong

Quote:
Originally Posted by cbottger
Master Chief now we are getting some where Thank you.

The trunk line is snap lock and yes they did not use wye connections on the two bottom connections and the two bottom connections should come off of the side not the bottom.

The ducts were installed in the hottest part of the attic because a upflow was installed in the up right position with the supply plenum on the top. should have used a horizontal or a downflow so the duct could be installed at a lower level.
They did use zip ties they were under the insulation as they should be. I did not have a a problem with the spacing of the drops.

I did not write up any corrective action on this just very poor craftmanship
For those of us who are not HVAC gurus, what is the functional problem with this installation?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thanks Nick I just hate it when I'm wrong cbottger Misc. Discussion 0 6/9/07 2:01 PM
see anything wrong jmaisano Electrical 16 10/31/06 5:23 PM
What's Wrong Here? jtedesco1 HVAC 20 6/29/06 6:50 PM
Anything Wrong Here? scosta HVAC 12 6/29/06 9:06 AM


All times are GMT -4. The time now is 8:06 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts