I found a basement installed oil tank with PVC fill and vent lines. The exterior lines are steel, but inside the basement they are PVC and poorly supported. I recommended replacement due to the location, poor supports and possibilities of spills if cracked or broken, especially during a delivery.
However, I can not find anything that says PVC cannot be used interior. I have found a reference to exterior oil fill and vent piping, but not interior. The use of PVC seems illogical to me, but does anyone know if it is allowed? Thanks, Fred Taken from:http://www.carpenterandsmith.com/oil_piping.html Piping materials All above ground piping should be iron or steel. Prior to a revision of NFPA 31 in 2001, copper and brass were also listed as acceptable piping materials, and installations completed prior to 2001 using copper or brass are considered to comply with the standards. Unfortunately, there have been a number of tanks incorrectly installed with plastic fill and vent pipes; plastic (including PVC) pipes are not suitable because they will burn, and (more important from our point of view) because the become brittle in cold weather and more likely to crack while tanks are being filled. NFPA standards do no specify materials for underground tanks, but they should resist corrosion and be strong enough so underground pipes are not collapsed or crimped by the pressure of the earth, frost, etc.
Last edited by fduemig; 3/23/08 at 1:25 PM.. Reason: Added Source |
|
#2
|
|||
|
|||
|
Fred
the IRC 2007, chapter 22,section M2202.1, piping shall consist of steel pipe,copper tubing or steel tubing conforming to ASTM A 539. Aluminium tubing shall not be used between the fuel oil tank & burner units. it does not mention plastic at all , hope this helps Dennis R.Goudreau D.R.G. Inspections LLC www.newhampshirehomeinspector.biz www.nhinfraredthermalinspections.com http://co.nachi.org/inachiawards |
|
#3
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#4
|
||||
|
||||
|
Hi! Fred;
I like the wire support, i'm with you Fred. Len |
|
#5
|
||||
|
||||
|
Thanks for the replies.
I can't believe PVC would be allowed either, however, I cannot find a reference that states plastic is not allowed at the interior for fill and vent lines. As far as I am concerned, it is a no-brainer as I would always recommend replacement. Fred |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Do you put polybutylene in the Summary? | jfunderburk | Plumbing Inspections | 41 | 4/5/12 6:43 AM |
| Bonding Piping 101....Good To Know ! | pabernathy | Electrical Inspections | 37 | 4/28/07 11:25 AM |
| Duct mastic on exhaust vent piping? | tsiegert | Inspecting HVAC Systems | 0 | 10/4/06 10:29 PM |