Old 3/23/08, 1:08 PM
Fred Duemig's Avatar
Fred Duemig Fred Duemig is offline
Default PVC Oil Fill & Vent Piping?
I found a basement installed oil tank with PVC fill and vent lines. The exterior lines are steel, but inside the basement they are PVC and poorly supported. I recommended replacement due to the location, poor supports and possibilities of spills if cracked or broken, especially during a delivery.
However, I can not find anything that says PVC cannot be used interior. I have found a reference to exterior oil fill and vent piping, but not interior. The use of PVC seems illogical to me, but does anyone know if it is allowed?
Thanks,
Fred
Taken from:http://www.carpenterandsmith.com/oil_piping.html
Piping materials
All above ground piping should be iron or steel. Prior to a revision of NFPA 31 in 2001, copper and brass were also listed as acceptable piping materials, and installations completed prior to 2001 using copper or brass are considered to comply with the standards. Unfortunately, there have been a number of tanks incorrectly installed with plastic fill and vent pipes; plastic (including PVC) pipes are not suitable because they will burn, and (more important from our point of view) because the become brittle in cold weather and more likely to crack while tanks are being filled. NFPA standards do no specify materials for underground tanks, but they should resist corrosion and be strong enough so underground pipes are not collapsed or crimped by the pressure of the earth, frost, etc.
Fred Duemig
Massapequa, NY
NACHI04032507
Old 3/23/08, 1:45 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
Default Re: PVC Oil Fill & Vent Piping?
Fred
the IRC 2007, chapter 22,section M2202.1, piping shall consist of steel pipe,copper tubing or steel tubing conforming to ASTM A 539. Aluminium tubing shall not be used between the fuel oil tank & burner units. it does not mention plastic at all , hope this helps
Old 3/24/08, 12:13 AM
Banned
Originally Posted by dgoudreau
Fred
Only wrought iron/steel/brass threaded supply and vent pipes for tank allowed in Canada. Tubing to burner from tank may be copper, brass, or steel.
Old 3/24/08, 11:08 AM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
Exclamation Re: PVC Oil Fill & Vent Piping?
Hi! Fred;
I like the wire support, i'm with you Fred.
Len
Old 3/25/08, 6:34 AM
Thanks for the replies.
I can't believe PVC would be allowed either, however, I cannot find a reference that states plastic is not allowed at the interior for fill and vent lines.
As far as I am concerned, it is a no-brainer as I would always recommend replacement.
Fred
Fred Duemig
Massapequa, NY
NACHI04032507
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Bonding Piping 101....Good To Know ! pabernathy Electrical Inspections 37 4/28/07 11:25 AM
Duct mastic on exhaust vent piping? tsiegert Inspecting HVAC Systems 0 10/4/06 10:29 PM