Default Question about a gas fireplace vent

I searched the archives, and found some good discussion, but not the answer to my question. I inspected a new construction home today, and the gas fireplace in the living room vented straight through the wall, out to a patio area. The vent is only a few feet off the ground, and a few feet from the living room windows. I only had it on for a short time, and the vent outside got extremely hot. My questions are, is this proper venting due to the safety hazard of the hot vent (ie. children touching it), will it damage the siding over time, and is there a CO2 danger with this thing venting that close to an interior window? I couldn't find installation directions on the Lenox website. Any input would be greatly appreciated, any diagrams or code reference would be even better!




http://www.nachi.org/forum/attachmen...1&d=1174361569








</IMG>
Attached Thumbnails
question-gas-fireplace-vent-quail-haven.jpg  
Reply With Quote
  #2  
Old 3/20/07, 1:15 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Question about a gas fireplace vent

Check this out Jeff.

http://lib.store.yahoo.net/lib/elitedeals/BGD33NR.pdf
Reply With Quote
  #3  
Old 3/20/07, 1:01 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: Question about a gas fireplace vent

Jeff,

I am unaware of any fireplace manufacturer that would allow such a small clearance to that side wall. It looks to be about 6" from combustibles (ouch).

Check with the manufcturer requirements as most of them will have installation guides to download.



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #4  
Old 3/20/07, 2:00 PM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about a gas fireplace vent

I finally found it! Lenox says the minimum clearance to a door or window that opens is 12 inches. Minimum clearance above grade, a deck, porch, etc. is 12 inches. That is what I was looking for. I think I will just point out to use caution when on the patio when the fireplace is operating, due to the hot vent. Looks like it was installed within recommended guidlines.
Reply With Quote
  #5  
Old 3/20/07, 3:19 PM
Douglas Cossar's Avatar
Douglas Cossar Douglas Cossar is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 1,228
Default Re: Question about a gas fireplace vent

I see that type of installation all the time- mostly newer homes.

I just advise the client as you said you did

ABC

Always be careful!

Cheers



Doug Cossar CMI, NHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #6  
Old 3/20/07, 5:21 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Question about a gas fireplace vent

Quote:
Originally Posted by jvogan
I finally found it! Lenox says the minimum clearance to a door or window that opens is 12 inches. Minimum clearance above grade, a deck, porch, etc. is 12 inches. That is what I was looking for. I think I will just point out to use caution when on the patio when the fireplace is operating, due to the hot vent. Looks like it was installed within recommended guidlines.
Some of the newer ones that I've seen have a metal shield stood off from the hot surface 1-2 inches to prevent burns. Sorry, I don't have a picture.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 3/20/07, 6:25 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: Question about a gas fireplace vent

Are there any restrictions regarding that side wall, especially since it is an inside corner?



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #8  
Old 3/20/07, 6:47 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Question about a gas fireplace vent

Quote:
Originally Posted by srowe
Are there any restrictions regarding that side wall, especially since it is an inside corner?
There is some helpful information here, Shawn, that Brian posted in #2:
http://lib.store.yahoo.net/lib/elitedeals/BGD33NR.pdf

I believe a 2" clearance to a combustible inside corner was listed.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 3/20/07, 7:06 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Question about a gas fireplace vent

Quote:
Originally Posted by lkage
There is some helpful information here, Shawn, that Brian posted in #2:
http://lib.store.yahoo.net/lib/elitedeals/BGD33NR.pdf

I believe a 2" clearance to a combustible inside corner was listed.
It surprised me too, I would have thought the clearance to the siding was a concern, but according to the link it is OK.

Nice to know you still care Larry.
</IMG></IMG>
Reply With Quote
  #10  
Old 3/20/07, 7:36 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Question about a gas fireplace vent

Quote:
Originally Posted by bkelly2
Nice to know you still care Larry.
</IMG></IMG>
Thanks, I'm tryin', but could you move your chair up a little?
Attached Thumbnails
question-gas-fireplace-vent-cubicle_buddies.jpg  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 3/20/07 at 10:31 PM..
Reply With Quote
  #11  
Old 3/20/07, 8:46 PM
Mike Nelson's Avatar
Mike Nelson Mike Nelson is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Marion, NY
Posts: 94
Default Re: Question about a gas fireplace vent

A family died of Carbon Monoxide poisoning when the vent got clogged with snow, these have some problems, mostly a lack of understanding from the installer. The best thing to do is look under the unit in the control panel, and see if you can pick up info there, or do what everyone els has, and get the model number etc.. and go look it up. Dale Febbs class F.I.R.E. is a great class to get certified to inspect these and add $100.00 bucks to your inspections.



Mike Nelson CPI, CMI
NYS License # 16000005765


(Just because you understand how something is built, in no way prepares you for the innumerable insults a human being can heap upon a domicile)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Question re combustion air connected to vent jhawes Canadian Inspectors 11 12/4/06 9:24 PM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 9:57 PM