Here's a call that might be interesting, but i have questions for some of the more experienced inspectors.

I'm a full time fireman and a part time home inspector. Last night we had a call for the CO detector that was going off. The weather was just above freezing with rain/sleet, very humid, the high efficency furnace was only 2 years old. The intake/exhaust was located in the rear corner of the house with a 5 ft wood fence on one side and the AC compressor on the other, the intake was facing down about 12 inches from the ground and the exhaust facing out. We had a low reading with the meter about 10 ppm in the house, nothing to be that concerned about. I went out to the back yard to check the intake/exhaust when my meter jumped to 800 ppm at the back door, the air was heavy, there was a sour smell and my eyes started to burn, and depending on how the wind was blowing the meter reading would change.
The reading at the intake pipe was 500 ppm depending on the wind which meant that the furnace was drawing up contaminated air. I believe that the high humidity had a part in suspending the CO in the air. I came to realize that some of the exhaust in the house was coming from the back door.

The questions are:
1. Is this more common than I realize? Has anybody else ever heard of this?
2. Since the reading was soo low in the house can CO be reburned by the furnace since it was in the intake air?
3. Does the exhaust normally have a smell like this?
Reply With Quote
  #2  
Old 4/13/08, 5:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about high efficient furnace's

The exhaust from high efficiency furnaces is quite caustic.
Reply With Quote
  #3  
Old 4/13/08, 7:51 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question about high efficient furnace's

Quote:
Originally Posted by emendelson
Here's a call that might be interesting, but i have questions for some of the more experienced inspectors.

I'm a full time fireman and a part time home inspector. Last night we had a call for the CO detector that was going off. The weather was just above freezing with rain/sleet, very humid, the high efficency furnace was only 2 years old. The intake/exhaust was located in the rear corner of the house with a 5 ft wood fence on one side and the AC compressor on the other, the intake was facing down about 12 inches from the ground and the exhaust facing out. We had a low reading with the meter about 10 ppm in the house, nothing to be that concerned about. I went out to the back yard to check the intake/exhaust when my meter jumped to 800 ppm at the back door, the air was heavy, there was a sour smell and my eyes started to burn, and depending on how the wind was blowing the meter reading would change.
The reading at the intake pipe was 500 ppm depending on the wind which meant that the furnace was drawing up contaminated air. I believe that the high humidity had a part in suspending the CO in the air. I came to realize that some of the exhaust in the house was coming from the back door.

The questions are:
1. Is this more common than I realize? Has anybody else ever heard of this?
2. Since the reading was so low in the house can CO be reburned by the furnace since it was in the intake air?
3. Does the exhaust normally have a smell like this?

Not common at all I think you have a very unusual situation and would have to think the intake or exhaust should be separated more due to the pocket it is discharging into created by the fence and the A/C unit.

No the furnace cannot re-burn Co it requires oxygen 20% just like you and I breath. When you start deluding the combustion air with Co the burner flame will turn yellow. Co has no smell one of the reasons it is so dangerous as to what the the smell was I don't have a clue.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 4/13/08, 8:51 PM
Edward Mendelson Edward Mendelson is offline
InterNACHI Member
 
Join Date: Sep 2007
Location: Elmwood Park, IL
Posts: 11
Default Re: Question about high efficient furnace's

Thank you Mr. Bottger for the answer. I see that you're a Master HVAC mechanic and I was hoping to get a answer from someone with your experience.
Have you ever questioned the placement of the intake/exhaust on a inspection? It seems to me that the two are too close together under normal installations anyways.

Last edited by emendelson; 4/13/08 at 8:56 PM..
Reply With Quote
  #5  
Old 4/13/08, 9:26 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question about high efficient furnace's

Quote:
Originally Posted by emendelson
Thank you Mr. Bottger for the answer. I see that you're a Master HVAC mechanic and I was hoping to get a answer from someone with your experience.
Have you ever questioned the placement of the intake/exhaust on a inspection? It seems to me that the two are too close together under normal installations anyways.
The Name is Charley, Mr. Bottger passed in 1962

I personally have never had to call one out on an inspection but they are mostly vertical in my area very few go horizontal but yes I would make the call if necessary. Normally they are installed in a open area where prevailing winds can carry the Co away before it can mix with the intake. Just because the installing contractor has a HVAC license does not mean they always install correctly just depends on who is watching as in AHJ.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 10:33 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts