Default Radiant ceiling heat?

i am inspecting a house thursday with a heating system im not familiar with, maybe someone can help. apparently all there is is wiring sandwiched between 2 pieces of drywall. separate thermostat for each room (zone). seems like a very simple, maintenance free system, i just want to be more familiar when i get there.

anyone got any thoughts? what to look at? look for?

thanks in advance
Bob
Reply With Quote
  #2  
Old 3/20/07, 6:48 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Radiant ceiling heat?

Quote:
Originally Posted by bmargiotti
i am inspecting a house thursday with a heating system im not familiar with, maybe someone can help. apparently all there is is wiring sandwiched between 2 pieces of drywall. separate thermostat for each room (zone). seems like a very simple, maintenance free system, i just want to be more familiar when i get there.

anyone got any thoughts? what to look at? look for?

thanks in advance
Bob
Bob; Wished I could hep ya but I don't have a clue what you are referring to Radiant ceiling heat can come in numerous forms what are we talking here.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 3/20/07, 7:08 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Radiant ceiling heat?

Quote:
Originally Posted by bmargiotti
i am inspecting a house thursday with a heating system im not familiar with, maybe someone can help. apparently all there is is wiring sandwiched between 2 pieces of drywall. separate thermostat for each room (zone). seems like a very simple, maintenance free system, i just want to be more familiar when i get there.

anyone got any thoughts? what to look at? look for?

thanks in advance
Bob
Just above this letter is the word search put in (Radiant ceiling heat ) You shouget a lot of recent posts. If not take out the word ceiling and you can be lept busy for a while and learn a lot .
All the best
Roy Cooke
Reply With Quote
  #4  
Old 3/20/07, 8:35 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Radiant ceiling heat?

Ceiling cable heat is manufactured in lengths relating to output wattage. In is stapled to a layer of drywall working back and forth across the room parallel to ceiling joists making sure to leave joists open. A layer of drywall mud is then put on and immediately put a 2nd layer of drywall mover the first. The mud sandwiched in between the drywall needs to fill the voids completely or the cable may fail in an air pocket. It overheats without the heatsink effect of the mud.
It is a very even warmth when operating. It is very slow recovery when the room gets a quick chill. Watch out for homes with things hanging from the ceiling. It is repairable from above by cutting out the top layer of drywall butt splicing the break and carefully mudding in the repair. The wet mud can possibly be energized until it's dry. The hard part is finding the break. Tic Tracers work the best.
Reply With Quote
  #5  
Old 3/20/07, 8:38 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,852
Default Re: Radiant ceiling heat?

Electric radiant ceiling heat was a popular option in new homes from the mid-1950s to the late 1970s in the region. It is, like all electric resistance heat baseboards, fan-forced wall heaters, electric furnaces 100 percent efficient in converting electricity into heat.
Unfortunately, many radiant ceiling heating systems were installed when electricity was considerably less expensive than it is now. As the cost has risen, so has the cost to heat a home using any kind of electric resistance heat. Radiant ceiling heat is no exception.
Radiant systems produce a very comfortable form of heat, similar to being warmed by the sun on a cool day. As long as the radiant heat source can "see" an object in the room... occupants, the furniture, the floor and walls... it will transfer heat to it. Radiant heating systems, whether they are in the ceiling, a panel on the wall or in the floor, will heat the objects in the room, no
Electric radiant ceiling heat was a popular option in new homes from the mid-1950s to the late 1970s in the region. It is, like all electric resistance heat baseboards, fan-forced wall heaters, electric furnaces 100 percent efficient in converting electricity into heat.
Unfortunately, many radiant ceiling heating systems were installed when electricity was considerably less expensive than it is now. As the cost has risen, so has the cost to heat a home using any kind of electric resistance heat. Radiant ceiling heat is no exception.
Radiant systems produce a very comfortable form of heat, similar to being warmed by the sun on a cool day. As long as the radiant heat source can "see" an object in the room... occupants, the furniture, the floor and walls... it will transfer heat to it. Radiant heating systems, whether they are in the ceiling, a panel on the wall or in the floor, will heat the objects in the room, not just the air in the room. The air will get warmer the longer the heating system runs because as the objects in the room warm, they heat the surrounding air.
Warm air rises, but heat moves from warm to cool. So regardless of where the radiant heating system is located, as long as the objects in the room are cooler than the temperature of the radiator, they will receive heat. t just the air in the room. The air will get warmer the longer the heating system runs because as the objects in the room warm, they heat the surrounding air.
Warm air rises, but heat moves from warm to cool. So regardless of where the radiant heating system is located, as long as the objects in the room are cooler than the temperature of the radiator, they will receive heat.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #6  
Old 3/20/07, 8:50 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Radiant ceiling heat?

Here in central Indiana electric is now cheaper than heating w/gas.
Reply With Quote
  #7  
Old 3/20/07, 9:42 PM
Mike Nelson's Avatar
Mike Nelson Mike Nelson is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Marion, NY
Posts: 86
Default Re: Radiant ceiling heat?

As far as I know, most of these systems started malfunctioning relatively soon as heating systems go, and they were simply not very efficient generally as most of these systems were placed in the attic, between joists, with the insulation laid on top of them. I have some of these types for my students in the Rochester NY school, every house I have inspected with this type of system, has had them disconnected.



Mike Nelson CPI, CMI
NYS License # 16000005765


(Just because you understand how something is built, in no way prepares you for the innumerable insults a human being can heap upon a domicile)
Reply With Quote
  #8  
Old 3/21/07, 12:32 AM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Radiant ceiling heat?

I would imagine that an infra-red thermometer would be a must for verifying operation.

Jim King
Reply With Quote
  #9  
Old 3/21/07, 1:37 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Radiant ceiling heat?

Quote:
Originally Posted by jking2
I would imagine that an infra-red thermometer would be a must for verifying operation.
Or a laser thermometer.

Probably half of my condo inspections have radiant ceiling heating.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 3/21/07, 8:55 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Radiant ceiling heat?

Quote:
Originally Posted by rray
Or a laser thermometer.
Sorry Russel, the laser has nothing to do with measuring the temperature. it is only the targeting device of a laser equipped infrared thermometer.
Reply With Quote
  #11  
Old 3/21/07, 11:02 AM
hmiller's Avatar
hmiller hmiller is offline
Active Poster
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 668
Please Note: hmiller is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Radiant ceiling heat?

Quote:
Originally Posted by jking2
I would imagine that an infra-red thermometer would be a must for verifying operation.

Jim King
That is what I use. I take an initial reading, then crank up the heat and come back an check in an hour, or so. They are so slow to respond, but the thermometer can identify wether they are working or not, .....better than touching the ceiling to see if it is warm .....
Reply With Quote
  #12  
Old 3/21/07, 12:40 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Radiant ceiling heat?

Radiant heating is one of the first things I look for as I'm doing the layout of the house. If I find one, I get out my trusty laser thermometer (which I've had since day one), check the temperature of the ceiling with several sweeps, turn it on, and then check it again as one of the final items I do before leaving (turning off lights and locking doors and windows are the other items).

Those that are still working seem to work fine. However, a great supermajority of people disconnected theirs during the pseudo-power crisis manufactured by Enron and others in 2000-2001.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 3/21/07, 1:12 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Radiant ceiling heat?

Quote:
Originally Posted by mlarson
Sorry Russel, the laser has nothing to do with measuring the temperature. it is only the targeting device of a laser equipped infrared thermometer.
Long before I had my first infrared measuring device .
We used a spray bottle with water.
Heat dried shortly, stayed wet broken wire .
Did one the other day 40 years +or- and they all worked great.
They can be slow to heat the home if you have been away for some time .

Roy Cooke
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radiant Ceiling Heat hhull Interior 6 7/26/07 9:19 AM
Radiant Heat jharashinski HVAC 2 9/18/06 8:33 AM
Radiant Heat Transfer rmyers1 Structural 0 6/1/06 12:21 AM


All times are GMT -4. The time now is 5:27 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts