#1
|
||||
|
||||
|
This vent pipe is connected directly to the exterior of the building. Is the pipe material okay, or should it be smooth wall galvanized steel, stainless steel, or copper? The NFPA recommends this type of material over open topped broiler in residential applications. Does a stove fall under the category of open topped broiler?
774 Manor Road Staten Island, NY 10314 718-514-3393 |
| Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
The coil needs to be stretched according to proper practice of the flex hose. I would mention this and explain why there is a problem with the installation.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 Last edited by kwood; 12/29/11 at 12:15 PM.. |
|
#3
|
||||
|
||||
|
Quote:
SECTION M1503 RANGE HOODS M1503.1 General. Range hoods shall discharge to the outdoors through a single-wall duct. The duct serving the hood shall have a smooth interior surface, shall be air tight and shall be equipped with a backdraft damper. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building. Exception: Where installed in accordance with the manufacturer's installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors. M1503.2 Duct material. Single-wall ducts serving range hoods shall be constructed of galvanized steel, stainless steel or copper. Exception: Ducts for domestic kitchen cooking appliances equipped with down-draft exhaust systems shall be permitted to be constructed of schedule 40 PVC pipe provided that the installation complies with all of the following: 1. The duct shall be installed under a concrete slab poured on grade; and 2. The underfloor trench in which the duct is installed shall be completely backfilled with sand or gravel; and 3. The PVC duct shall extend not more than 1 inch (25 mm) above the indoor concrete floor surface; and 4. The PVC duct shall extend not more than 1 inch (25 mm) above grade outside of the building; and 5. The PVC ducts shall be solvent cemented. M1503.3 Kitchen exhaust rates. Where domestic kitchen cooking appliances are equipped with ducted range hoods or down-draft exhaust systems, the fans shall be sized in accordance with Section MI507.3. SECTION M1504 INSTALLATION OF MICROWAVE OVENS M1504.1 Installation of microwave oven over a cooking appliance. The installation of a listed and labeled cooking 335 EXHAUST SYSTEMS appliance or microwave oven over a listed and labeled cooking appliance shall conform to the terms of the upper appliance's listing and label and the manufacturer's installation instructions. The microwave oven shall conform to UL 923. SECTION M1505 OVERHEAD EXHAUST HOODS M1505.1 General. Domestic open-top broiler units shall be provided with a metal exhaust hood, not less than 28 gage, with 1/4 inch (6 mm) between the hood and the underside of combustible material or cabinets. A clearance of at least 24 inches (610 mm) shall be maintained between the cooking surface and the combustible material or cabinet. The hood shall be at least as wide as the broiler unit and shall extend over the entire unit. Such exhaust hood shall discharge to the outdoors and shall be equipped with a backdraft damper or other means to control infiltrationlexfiltration when not in operation. Broiler units incorporating an integral exhaust system, and listed and labeled for use without an exhaust hood, need not be provided with an exhaust hood. SECTION M1506 EXHAUST DUCTS M1506.1 Ducts. Where exhaust duct construction is not specified in this chapter, such construction shall comply with Chapter 16. ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#4
|
||||
|
||||
|
Barry, what code is it that you are referencing?
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#5
|
||||
|
||||
|
International Mechanical Code
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
John it does not matter what code it is we can only recommend what was OK at the time. I do not agree to leave it like this and once you mention it needs to be stretched we hope that the person they call will correct it properly. We can say it would be best if it was solid metal according to proper practice today. M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter 16. This is from the IRC 2006 also. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 Last edited by kwood; 12/29/11 at 8:56 AM.. |
|
#7
|
||||
|
||||
|
I reported it does not meet current standards and may not be as safe as current standard material and installation practice. Thanks for the help.
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#8
|
||||
|
||||
|
2012 irc it's basically the same in all previous versions
corrugated or accordion style is not smooth wall, "gunk" (inspectorspeak) will build up on the ridges/irregularities and become a combustion-fire hazard, therefore not allowed for this application ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#9
|
||||
|
||||
|
I should also mention that a manufacturer is making flex duct fire proof!
That being said Yes I would agree with the grease problem as Barry is pointed out. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 Last edited by kwood; 12/29/11 at 9:33 AM.. |
|
#10
|
||||
|
||||
|
Quote:
i'm not saying the code has to be quoted in a report but knowing what is not allowed is an automatic noted deficiency that requires removal and replacement with proper materials any less is just another logo certified soft report ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#11
|
||||
|
||||
|
looks like the jiffy pop exploded....
|
|
#12
|
||||
|
||||
|
I was referring to the design of the duct in question. It is designed to be stretched in the manufactured installation guidelines. I was not saying that this is acceptable.
M1503.1 General. The AHJ may allow it and this is sad but that is why we are in this business. This could be an outside wall side exhaust hood that presents no danger. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#13
|
||||
|
||||
|
Quote:
Slinkys are a grease trap. The client needs to be made aware of the potential hazard and that they can not be cleaned. My non CMI opinion of course. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
| Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
But then I'm not a CMI either! Look at what I've been missing all these years!? You have to have 26ga metal duct go through the garage wall to your HVAC equipment, but "foil" duct is OK directly above the stove... "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#15
|
||||
|
||||
|
I did not say it was OK!
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Pellet stove help | chellickson | General Inspection Discussion | 23 | 8/19/10 1:23 AM |
| Help - Polybutylene Pipes | Rick G | Plumbing Inspections | 39 | 2/12/09 8:16 AM |
| Outside Hot Water Heater With Vent Pipe Outside Kitchen Window | bwilliams | Plumbing Inspections | 4 | 12/8/08 11:10 PM |
| Direct vent WH with draft hood | dpeterson | Plumbing Inspections | 9 | 12/30/06 3:35 PM |
| Asbestos Vent Pipe??? | psmothers | Plumbing Inspections | 17 | 5/22/06 2:14 AM |