Default Range hood vent pipe material

This vent pipe is connected directly to the exterior of the building. Is the pipe material okay, or should it be smooth wall galvanized steel, stainless steel, or copper? The NFPA recommends this type of material over open topped broiler in residential applications. Does a stove fall under the category of open topped broiler?
Attached Thumbnails
range-hood-vent-pipe-material-img_5305.jpg   range-hood-vent-pipe-material-img_5304.jpg  




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/29/11, 7:49 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: Range hood vent pipe material

The coil needs to be stretched according to proper practice of the flex hose. I would mention this and explain why there is a problem with the installation.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 12/29/11 at 12:15 PM..
Reply With Quote
  #3  
Old 12/29/11, 8:28 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Range hood vent pipe material

Quote:
Originally Posted by kwood View Post
The coil needs to be strecthed according to proper practice. I would mention this and explain why there is a problem with the installation.
the problem is the duct material is not allowed with either exhaust system no matter how far you stretch it or how neatly it's installed

SECTION M1503
RANGE HOODS
M1503.1 General. Range hoods shall discharge to the outdoors
through a single-wall duct. The duct serving the hood
shall have a smooth interior surface, shall be air tight and shall
be equipped with a backdraft damper. Ducts serving range
hoods shall not terminate in an attic or crawl space or areas
inside the building.
Exception: Where installed in accordance with the manufacturer's
installation instructions, and where mechanical or
natural ventilation is otherwise provided, listed and labeled
ductless range hoods shall not be required to discharge to
the outdoors.
M1503.2 Duct material. Single-wall ducts serving range
hoods shall be constructed of galvanized steel, stainless steel or
copper.
Exception: Ducts for domestic kitchen cooking appliances
equipped with down-draft exhaust systems shall be permitted
to be constructed of schedule 40 PVC pipe provided that
the installation complies with all of the following:
1. The duct shall be installed under a concrete slab
poured on grade; and
2. The underfloor trench in which the duct is installed
shall be completely backfilled with sand or gravel; and
3. The PVC duct shall extend not more than 1 inch (25
mm) above the indoor concrete floor surface; and
4. The PVC duct shall extend not more than 1 inch (25
mm) above grade outside of the building; and
5. The PVC ducts shall be solvent cemented.
M1503.3 Kitchen exhaust rates. Where domestic kitchen
cooking appliances are equipped with ducted range hoods or
down-draft exhaust systems, the fans shall be sized in accordance
with Section MI507.3.
SECTION M1504
INSTALLATION OF MICROWAVE OVENS
M1504.1 Installation of microwave oven over a cooking
appliance. The installation of a listed and labeled cooking
335
EXHAUST SYSTEMS
appliance or microwave oven over a listed and labeled cooking
appliance shall conform to the terms of the upper appliance's
listing and label and the manufacturer's installation instructions.
The microwave oven shall conform to UL 923.
SECTION M1505
OVERHEAD EXHAUST HOODS
M1505.1 General. Domestic open-top broiler units shall be
provided with a metal exhaust hood, not less than 28 gage, with
1/4 inch (6 mm) between the hood and the underside of combustible
material or cabinets. A clearance of at least 24 inches (610
mm) shall be maintained between the cooking surface and the
combustible material or cabinet. The hood shall be at least as
wide as the broiler unit and shall extend over the entire unit.
Such exhaust hood shall discharge to the outdoors and shall be
equipped with a backdraft damper or other means to control
infiltrationlexfiltration when not in operation. Broiler units
incorporating an integral exhaust system, and listed and
labeled for use without an exhaust hood, need not be provided
with an exhaust hood.
SECTION M1506
EXHAUST DUCTS
M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter
16.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #4  
Old 12/29/11, 8:40 AM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Range hood vent pipe material

Barry, what code is it that you are referencing?




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #5  
Old 12/29/11, 8:52 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Range hood vent pipe material

Quote:
Originally Posted by jgromkoski View Post
Barry, what code is it that you are referencing?
International Mechanical Code



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 12/29/11, 8:52 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: Range hood vent pipe material

John it does not matter what code it is we can only recommend what was OK at the time. I do not agree to leave it like this and once you mention it needs to be stretched we hope that the person they call will correct it properly. We can say it would be best if it was solid metal according to proper practice today. M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter
16. This is from the IRC 2006 also.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 12/29/11 at 8:56 AM..
Reply With Quote
  #7  
Old 12/29/11, 8:59 AM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Range hood vent pipe material

I reported it does not meet current standards and may not be as safe as current standard material and installation practice. Thanks for the help.




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #8  
Old 12/29/11, 9:01 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Range hood vent pipe material

2012 irc it's basically the same in all previous versions

corrugated or accordion style is not smooth wall, "gunk" (inspectorspeak) will build up on the ridges/irregularities and become a combustion-fire hazard, therefore not allowed for this application



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #9  
Old 12/29/11, 9:08 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: Range hood vent pipe material

I should also mention that a manufacturer is making flex duct fire proof!
That being said Yes I would agree with the grease problem as Barry is pointed out.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 12/29/11 at 9:33 AM..
Reply With Quote
  #10  
Old 12/29/11, 9:09 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Range hood vent pipe material

Quote:
Originally Posted by kwood View Post
John it does not matter what code it is we can only recommend what was OK at the time. I do not agree to leave it like this and once you mention it needs to be stretched we hope that the person they call will correct it properly. We can say it would be best if it was solid metal according to proper practice today. M1506.1 Ducts. Where exhaust duct construction is not specified
in this chapter, such construction shall comply with Chapter
16. This is from the IRC 2006 also.
where is it allowed in 16

i'm not saying the code has to be quoted in a report but knowing what is not allowed is an automatic noted deficiency that requires removal and replacement with proper materials

any less is just another logo certified soft report



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #11  
Old 12/29/11, 9:29 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: Range hood vent pipe material

looks like the jiffy pop exploded....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #12  
Old 12/29/11, 9:29 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: Range hood vent pipe material

I was referring to the design of the duct in question. It is designed to be stretched in the manufactured installation guidelines. I was not saying that this is acceptable.
M1503.1 General.
The AHJ may allow it and this is sad but that is why we are in this business. This could be an outside wall side exhaust hood that presents no danger.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #13  
Old 12/29/11, 10:49 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Range hood vent pipe material

Quote:
Originally Posted by kwood View Post
I was referring to the design of the duct in question. It is designed to be stretched in the manufactured installation guidelines. I was not saying that this is acceptable.
M1503.1 General.
The AHJ may allow it and this is sad but that is why we are in this business. This could be an outside wall side exhaust hood that presents no danger.
I disagree.

Slinkys are a grease trap.

The client needs to be made aware of the potential hazard and that they can not be cleaned.

My non CMI opinion of course.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/29/11, 11:18 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Range hood vent pipe material

Quote:
This could be an outside wall side exhaust hood that presents no danger.
That makes about as much sense to me as the need to "stretch it out more"...

But then I'm not a CMI either!

Look at what I've been missing all these years!?

You have to have 26ga metal duct go through the garage wall to your HVAC equipment, but "foil" duct is OK directly above the stove...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #15  
Old 12/29/11, 11:31 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: Range hood vent pipe material

I did not say it was OK!



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Outside Hot Water Heater With Vent Pipe Outside Kitchen Window bwilliams Plumbing Inspections 4 12/8/08 11:10 PM
Direct vent WH with draft hood dpeterson Plumbing Inspections 9 12/30/06 3:35 PM
Asbestos Vent Pipe??? psmothers Plumbing Inspections 17 5/22/06 2:14 AM


All times are GMT -4. The time now is 10:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts