Default Readily Accessible Disconnect

I've been reading some posts on this mb and thought I knew what I was doing (thought!!)

My question relates to today's heat pump, but actually applies to any central heating furnace.

Can the breakers ON the unit be counted as the disconnect for the "appliance"? I'm looking at IRC 4001.5 table. Beneath the table is the line, "...permitted to be installed on or within the unit. It shall not be located on panels designed to allow access to the unit." Now obviously the mfr. installed these breakers.

So for the photo below, is another disconnect required? The breaker is at the lower left of the unit (behind the plastic panel). I know you all know that.

I have an idea, but I'm holding my cards close (so I don't look like a complete idiot).

Thanks in advance,
Bruce
Attached Thumbnails
readily-accessible-disconnect-copy-s6307135-compress.jpg  



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #2  
Old 2/18/08, 3:49 PM
dbush's Avatar
dbush dbush is offline
Active Poster
 
Join Date: Dec 2002
Location: Joplin, MO
Posts: 243
Send a message via MSN to dbush Send a message via Yahoo to dbush
Please Note: dbush is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Readily Accessible Disconnect

Bruce, the realidy accessible breaker on the unit should suffice in most if not all jurisdictions. If it is not a code question, then it does suffice because it offers breaker protection without having to remove a portion of the equipment.
Reply With Quote
  #3  
Old 2/18/08, 4:04 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Readily Accessible Disconnect

It's not a code question. In my way of thinking (twisted granted), there is still power to these small breakers (even if off). I wouldn't want to work on the unit with electricity that close.

Thanks for the comments.



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #4  
Old 2/18/08, 9:31 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Readily Accessible Disconnect

Quote:
Originally Posted by bthompson1
It's not a code question. In my way of thinking (twisted granted), there is still power to these small breakers (even if off). I wouldn't want to work on the unit with electricity that close.

Thanks for the comments.
Bruce that breaker is perfectly fine. If one follows standard safety procedures such as using a meter to determine that the breakers actually turned off the power, not a problem. How I stayed alive long enough to retire was following safety standards. I never just assume the breaker was not burnt in the closed position before I stick my hands in there just common sense.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 2/18/08, 9:34 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Readily Accessible Disconnect

Quote:
Originally Posted by cbottger
Bruce that breaker is perfectly fine. If one follows standard safety procedures such as using a meter to determine that the breakers actually turned off the power, not a problem. How I stayed alive long enough to retire was following safety standards. I never just assume the breaker was not burnt in the closed position before I stick my hands in there just common sense.
Thanks. I was hoping you would login and read my post. I appreciate it.

Bruce



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #6  
Old 2/20/08, 6:53 AM
rgallahorn rgallahorn is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Charleston, SC
Posts: 58
Default Re: Readily Accessible Disconnect

Be careful, on some AHU's the breaker only controls the heat strips and the unit has a second feed for the controls and fan assembly. Did this unit have 2 breakers behind the panel. It seems to have 2 feeds coming in at the base of the unit.
Reply With Quote
  #7  
Old 2/20/08, 11:32 AM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Readily Accessible Disconnect

Quote:
Originally Posted by rgallahorn
Be careful, on some AHU's the breaker only controls the heat strips and the unit has a second feed for the controls and fan assembly. Did this unit have 2 breakers behind the panel. It seems to have 2 feeds coming in at the base of the unit.
It did have 2 breakers behind the panel.



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #8  
Old 2/21/08, 2:14 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Readily Accessible Disconnect

Quote:
Originally Posted by bthompson1
It did have 2 breakers behind the panel.
Many of the heat strips I have installed on air handlers had one or two 240V 2-pole breakers with feeders for only the heat strip. The air handler typically needed a separate 120V feeder and disconnect.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
Home Inspection IS NOT ABOUT SAFETY jcahill General Inspection Discussion 39 2/25/07 11:08 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 6:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts