Default Re: Is this reasonable?

Quote:
Originally Posted by fnewman View Post
No, only 2 deg. more than the room temp. It was a digital thermostat, so I should have seen an indication in the display if the aux was on. I guess it could have been on if the the thermostat wiring was incorrect at the unit. Given that the house is essentially new, such a problem could have gone unnoticed by the previous occupants.
Frank,
At 55 deg outside I don't think it is unreasonable for that size unit to produce 115, but I what do I know. I have found a few that put out the heat but they are usualy new or close to it. The rest when working pump out between 90 to 105 in testing both sides.

Here are the facts for you..
First, if you grab the line set and its hot you know the heat pump is working.


Second if the aux heat is pushing 90 or better you know the heat strips are working.

Thats really all you need to worry about because the system is working and your functional part of inspectiing the heat pump is now complete..

I understand your wonder though, I had the same thought before to.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net

Last edited by sfogarty; 12/17/10 at 9:54 PM..
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 12/17/10, 9:48 PM
RAY THOROMAN RAY THOROMAN is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Gainesville, GA
Posts: 629
Default Re: Is this reasonable?

Quote:
Originally Posted by cbottger View Post
Frank I quit posting for over a year until just recently all I can say they are in the archives.

Ok lets see if I can bring the SOP nuts out of the woodwork.

The only true way to determine if the aux is on and how many of the aux's because there will normally be more than one strip is to use a amp meter.

The strips are staged on by the stat each strip will draw approximately 20 amps.

One has to take the excess panel off the furnace to expose the strips then you can count the # of strips if there are 3 strips if all are operating you should have 60 amps or close

Whoops have to go carry Grocery's get back to this later


Good info Charley


Frank, I'd say sure that's reasonable. But I'd not concern myself or report on issues outside the iNACHI sop if that is what you inspect to. You can evaluate systems above the sop, just do not report over the sop.

Just sayin' I inspect in your State GA and same general area.



Reply With Quote
  #18  
Old 12/17/10, 9:53 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Is this reasonable?

I do try to stay close to SOP, but sometimes, when I run across something out of the ordinary, I like to dig a little deeper just to satisfy my own curiosity, if nothing else. The problem, in most cases, is that time is limited and you can spend a lot of time in the name of learning a bit more. That's really why I asked the question in the first place - to see if some of the experts could shed a little light on the situation.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #19  
Old 12/17/10, 9:59 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Is this reasonable?

Quote:
Originally Posted by fnewman View Post
I do try to stay close to SOP, but sometimes, when I run across something out of the ordinary, I like to dig a little deeper just to satisfy my own curiosity, if nothing else. The problem, in most cases, is that time is limited and you can spend a lot of time in the name of learning a bit more. That's really why I asked the question in the first place - to see if some of the experts could shed a little light on the situation.
I would like to know myself.. Is it unusaual to have a heat pump put out that much or is the thermostat wired wrong where both sides are running?




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #20  
Old 12/17/10, 11:11 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this reasonable?

Quote:
Originally Posted by fnewman View Post
I understand how the strips work and how to use the clamp-on amp meter I carry in my case, but what I really was oringally asking was whether a supply temp of about 115 is likely without strips for the situation I described. It just seemed so high that I suspected at least one strip was on - if so, the question would be why? With the old analog thermostats I coudl always tell if the Aux had been turned on, but with the digitals, it is not as easily determined.
At 55 degrees outside ambient a 115 degrees on the supply side is possible on some HP's very close to the max I have ever seen. I still would have used the amp meter to see if one of the elements was activated the unit could have been wired to bring one element on with normal heat. It should not be wired that way but I don't trust contractors to do what is right.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #21  
Old 12/17/10, 11:27 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this reasonable?

Quote:
Originally Posted by jfunderburk View Post
Of course Charley, you are right. And if they wanted a technically exhaustive inspection, I'd do it your way.
So basically you don't care if the unit is performing as the MFG intended. Technically Exhaustive Should have nothing to do with the operation of this piece of equipment it either operates as the MFG intended or it does not. How does one know AMP meter. Just because some desk jocky that wrote the SOP did not have enough knowledge about proper operation of a heat HP does not make it right

Joe you have been doing HI's for a long time now and I believe you know the SOP is just the minimum required to perform just as building Codes are the minimum requirements for a builder. I see HI's slamming builders all the time for constructing homes to minimum codes and then they turn around and inspect to SOP the minimum standards for HI's.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #22  
Old 12/17/10, 11:44 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this reasonable?

Quote:
Originally Posted by sfogarty View Post
I would like to know myself.. Is it unusaual to have a heat pump put out that much or is the thermostat wired wrong where both sides are running?

Yes and don't you think your client would like to know the same thing being they are the ones going to be paying the utility bills



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #23  
Old 12/17/10, 11:58 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Is this reasonable?

Quote:
Originally Posted by fnewman View Post
Just finished an inspection on a 2 year old home, 2800 sq. ft. with a 5 ton Lennox heat pump. Outside air was about 55 F this morning. Supply / return differential was approx. 32 degrees. I've never seen one that high, so am wondering if that is reasonable without the aux. heat being on? TIA

Sounds like you have R410 units since the house is only two years old and those temps are typical.

I have lots of testing experience with these.

I have owned two heat pumps with R410 for 9 years now, one is a 3 ton and the other a 3.5 ton. Both have the same type variable speed air handlers with 10kw strips in each. Also have the outside temperature sensor option so I can program the aux heat strips to stay off unless its really cold out. The defrost mode still kicks on the aux heat during the 1-2 minute cycle to knock off the chilled air.

These R410 units are awesome, the supply air will vary depending on the outside temperature. Properly sized, they will heat a properly insulated house with no aux strips running down to the low 20's or even below in some cases.

I can see where a miswired unit could be overlooked and you could have aux heat running when it should not (costs 3 times more to heat with electric strips than R410 system). With outside temp at 55 and heat pump and aux heat running you could see supply air above 130 easy, but depends on the size of the aux strips installed.

Since my variable speed units were a new thing in 2001, the installer wired them wrong. They worked ok but made some weird very high speed fan cycles during defrost mode. The airhandlers have several jumper settings for comfort modes and efficiency modes etc so I eventually took the 4 pages of system wiring options up there and figured it out. They were wired as basic air handlers instead of variable speed types.

One of the things I write up on new homes is the lack of labeling on the airhandler cabinet to indicate which size aux heat kit is installed.

Another difference with R410 is the presence of a little more ice on the outside unit before the defrost kicks in than you might be used to seeing on the old R22 systems, not a problem. The outside units typically have a jumper adjustment to choose the total run time between defrost cycles.
I think mine came set for 45 minutes and I changed it to defrost a little sooner.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #24  
Old 12/18/10, 4:19 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Is this reasonable?

Quote:
Originally Posted by cbottger View Post
So basically you don't care if the unit is performing as the MFG intended. Technically Exhaustive Should have nothing to do with the operation of this piece of equipment it either operates as the MFG intended or it does not. How does one know AMP meter. Just because some desk jocky that wrote the SOP did not have enough knowledge about proper operation of a heat HP does not make it right

Joe you have been doing HI's for a long time now and I believe you know the SOP is just the minimum required to perform just as building Codes are the minimum requirements for a builder. I see HI's slamming builders all the time for constructing homes to minimum codes and then they turn around and inspect to SOP the minimum standards for HI's.
Charley, I know about how a heat pump ought to feel because I have one. If it's blowing hot air, I'm not too concerned and will let the HVAC guy pick the system apart with a fine tooth comb during his annual inspection (I recommend a full HVAC eval. prior to closing also). If the system is blowing air below 80 deg. in aux. mode with the outdoor coil off, I question the functionality of the heat strip(s) and refer it out. But if it's blowing warm air, I'm not taking the cabinet apart (especially not in a hot attic).

I don't check refrigerant pressure either and I'm sure the MFG has a standard for what that out to be. If they want a technically exhaustive inspection, I offer one for $10,000 and allow them to pay at closing also.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #25  
Old 12/18/10, 6:38 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Is this reasonable?

Quote:
Originally Posted by jfunderburk View Post
Charley, I know about how a heat pump ought to feel because I have one. If it's blowing hot air, I'm not too concerned and will let the HVAC guy pick the system apart with a fine tooth comb during his annual inspection (I recommend a full HVAC eval. prior to closing also). If the system is blowing air below 80 deg. in aux. mode with the outdoor coil off, I question the functionality of the heat strip(s) and refer it out. But if it's blowing warm air, I'm not taking the cabinet apart (especially not in a hot attic).

I don't check refrigerant pressure either and I'm sure the MFG has a standard for what that out to be. If they want a technically exhaustive inspection, I offer one for $10,000 and allow them to pay at closing also.
Don't get your panties in a wad Joe Cain't you tell by now when I am ragging someone just having fun with you. Your just to easy



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #26  
Old 6/9/11, 1:49 PM
Scott Donnelly Scott Donnelly is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 22
Default Re: Is this reasonable?

There are a number of things that can cause the temp. to be this high but with out the heat strips working none of them are good. I suspect your thermostate is miss wired. I find some heat strips come on with just 2 degree change at the thermostate. Try turning it up 1 degree and see what happens.
Reply With Quote
  #27  
Old 6/9/11, 4:07 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Is this reasonable?

The Unit probably has a Gas Furnace.

Charley would be there all day with his Clamp Meter.
Reply With Quote
  #28  
Old 6/10/11, 1:06 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Is this reasonable?

Hay Scott; quit trying to resurect the "dead".

This post was started Dec 2010!

If you perport to know anything about HVAC you know that under "any" test conditions that a dry bulb temperature differential can tell you "nothing" about how the equipment is operating!

The unit was "starving" because of the low ambient conditions.
Simple "matter-of-fact".



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 6/10/11, 4:45 PM
Jay Bucklew Jay Bucklew is offline
New User
 
Join Date: Jun 2011
Posts: 1
Please Note: Jay Bucklew is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this reasonable?

Don't know if 1st reply was sent. So.. I am a cunsumer. I am looking to replace a heat pump system. My question re: the air handler. Today's options include a multi- or variable speed handler. This was not a choice available 30 yrs ago when current handler was installed. Single speed handler is either on/off depending on whether compressor is running. My understanding is the multi or variable speed motor will run continuously (although at varying speeds), & thus use varying amounts of electricity. Is the multi/variable speed handler less efficient in the use of electricity? I know when single speed is on, it will run at higher speed, but by being off at times may actually cost less. I am told the variable/multi speed handler makes the HVAC experience more comfortable. Am I worrying about pennies or nickles here, or is it a reasonable question and concern in my purhcase decision? I am new to the group. Power company could give me no help on this. I hope you all can. Thanx
Jay
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Legal: Buyer points blame at sellers when basement repeatedly floods. gromicko Legislation, Licensing & Legal Issues for Inspectors 0 6/10/08 2:42 PM
GOOD and Reasonable WEBSITE Builder NEEDED. dadamescu Miscellaneous Discussion for Inspectors 19 2/9/08 12:45 AM
Anyone smart enough to know a reasonable solution to this problem? Bill Featherstone Inspecting HVAC Systems 4 12/6/07 11:15 PM
Reasonable Apprehension of Bias and Vexatious Actions of OAHI rwand1 Canadian Inspectors 25 8/26/06 5:02 PM


All times are GMT -4. The time now is 10:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts