I have a client who's furnace shuts down on a regular basis . She had a heatind man look at it and tell her that being a two cycle furnace , when on the low cycle, spent gasses are not being forced up the chimney and the sensors are shutting down the whole system . She resets it and all is well for a day or two then it happens again. the heater man is telling her to put a chimney liner in the chimney and it should stop the problem. any thoughts out there.
Reply With Quote
  #2  
Old 1/18/06, 2:47 PM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: it is a reem

If this is a two cycle furnace it is most likely also a 90+ condensing gas furnace. If so it shouldn't be going up the chimney anyway. If the flue is plastic it should be run to the outside entirely in plastic. 2 or 4 inch schedule 40 pvc.
Reply With Quote
  #3  
Old 1/18/06, 11:23 PM
Dean Call Dean Call is offline
New User
 
Join Date: Jan 2005
Posts: 23
Please Note: Dean Call is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: it is a reem

If it's a non condensing high efficiency furnace it should have a chimney liner anyway but that may not be the cause of the "lock out"condition.

She should ask him if he will guarntee that will fix the problem.

Furnace "lock out" problems are sometimes not easy to diagnose.
Reply With Quote
  #4  
Old 1/18/06, 11:53 PM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: it is a reem

There are so many things that will lock out a modern high end furnace we don't have enough info. All we can do from here is guess.
Reply With Quote
  #5  
Old 1/19/06, 3:39 PM
jrupert jrupert is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Grove City, OH
Posts: 47
Default Re: it is a reem

Almost all codes and all manufactures will tell you to install a flue liner on any 80% furnace single or two stage on a masonry chimney. The problem is compounded with a two-stage unit because on low fire the volume of flue gasses going up the chimney are 1/3 less and not do not contain enough heat to warm the masonry chimney for proper venting. This can be an interment issue depending on weather conditions. Even if a hot water heater vents to the same chimney as the furnace.

Furnaces have a pressure sensor that monitors the “pressure” venting into the chimney, when the flue gases cool part way up the chimney they create a “thermal block” it’s like closing the chimney, this will trip the pressure switch shutting down the furnace. Some furnace will restart over and over, others have a lock out designed to keep the furnace off after 3 failures.

It is always a good protection as a consumer to have the results of any work put in writing



John Rupert
Accurate Property Inspections
Solitaire Heating & Cooling
CSG Training (HVAC Training & Consulting)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts