In a case like this would one recommend how to fix it or just defer the fix to someone else? I could see the HVAC guy just changing the type of control conductors and making the same mistake twice.
|
| Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#17
|
||||
|
||||
|
I report that low voltage and high voltage components must be in separate enclosures and/or conduit. I don't reference the conductor types.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#18
|
||||
|
||||
|
What about telephone cables (at bottom) in conduit with SEC, not what I'm pointing at (mismatched breakers).
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#19
|
||||
|
||||
|
What about them?
Did you have a question about mixing hi/lo voltage conductors? "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission |
|
#20
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The real issue here is that many electrician's and HVAC techs think that you can install class 2 conductors and power conductors in the same raceway, they typically will cite (incorrectly) NEC 300.3(C).
Quote:
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| I need to refer Chattanooga TN Inspector | rthoroman | Miscellaneous Discussion for Inspectors | 1 | 2/24/11 5:33 PM |
| what type of specialist to refer | cwillick1 | Structural Inspections | 13 | 9/15/07 7:09 PM |
| Do you refer clients to Nachi to find an inspector? | mroe | Miscellaneous Discussion for Inspectors | 1 | 8/21/07 12:34 PM |
| Need to refer a mold test in WI | gliebig | General Inspection Discussion | 5 | 4/30/07 4:04 PM |