Default Refrigerant line question

Is there anything against using hard copper pipe with soldered fittings on the suction side of the AC refrigerant line?




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/14/11, 6:52 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Refrigerant line question

Depends, is approved for refrigeration? thick wall or did Billy bob use water pipe lol



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #3  
Old 11/14/11, 1:02 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Refrigerant line question

The soft copper line sets that are used are cleaned inside to prevent contamination of the system. Water pipe isn't prepared the same way. Plus with the rigid you will need more fittings and thus more areas for restriction and possible leaks. Soldering put contaminates inside the pipe and isn't as secure of a connection as brazing.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #4  
Old 11/14/11, 2:32 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Refrigerant line question

these have different ID and OD than soft copper and as already pointed out not made to the same standards. I still find copper lines for gas used for plumbing with boogered up flared fittings and connections....always leaking



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #5  
Old 11/14/11, 5:36 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Refrigerant line question

They sell hard drawn refrigerant tubing that is sealed with nitrogen it has rubber plugs in both ends



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 11/14/11, 5:39 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Refrigerant line question

Yep all commercial lines are solid . I never ad a problem with corrosion



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #7  
Old 11/14/11, 7:04 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Refrigerant line question

Quote:
Originally Posted by cbottger View Post
They sell hard drawn refrigerant tubing that is sealed with nitrogen it has rubber plugs in both ends
Same here Charley, and all joints are silver soldered.
Reply With Quote
  #8  
Old 11/14/11, 8:21 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Refrigerant line question

Quote:
Originally Posted by mcyr View Post
Same here Charley, and all joints are silver soldered.
Yes sir I used to cuss those dudes that used soft solder on suction lines it is allowed but a pain in the Butt when all yous have in your bag is silver solder the two don't mix



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 11/24/11, 10:14 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Refrigerant line question

1107.5 Materials for refrigerant pipe and tubing. Piping materials shall be as set forth in Sections 1107.5.1 through 1107.5.5.

1107.5.3 Copper tube. Copper tube used for refrigerant piping erected on the premises shall be seamless copper tube of Type ACR (hard or annealed) complying with ASTM B 280. Where approved, copper tube for refrigerant piping erected on the premises shall be seamless copper tube of Type K, L or M (drawn or annealed) in accordance with ASTM B 88. Annealed temper copper tube shall not be used in sizes larger than a 2-inch (51 mm) nominal size. Mechanical joints shall not be used on annealed temper copper tube in sizes larger than 7/8-inch (22.2 mm) OD size.

and

1107.5.4 Copper tubing joints. Copper tubing joints used in refrigerating systems containing Group A2, A3, B2 or B3 refrigerants shall be brazed. Soldered joints shall not be used in such refrigerating systems



Paul W. Abernathy
Reply With Quote
  #10  
Old 11/24/11, 10:14 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Refrigerant line question

and you all thought I only knew Electrical.....lol



Paul W. Abernathy
Reply With Quote
  #11  
Old 11/24/11, 10:31 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Refrigerant line question

Quote:
Originally Posted by pabernathy View Post
and you all thought I only knew Electrical.....lol
Its been a while but I have changed out compressors in refrigerant units that the MFG used soft solder on suction lines. MFG always trumps ya code book



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 11/25/11, 6:46 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Refrigerant line question

Quote:
Originally Posted by cbottger View Post
Its been a while but I have changed out compressors in refrigerant units that the MFG used soft solder on suction lines. MFG always trumps ya code book
Aww..poopoo...lol.....follow the code and you can't go wrong. And atleast you will have the most unsafe home the code will allow...



Paul W. Abernathy
Reply With Quote
  #13  
Old 11/25/11, 9:33 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Refrigerant line question

Quote:
Originally Posted by cbottger View Post
Its been a while but I have changed out compressors in refrigerant units that the MFG used soft solder on suction lines. MFG always trumps ya code book
I also wanted to respectfully disagree....lol....In accordance with Section 304.2 of the International Mechanical Code. Where there is a conflict between the code and the installation instructions or listing the provisions of the CODE shall apply. Now, where the code is less restrictive than the listing or manufactures instructions then you follow the listings and/or instructions.

However, the most restrictive will apply here so not always will the MFG trump the code book my friend....lol......Go..Guru...Go Shamu...i mean Guru !



Paul W. Abernathy
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/28/11, 10:15 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Refrigerant line question

Quote:
Originally Posted by cbottger View Post
MFG always trumps ya code book
Only if it's not covered by the code or more restrictive than the code ...

Soldered refrigerant joints are now specifically prohibited by the code, so they cant be used if an IRC based code is in effect.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 11/28/11, 10:30 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,110
Default Re: Refrigerant line question

YEP! I have used that argument more than once Paul.
It could save some HI some much heartache and pain.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas line Cut-off question...pic dnasser Inspecting HVAC Systems 4 10/22/10 10:07 PM
Main Line vs. Supply Line Reporting Details sshockley Plumbing Inspections 2 6/14/09 3:07 PM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical Inspections 0 12/2/07 1:43 PM
Supply Line Question hmcclard Plumbing Inspections 5 10/29/07 10:42 AM
Size of supply line aobrien Inspecting HVAC Systems 7 1/2/07 12:40 PM


All times are GMT -4. The time now is 10:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts