Default Relective radiant barriers in southern climates

Can on you in the souther states that use refective radiant barriers in the attic spaces please tell me the reasoning behind using the barriers directly applied the underside of the roof deck?

I understand attaching the barriers to the underside of the rafters as that creates a vented air space. Or even using the double foiled bubble wrap stuff as effective methods.

What I don't understand is something like if foil faced sheathing is used, how is the barrier suposed to reflect radiant heat back out when it is in direct contact with the deck sheathing? Reflective radiant bariers need a air space to be most effective do they not?
Reply With Quote
  #2  
Old 2/27/07, 1:36 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Relective radiant barriers in southern climates

Quote:
Originally Posted by phinsperger
Can on you in the souther states that use refective radiant barriers in the attic spaces please tell me the reasoning behind using the barriers directly applied the underside of the roof deck?

I understand attaching the barriers to the underside of the rafters as that creates a vented air space. Or even using the double foiled bubble wrap stuff as effective methods.

What I don't understand is something like if foil faced sheathing is used, how is the barrier suposed to reflect radiant heat back out when it is in direct contact with the deck sheathing? Reflective radiant bariers need a air space to be most effective do they not?
Paul I could ask the same question as my thinking is the same as yours. My new house inspection today was my first encounter with the foil lined backing on the roof decking it would be interesting to go back into that attic when it is a 100+ outside ambient.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 2/27/07, 2:07 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,749
Default Re: Relective radiant barriers in southern climates

http://www.radiantbarrier.com/physics_of_foil.htm

Quote:
Materials whose surfaces do not appreciably reflect infrared rays, i.e.: paper, asphalt, wood, glass and rock, have absorption and emissivity rates ranging from 80% to 93%. Most materials used in building construction -- brick, stone, wood, paper, and so on -- regardless of their color, absorb infrared radiation at about 90%. It is interesting to note that a mirror of glass is an excellent reflector of light but a very poor reflector of infrared radiation. Mirrors have about the same reflectivity for infrared as a heavy coating of black paint.
The surface of aluminum has the ability NOT TO ABSORB, but TO REFLECT 95% of the infrared rays which strike it. Since aluminum foil has such a low mass to air ratio, very little conduction can take place, particularly when only 5% of the rays are absorbed.
Does this help?



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #4  
Old 2/27/07, 4:07 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relective radiant barriers in southern climates

Not quite Brain. I read that same material already on a different site but I still don't see the answer to my question. How does the reflective barrier work when it is in direct contact (no air space) on the underside of the roof sheathing?
Reply With Quote
  #5  
Old 2/27/07, 4:26 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,749
Default Re: Relective radiant barriers in southern climates

Quote:
Originally Posted by phinsperger
Can on you in the souther states that use refective radiant barriers in the attic spaces please tell me the reasoning behind using the barriers directly applied the underside of the roof deck?

I understand attaching the barriers to the underside of the rafters as that creates a vented air space. Or even using the double foiled bubble wrap stuff as effective methods.

What I don't understand is something like if foil faced sheathing is used, how is the barrier suposed to reflect radiant heat back out when it is in direct contact with the deck sheathing? Reflective radiant bariers need a air space to be most effective do they not?
Yes to be effective for "radiant" heat there needs to be an airgap.

http://www.radiantbarrier.com/physics_of_foil.htm

Quote:
Reflection and emissivity by surfaces can ONLY occur in SPACE. The ideal space is any dimension 3/4" or more. Smaller spaces are also effective, but decreasingly so. Where there is no air space, we have conduction through solids. When a reflective surface of a material is attached to a ceiling, floor or wall, that particular surface ceases to have radiant insulation value at the points in contact.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail

Last edited by bkelly2; 2/27/07 at 4:29 PM..
Reply With Quote
  #6  
Old 2/27/07, 7:44 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relective radiant barriers in southern climates

Then why is foil faced roof decking being used in the south?
Reply With Quote
  #7  
Old 2/27/07, 7:48 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,700
Default Re: Relective radiant barriers in southern climates

There are three types of heat transfer; conduction, convection, radiation.
They are three separate distinct means of transfer. Reflective substances reflect radiation. Contact has to do with conduction and is not related.
Airspace is a very good insulator and prevents conduction from happening at radiation barriers. Airspace is not necessary for the reflective device to work, however adding an airspace will improve the overall construction of the wall/ roof /ceiling.


Quote:
Mirrors have about the same reflectivity for infrared as a heavy coating of black paint.
I don't know what this is about, but a reflective surfaces reflect radiation. It does not have the same absorption factor as black paint! A little more information on this perception would be interesting.

Maybe I'm just tired but I'm not grasping the concept you are communicating.
Reply With Quote
  #8  
Old 2/27/07, 8:16 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relective radiant barriers in southern climates

Quote:
Mirrors have about the same reflectivity for infrared as a heavy coating of black paint.
That is their quote not mine, but I beleive what they are saying is that a mirror reflects the visible light sectrum greatly but only reflects the infared spectrum little. I suspect that is because the glass is in direct contact with the reflecive surface coating.


Quote:
Originally Posted by dandersen
Airspace is a very good insulator and prevents conduction from happening at radiation barriers.
Right. Now with the foil faced roof sheathing, it is installed with the foil side down facing the interior of the attic.

So solar radiation comes from the sun and hit the shingles and converts to thermal heat in the shingles. That thermal heat is conducted to the roof deck because the shingles are in contact with the roof deck. The underside of the roof deck is face with aluminum reflective foil. Because the decking is in direct contact with the roof deck the foil also gathers thermal heat.

Now here the tricky part. Because the foil has a very low emissivity (5%) the there is very little radiant heat leaving the roof deck into the attic area. So the attic is a bit cooler. Great. but what happened to that heat that would have normally been radiated into the attic? It stays a thermal heat in the roof deck and .... you guessed it. - the shingles. The shingles and roof deck are receiving 95% of the solar radiation hiting them ! That is a lot of energy cooking the shingles!
Reply With Quote
  #9  
Old 2/28/07, 11:57 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,700
Default Re: Relective radiant barriers in southern climates

Yes, I know it's them talking. Not you.
I just don't know what they're getting at.

Part two: yes that is a lot of energy on the shingles!
Reply With Quote
  #10  
Old 2/28/07, 8:11 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Relective radiant barriers in southern climates

Thanks David.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Forum 0 10/9/07 7:45 PM
About Air Barriers mcyr General Inspection Discussion 5 9/29/07 11:10 PM
Radiant ceiling heat? bmargiotti HVAC 12 3/21/07 1:12 PM


All times are GMT -4. The time now is 11:59 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts