Default Required outlet at exterior units

Can someone tell me where I might find the requirement that an "exterior" outlet be in the vicinity of the exterior ac units?
Thanks...



www.HomeInspectionGA.com
McDonough, GA.
770-722-3717
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/18/10, 1:35 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Required outlet at exterior units

There isn't a requirement around the unit. Exterior receptacles are required at the front and back of the dwelling.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 10/18/10, 1:38 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Required outlet at exterior units

Do you me the ac disconnect? If so it has to be within sight, I also believe within 50 ft.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 10/18/10, 1:41 PM
Charles L. Harper's Avatar
Charles L. Harper Charles L. Harper is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: McDonough, GA
Posts: 351
Default Re: Required outlet at exterior units

Thanks guys, I found it.

210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet. A 125-volt, single phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.



www.HomeInspectionGA.com
McDonough, GA.
770-722-3717
Reply With Quote
  #5  
Old 10/18/10, 1:52 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Required outlet at exterior units

Quote:
Originally Posted by charper View Post
Thanks guys, I found it.

210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet. A 125-volt, single phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
What year is this from?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 10/18/10, 1:54 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Required outlet at exterior units

I thought you said on the outside, not a crawl space.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #7  
Old 10/18/10, 2:07 PM
Charles L. Harper's Avatar
Charles L. Harper Charles L. Harper is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: McDonough, GA
Posts: 351
Default Re: Required outlet at exterior units

That is exterior, usually very close to your ac units....



www.HomeInspectionGA.com
McDonough, GA.
770-722-3717
Reply With Quote
  #8  
Old 10/18/10, 2:24 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Required outlet at exterior units

I simply note whether GFCI outlets are installed on the exterior of the home I'm in inspecting. I'm not concerned with outlets installed within a proximity of a condenser.
Reply With Quote
  #9  
Old 10/18/10, 2:26 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Required outlet at exterior units

There is no requirement for one on the exterior near AC units. Only exterior receptacle requirements are on the front and rear of the home.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #10  
Old 10/18/10, 2:46 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Required outlet at exterior units

Quote:
Originally Posted by charper View Post
Thanks guys, I found it.

210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet. A 125-volt, single phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
You forgot the rest of that code....

exception: A receptacle outlet shall not be required at one and two-family dwellings for the service of evaporative coolers.


Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #11  
Old 10/18/10, 4:27 PM
Jim Hime Jim Hime is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Dickinson, Tx
Posts: 103
Default Re: Required outlet at exterior units

Quote:
Originally Posted by charper View Post
Can someone tell me where I might find the requirement that an "exterior" outlet be in the vicinity of the exterior ac units?
Thanks...
Started in 1987 NEC 210.63 (bar by section) to current 2008 NEC 210.63
Reply With Quote
  #12  
Old 10/18/10, 5:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Required outlet at exterior units

Quote:
Originally Posted by sstanczyk View Post
There is no requirement for one on the exterior near AC units. Only exterior receptacle requirements are on the front and rear of the home.
Unless the required exterior outlet(s) is within 25 feet of the appliance, NEC 210.63 requires an additional outlet to be installed specifically for servicing of the appliance.

This requirement has been around for quite some time.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 10/18/10, 6:57 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Required outlet at exterior units

Quote:
Originally Posted by jpope View Post
Unless the required exterior outlet(s) is within 25 feet of the appliance, NEC 210.63 requires an additional outlet to be installed specifically for servicing of the appliance.

This requirement has been around for quite some time.
Strange. Just finished a new construction inspection an hour ago. Went past 4 homes that chose heat pumps instead of the gas furnace. Not one of them had a receptacle anywhere near the units. I also had a new heat pump install a short itme ago, with permit, at my son's house. The nearest exterior receptacle is on the far end of the home, probably 45 feet away. At first I thought maybe it is a regional thing but WA is using the 2008 NEC. Or maybe the AHJ just does not care......... imagine that. My bad.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/18/10, 7:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Required outlet at exterior units

As with any code, the local AHJ has the final word.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 10/25/10, 8:22 PM
rjohnson11 rjohnson11 is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Binbrook Ontario
Posts: 17
Default Re: Required outlet at exterior units

Quote:
Originally Posted by charper View Post
Thanks guys, I found it.

210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet. A 125-volt, single phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
I do believe that only concerns commercial applications, not residential. In 28 years as a mechanical contractor, the only time we were ever required to install conv outlets was on commercial/industrial applications in Michigan, Ohio, Washington DC and Florida.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
TREC windows jcahill Legislation, Licensing & Legal Issues for Inspectors 8 5/2/08 1:41 AM
Testing a dryer outlet acox Electrical Inspections 14 7/27/06 10:51 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 10:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts