Old 5/11/07, 10:51 PM
Kenneth E. Sitzes's Avatar
Kenneth E. Sitzes Kenneth E. Sitzes is offline
Send a message via Skype™ to ksitzes
Default requried height
Is there a required height for a exhausted from a furnace
Kenneth Sitzes
NACHI #04122492
Eagle Inspection of Illinois
618-830-8283
Waterloo, Illinois 62298
ghinspector@yahoo.com
InterNACHI State of Illinois Continuing Education Administrator
Old 5/12/07, 12:14 AM
Stephen W. Stanczyk's Avatar
Default Re: requried height
I have never seen any this low and would be interested to see what the group comes up with. My biggest concern at this height would be the potential for animal / pest intrusion.
Stephen Stanczyk
Old 5/12/07, 12:18 AM
Joseph Hagarty,  CMI's Avatar
Generally 12 inches (USA Standard) above expected snowfall.
In an area with no snow expectations.....12 inches from grade.
Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net
Old 5/12/07, 12:36 AM
whandley's Avatar
whandley whandley is offline
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Ditto....
2006 ICC
804.3.4 Horizontal terminations.
shall comply with the following requirements:
1. Where located adjacent to walkways, the termination
of mechanical draft systems shall be not less than 7
feet (2134 mm) above the level of the walkway.
2. Vents shall terminate at least 3 feet (914 mm) above
any forced air inlet located within 10 feet (3048 mm).
3. The vent system shall terminate at least 4 feet (1219
mm) below, 4 feet (1219 mm) horizontally from or 1
foot (305 mm) above any door, window or gravity air
inlet into the building.
4. The vent termination point shall not be located closer
than 3 feet (914 mm) to an interior corner formed by
two walls perpendicular to each other.
5. The vent termination shall not be mounted directly
above or within 3 feet (914 mm) horizontally from an
oil tank vent or gas meter.
6. The bottom of the vent termination shall be located at
least 12 inches (305 mm) above finished grade.
Old 5/12/07, 12:58 AM
Joe Funderburk, CMI's Avatar
If that's the height of the crawl space, the ventilation on that side must also be lacking. Can they redirect it to a higher side?
Theodore Roosevelt
Joe Funderburk, CMI
NACHI ID: NACHI05120170
www.aohomeinspection.com
Old 5/12/07, 1:45 AM
It is the basement.
Kenneth Sitzes
NACHI #04122492
618-830-8283
Old 5/16/07, 8:49 PM
David A. Andersen's Avatar
Snow blockage is the concern. It will shut down the furnace.
It can be raised up and turned back down (if that window above can not be opened).
Chimney Height dmacy Exterior Inspections 3 6/22/07 3:56 PM
Max Breaker height. jlybolt Electrical Inspections 5 5/22/07 9:26 AM
Ceiling height question Chris Watkins Interior Inspections 13 5/10/07 8:25 PM
Exterior outlet height jharashinski Electrical Inspections 7 4/3/06 8:25 AM
Chimney Height for combustable gas dmacy Exterior Inspections 7 1/21/06 9:58 PM