Default Return air in basement?

Hope to get all the conditions clear on this.

Furnace in unfinished basement about 12 x 30 ft 8 ft height

Finished side of the basement is about the same size.

2 return air ducts in the finished side that is separated by a solid wood door.

No vents to exchange air between sides.

Supply vents in the unfinished side are sealed.

The return air ducts are less than 6 feet log. One vent is about 10 feet away and the other is about 15 feet away. both around the corner.

There is NO passthrough at the floor joists. It has been blocked.

The furnace is 80 percent efficient with induced draft.

My thoughts are that the combustion air source has been reduced by the refinishing and the blower may create a negative pressure that would cause combustion air around the burners to be drawn into the return air ducts.

I suggested a HVAC expert evaluate the situation.

There is no evidence of spillage on the 4 year old furnace.

any suggestions?



Rick A. Harrington

Patch Independent Home Inspections, LLC
Serving Columbus and Central Ohio
Home Energy Tune-uP
Certified Specialist - Infrared Residential Inspections Advanced
Certified Level 1 Thermographer
Certified Mold Inspector


http://www.patchhomeinspections.com
http://www.centralohiohomeinspector.com
http://www.columbusohiohomeinspector.com
http://www.thermalimagescanning.com
Reply With Quote
Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America)
  #2  
Old 9/5/08, 9:46 AM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Return air in basement?

Quote:
Originally Posted by rharrington
Hope to get all the conditions clear on this.

Furnace in unfinished basement about 12 x 30 ft 8 ft height

Finished side of the basement is about the same size.

2 return air ducts in the finished side that is separated by a solid wood door.

No vents to exchange air between sides.

Supply vents in the unfinished side are sealed.

The return air ducts are less than 6 feet log. One vent is about 10 feet away and the other is about 15 feet away. both around the corner.

There is NO passthrough at the floor joists. It has been blocked.

The furnace is 80 percent efficient with induced draft.

My thoughts are that the combustion air source has been reduced by the refinishing and the blower may create a negative pressure that would cause combustion air around the burners to be drawn into the return air ducts.

I suggested a HVAC expert evaluate the situation.

There is no evidence of spillage on the 4 year old furnace.

any suggestions?
You do home energy tune-ups and may have a micromanometer or magnahelics gauge that could test the internal house pressures to determine if there is very high (or low, depending how you look at it) negative pressure in the furnace room.

With induced draft venting, the unit fan is strong enough to overcome any regular/normal house depressurization values. Juss make sure there is a CO detector in the area of the unit in case of fan failure....and in case the unit does not shut down upon a venting fan failure.

Some info:
http://www.google.ca/search?sourceid...ts+%2b+heating

http://healthandenergy.com/ventilati...r_pressure.htm

http://www.homeenergy.org/archive/he...96/960911.html

Last edited by Brian A. MacNeish; 9/5/08 at 2:12 PM.
Reply With Quote
  #3  
Old 9/5/08, 9:59 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: Return air in basement?

Quote:
Originally Posted by rharrington
Hope to get all the conditions clear on this.

Furnace in unfinished basement about 12 x 30 ft 8 ft height

Finished side of the basement is about the same size.

2 return air ducts in the finished side that is separated by a solid wood door.

No vents to exchange air between sides.

Supply vents in the unfinished side are sealed.

The return air ducts are less than 6 feet log. One vent is about 10 feet away and the other is about 15 feet away. both around the corner.

There is NO passthrough at the floor joists. It has been blocked.

The furnace is 80 percent efficient with induced draft.

My thoughts are that the combustion air source has been reduced by the refinishing and the blower may create a negative pressure that would cause combustion air around the burners to be drawn into the return air ducts.

I suggested a HVAC expert evaluate the situation.

There is no evidence of spillage on the 4 year old furnace.

any suggestions?
You answered your own question 10 feet is the magic number



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #4  
Old 9/5/08, 10:41 AM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Return air in basement?

Quote:
Originally Posted by cbottger
You answered your own question 10 feet is the magic number
Charlie:

Why is 10 feet considered a "magic number" when negative pressure is the active ingredient in these situations? As older, loose houses are retrofitted for energy effiiciency, I feel this guideline or code requirement will have to change to reflect house pressures.
Reply With Quote
  #5  
Old 9/5/08, 2:05 PM
Rick A. Harrington's Avatar
Rick A. Harrington Rick A. Harrington is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Pickerington, Oh
Posts: 107
Rick A. Harrington is generally well trusted
Default Re: Return air in basement?

My thoughts are these guidelines or codes are set up so that in the event of equipment failure the conditions are such that it reduces the chance of a health issue in the structure. We all known things fail.

I would think that this current set up may be okay while everything is working but a failure in any number of places may put the occupants at an unnecessary risk. I did recommend mulitiple carbon monoxide detectors. I just hate to keep referring out to experts but in this case I provided the information to the client as to my thinking and that he may want to consult an expert in the field.

Thanks for the great info.



Rick A. Harrington

Patch Independent Home Inspections, LLC
Serving Columbus and Central Ohio
Home Energy Tune-uP
Certified Specialist - Infrared Residential Inspections Advanced
Certified Level 1 Thermographer
Certified Mold Inspector


http://www.patchhomeinspections.com
http://www.centralohiohomeinspector.com
http://www.columbusohiohomeinspector.com
http://www.thermalimagescanning.com
Reply With Quote
  #6  
Old 9/5/08, 2:27 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,281
Charley L. Bottger .
Default Re: Return air in basement?

Quote:
Originally Posted by Brian A. MacNeish
Charlie:

Why is 10 feet considered a "magic number" when negative pressure is the active ingredient in these situations? As older, loose houses are retrofitted for energy effiiciency, I feel this guideline or code requirement will have to change to reflect house pressures.
You are probably right codes change periodically as to different needs but until they do all we can do as professionals is just make recommendations.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #7  
Old 9/5/08, 3:48 PM
Mark Thorman Mark Thorman is offline
New User
 
Join Date: Mar 2008
Posts: 78
Mark Thorman is generally well trusted
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Return air in basement?

If the furnace is in the unfinished side and the returns and supplys are in the finished side with a relatively tight separation between the two, the only concern would conbustion air. Whats the btu of the furnace and is there any vents to the exterior at the unfinished side of the basement.

www.mauihomeinspections.com
Reply With Quote
  #8  
Old 9/5/08, 11:37 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Return air in basement?

Quote:
Originally Posted by Mark Thorman
If the furnace is in the unfinished side and the returns and supplys are in the finished side with a relatively tight separation between the two, the only concern would conbustion air. Whats the btu of the furnace and is there any vents to the exterior at the unfinished side of the basement.

www.mauihomeinspections.com
An interesting thing happens when we install higher efficiency heating appliances........they need need much less air to operate efficiently and safely.

(1) since their is better burner design leading to better mixing of fuel and oxygen in the air, less excess air is required for complete combustion

(2) since a fan driven induced draft unit has a forced draft, there is no need for draft hoods/barometric dampers to keep pressures in the fire chamber at/near disgn values....therefore, this secondary air supply is not needed.

Thus usually there is enough leakage from the exterior or from other areas of the house. The house will bleed air into the family room through all the gaps created by wiring, plumbing and heating penetrations. Check the pressures in the room near the heating applaince to ensure they do not get severely negative.

I have seen passive supply air ducts into the mechanical room actually suck air out of the room (tested with smoke) when the exterior hood is in the lee of the wind....most of this side of house goes negative in strong wind gusts!!! The theory is to have supply air vents high and low to suply air but when they are both in negative pressures from wind conditions, they are both sucking air from the room.

As mentioned before, the WETT Assoc in Canada has a homeowner video of a fire in a zero clearance , high efficiency, airtight wood fireplace during which in strong wind gusts, smoke emitted from the combustion air wall supply hood in the lee of the wind while the fire burnt downwards through the firewood and was being supplied with combustion air from the chimney......a fire burning downwards.......Chris Angel must be around!!!! The single wall, uninsulated metal combustion air supply pipe was installed horizontally on wood drywall ceiling strapping/furring under the floor joists of the floor supporting the fireplace.

I find some of the standards committees setting the guidelines/codes do not have enough building science and field experience or field contact to properly move ahead to make rules that are up-to-date with research and new equipment. Up here it's a bit of a honour/feather-in-the-cap to sit on these commiittees but they don't necessarily bring enough to the table!!
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Options in selecting materials for basement construction wdevries Canadian Inspectors 2 8/4/08 2:30 PM
Site grading and drainage wdevries Canadian Inspectors 4 8/2/08 2:27 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
cold air return in basement? bmargiotti HVAC 9 1/24/06 6:51 PM


All times are GMT -4. The time now is 8:13 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics