Question Return air near furnace

I have been finding more return air vents close to the furnace and sometimes right above the filter area. I know this is a safety issue on older furnaces. Does it still apply to direct vent furnaces?
Attached Thumbnails
return-air-near-furnace-hpim1278.jpg  
Reply With Quote
  #2  
Old 3/25/08, 12:36 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Return air near furnace

Quote:
Originally Posted by kmalone
I have been finding more return air vents close to the furnace and sometimes right above the filter area. I know this is a safety issue on older furnaces. Does it still apply to direct vent furnaces?
Not allowed in this state period?????



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 3/25/08, 5:33 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Return air near furnace

Quote:
Originally Posted by kmalone
I have been finding more return air vents close to the furnace and sometimes right above the filter area. I know this is a safety issue on older furnaces. Does it still apply to direct vent furnaces?
Shouldn't be a problem with sealed combustion direct vent system but still not the best of practices. Check with local AHJ to see if they have policy/rules on this item.
Reply With Quote
  #4  
Old 3/25/08, 7:33 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Return air near furnace

First consideration is the location of the unit, itself. Return air cannot come from a closet, bathroom, kitchen, garage or mechanical room.

If the sole source of return air is in the same room as unit, the return source must be located more than 10 feet from the unit.

If this unit were not in a "room" but was in an open and unfinished basement, I think it would be okay. If it were not, I would write it up.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #5  
Old 3/25/08, 9:05 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Return air near furnace

Quote:
Originally Posted by jbushart
First consideration is the location of the unit, itself. Return air cannot come from a closet, bathroom, kitchen, garage or mechanical room.

If the sole source of return air is in the same room as unit, the return source must be located more than 10 feet from the unit.

If this unit were not in a "room" but was in an open and unfinished basement, I think it would be okay. If it were not, I would write it up.
In the Pic I see a supply air grill top left side, in the bottom right side I see a water heater. Does not matter if it is the sole source or not air is just like water takes the path of least resistance. That return air grill on the plenum is going to be creating substantial velocity noise will short circuit air flow from the supply grill. Create a back draft on the hot water heater. I see nothing Okay about that install would write it up every time.

Return air grills on the return air plenum's solves no problems
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 3/25/08, 4:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Return air near furnace

Quote:
Originally Posted by cbottger
Not allowed in this state period?????
The same goes for CA.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 3/25/08, 5:00 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Return air near furnace

I RED-FLAG all return vents in the same room as the furnace.

Direct-vent or not.....
Reply With Quote
  #8  
Old 3/25/08, 8:53 PM
Kenneth R. Malone Kenneth R. Malone is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Sycamore, IL
Posts: 70
Default Re: Return air near furnace

I have been writing them all up. I am just wondering if the HVAC guys don't think it matters anymore when using a direct vent furnace. Thanks, Ken
Reply With Quote
  #9  
Old 3/26/08, 6:11 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Return air near furnace

Quote:
Originally Posted by kmalone
I have been writing them all up. I am just wondering if the HVAC guys don't think it matters anymore when using a direct vent furnace. Thanks, Ken
cbottger saw a natural draft water heater in the same room or area.....then the return will/may cause a problem, so these HVAC guys have to be careful, re-train on managing house pressures, etc.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Return in Furnace closet dmacy Inspecting HVAC Systems 2 2/24/08 3:30 PM
furnace return air duct vwood Inspecting HVAC Systems 5 6/19/07 1:18 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer Inspecting HVAC Systems 19 4/9/07 8:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM