This may be a question for another message board but I thought I'd ask.
We installed a replacement furnace in my house and can only get 7" of water column on the manifold side of the valve. The install manual says it needs between 10" and 12". Local rep says the valve needs to be replaced...we replace it with two new ones...still only 7" of water column with none of the valves adjustable (tighten screw or loosen and no difference in pressure). We put a newer model of the gas valve on, per the local rep, with no change in performance. Local rep then says he called the factory and they say run it with the nice blue flame we have and forget it...I am wondering. What say you? ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#2
|
||||
|
||||
|
Larry,
Did anyone check the BTU input/output of the present set up to confirm that you are getting the rated input/output? I think I would like to know that if it were mine. It is quite easy to do. |
|
#3
|
|||
|
|||
|
Quote:
How is it done? ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#4
|
||||
|
||||
|
Basically you observe the gas consumption over a period of time(10 -30 minutes should be enough)
The burner has to be running full out and all other gas appliances turned off or at least not operating. Then you have to know the BTU per cu ft. of your local gas supply and calulate from there.(should be appx 1000 BTU.cu.ft.) example: 100,000 BTU/Hr rated input. Burner on full for 15 minutes. Used 25 cu ft. 25/ 1/4 hr x 1000= 100,000 BTU/Hr Last edited by mlarson; 10/23/07 at 7:43 PM.. |
|
#5
|
|||
|
|||
|
Thanks, Michael, I just got back in from taking a break to stack wood. Neighbor thinks winter is coming...
Any other input as to why we can't get the pressure needed through the valve? ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#6
|
||||
|
||||
|
What's your pressure at the meter?
It should be stated on the meter. |
|
#7
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#8
|
||||
|
||||
|
Quote:
Forget what I said about measuring input. You need a way to measure the actual gas used to determine if it is delivering the rated input. BTW - Propane is 2488 BTU per Cu ft. The nice blue flame is a good sign but it doesn't tell you if the correct burner and orifice are in place. |
|
#9
|
|||
|
|||
|
I switched out the orifices and put in the other parts of the conversion kit, so I know that was done.
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#10
|
||||
|
||||
|
Larry it sounds to me as if you are having line drop. What is the size of your supply line and what is the distance from the tank to the furnace.
I ran a one inch line from my tank to the furnace approximately 75 feet and had to adjust the regulator at the tank in order to get 11 inches at the gas valve on the furnace. you can still have a blue flame with less inches of water column but the BTU output will drop and the furnace will run longer to do its job. Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#11
|
|||
|
|||
|
Quote:
I think we may have it figured out. It appears that the regulator on the tank is bad and fluctuating. We were able to get 11", by adjusting that, but not continually. It is running at 9 1/2" of water column now. Tech from the LP gas company is coming out on Monday next to "upgrade the equipment". Thanks for the help everyone. ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#12
|
||||
|
||||
|
Way to go Larry. Persistance pays.
|
|
#13
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#14
|
||||
|
||||
|
Quote:
Glad you got it fixed winter is on the way stay warm. Or I should say repaired fix is what we do to cats and dogs. Freedom Express Inspections LLC CMOR Thermography Certified Level 11 #2097 freedomexpressinspections.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F Professional Home Inspector State License # 130 Reporting system by Home Inspector Pro Serving the State of Okla. |
|
#15
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Good find Larry. Now have a co/combustion test done on the flue gases. A few years back found bad co readings when the main blower came on. Someone at the factory left a screw out. Would have never known unless I had tested.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Rheem - Electric Furnace Age | charper | HVAC | 1 | 8/31/07 2:55 PM |
| Need Rheem age for furnace | rray | HVAC | 2 | 8/23/07 12:17 AM |
| Age of Rheem Furnace | jhanna1 | HVAC | 3 | 2/7/07 6:18 PM |
| Rheem Furnace | bhartley | HVAC | 1 | 9/19/06 12:20 AM |
| Need age on Rheem furnace | rslocum | HVAC | 13 | 4/24/06 11:21 AM |