This may be a question for another message board but I thought I'd ask.

We installed a replacement furnace in my house and can only get 7" of water column on the manifold side of the valve. The install manual says it needs between 10" and 12".

Local rep says the valve needs to be replaced...we replace it with two new ones...still only 7" of water column with none of the valves adjustable (tighten screw or loosen and no difference in pressure).

We put a newer model of the gas valve on, per the local rep, with no change in performance.

Local rep then says he called the factory and they say run it with the nice blue flame we have and forget it...I am wondering.

What say you?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #2  
Old 10/23/07, 7:11 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Larry,

Did anyone check the BTU input/output of the present set up to confirm that you are getting the rated input/output?

I think I would like to know that if it were mine. It is quite easy to do.
Reply With Quote
  #3  
Old 10/23/07, 7:15 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Quote:
Originally Posted by mlarson
Larry,

Did anyone check the BTU input/output of the present set up to confirm that you are getting the rated input/output?

I think I would like to know that if it were mine. It is quite easy to do.
I don't think my guy did that but I'll ask tomorrow.

How is it done?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 10/23/07, 7:22 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Basically you observe the gas consumption over a period of time(10 -30 minutes should be enough)
The burner has to be running full out and all other gas appliances turned off or at least not operating.

Then you have to know the BTU per cu ft. of your local gas supply and calulate from there.(should be appx 1000 BTU.cu.ft.)

example:
100,000 BTU/Hr rated input.
Burner on full for 15 minutes.
Used 25 cu ft.
25/ 1/4 hr x 1000= 100,000 BTU/Hr

Last edited by mlarson; 10/23/07 at 7:43 PM..
Reply With Quote
  #5  
Old 10/23/07, 8:03 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Thanks, Michael, I just got back in from taking a break to stack wood. Neighbor thinks winter is coming...

Any other input as to why we can't get the pressure needed through the valve?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #6  
Old 10/23/07, 8:07 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Rheem LP gas furnace model RGPN-12EARJR

What's your pressure at the meter?

It should be stated on the meter.
Reply With Quote
  #7  
Old 10/23/07, 8:09 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Quote:
Originally Posted by mlarson
What's your pressure at the meter?

It should be stated on the meter.
It's a LP tank and on the tank side of the valve we get 12".



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 10/23/07, 8:23 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Quote:
Originally Posted by lkage
It's a LP tank and on the tank side of the valve we get 12".
Oops!

Forget what I said about measuring input.

You need a way to measure the actual gas used to determine if it is delivering the rated input.

BTW - Propane is 2488 BTU per Cu ft.

The nice blue flame is a good sign but it doesn't tell you if the correct burner and orifice are in place.
Reply With Quote
  #9  
Old 10/23/07, 8:33 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Rheem LP gas furnace model RGPN-12EARJR

I switched out the orifices and put in the other parts of the conversion kit, so I know that was done.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #10  
Old 10/23/07, 9:35 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Larry it sounds to me as if you are having line drop. What is the size of your supply line and what is the distance from the tank to the furnace.
I ran a one inch line from my tank to the furnace approximately 75 feet and had to adjust the regulator at the tank in order to get 11 inches at the gas valve on the furnace. you can still have a blue flame with less inches of water column but the BTU output will drop and the furnace will run longer to do its job.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #11  
Old 10/24/07, 4:13 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Quote:
Originally Posted by cbottger
Larry it sounds to me as if you are having line drop. What is the size of your supply line and what is the distance from the tank to the furnace.
I ran a one inch line from my tank to the furnace approximately 75 feet and had to adjust the regulator at the tank in order to get 11 inches at the gas valve on the furnace. you can still have a blue flame with less inches of water column but the BTU output will drop and the furnace will run longer to do its job.
Thanks Charley.

I think we may have it figured out. It appears that the regulator on the tank is bad and fluctuating. We were able to get 11", by adjusting that, but not continually. It is running at 9 1/2" of water column now.

Tech from the LP gas company is coming out on Monday next to "upgrade the equipment".

Thanks for the help everyone.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #12  
Old 10/24/07, 5:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Way to go Larry. Persistance pays.
Reply With Quote
  #13  
Old 10/24/07, 5:25 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Quote:
Originally Posted by mlarson
Way to go Larry. Persistance pays.
Thanks, Michael. This certainly has been a learning experience for me and I really appreciate my 75 year old friend that has a lifetime of HVAC experience that seems to get misplaced here and there.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #14  
Old 10/24/07, 6:26 PM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Quote:
Tech from the LP gas company is coming out on Monday next to "upgrade the equipment".
Had to change mine two years ago they don't as some think last for ever.

Glad you got it fixed winter is on the way stay warm. Or I should say repaired fix is what we do to cats and dogs.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #15  
Old 10/26/07, 8:28 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 212
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Rheem LP gas furnace model RGPN-12EARJR

Good find Larry. Now have a co/combustion test done on the flue gases. A few years back found bad co readings when the main blower came on. Someone at the factory left a screw out. Would have never known unless I had tested.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rheem - Electric Furnace Age charper HVAC 1 8/31/07 2:55 PM
Need Rheem age for furnace rray HVAC 2 8/23/07 12:17 AM
Age of Rheem Furnace jhanna1 HVAC 3 2/7/07 6:18 PM
Rheem Furnace bhartley HVAC 1 9/19/06 12:20 AM
Need age on Rheem furnace rslocum HVAC 13 4/24/06 11:21 AM


All times are GMT -4. The time now is 7:58 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts