Question Rule of Thumb A/C sizing question from Practice Exam

I have a question regarding a question on the practice test. On page 11 there is a question that seems to conflict with the information I was looking up. The correct answer is 700 sq ft but some of the research I did supported 500 sq ft per ton. What is the correct answer? Wisconsin requires passing the National Exam and I’m doing everything I can to get ready for it within 2 weeks.

Greg Liebig
NACHI06051095

A rule of thumb for air conditioning is a ton of air conditioning is needed for:
  • 700 square ft
  • 500 square ft
  • A one story house
  • A hot day

References:
http://www.healthgoods.com/education/healthy_home_information/Space_Heating_and_Cooling/sizing_heat_and_ac.htm

The contractor asks you how many square feet of living space there are in your house. He (or she) then tells you what size unit you need. This is called "sizing by square footage" and is the most commonly used inaccurate method of sizing. A typical value used for air conditioners is one ton (12,000 Btu/hour) per 500 square feet (46 m2). This does not take into account differences among houses in design, construction, or energy efficiency.

http://www.uppco.com/business/eba_9.asp

Table 1: Capacity rules of thumb for room air conditioners

Rules of thumb for estimating air conditioner size vary by manufacturer. This example, from Carrier, includes the following suggestions for adjustments: If a room is heavily shaded, reduce capacity by 10 percent; if the room is very sunny, increase by 10 percent; and if using the unit in a kitchen, increase capacity by 4,000 Btu per hour.

Room area Capacity
(ft²) (Btu/h)
100 to 150 5,000
150 to 250 6,000
250 to 300 7,000
300 to 350 8,000
350 to 400 9,000
400 to 450 10,000
450 to 550 12,000
550 to 700 14,000
700 to 1,000 18,000

Source: Platts
Reply With Quote
  #2  
Old 5/23/06, 12:17 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 476
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Rule of Thumb A/C sizing question from Practice Exam

That's the rule-of-thumb we used for the Texas TREC exam. Of course, Texas is a bit warmer than some climates.
Reply With Quote
  #3  
Old 5/23/06, 10:37 PM
jwilliams7 jwilliams7 is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Springdale, AR
Posts: 36
Default Re: Rule of Thumb A/C sizing question from Practice Exam

I passed the National Exam about a month and a half ago, I used 500 sq feet/ton.
Reply With Quote
  #4  
Old 5/23/06, 10:48 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 212
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Rule of Thumb A/C sizing question from Practice Exam

Rules of thumb are dumb.

Using Air Conditioning Contractors of America (ACCA) Manual J heat loss/gain calculation method is more precise with less chance of oversizing equipment and reducing comfort.
Reply With Quote
  #5  
Old 5/24/06, 12:14 AM
Joseph T. Burkeson, CMI's Avatar
Joseph T. Burkeson, CMI Joseph T. Burkeson, CMI is online now
InterNACHI Member
 
Join Date: May 2003
Location: Riverview, FL
Posts: 8,596
Default Re: Rule of Thumb A/C sizing question from Practice Exam

Quote:
Originally Posted by Gary Reecher
Rules of thumb are dumb.

Using Air Conditioning Contractors of America (ACCA) Manual J heat loss/gain calculation method is more precise with less chance of oversizing equipment and reducing comfort.
You Betcha!

IRC - M1401.3 Sizing.
Heating and cooling equipment shall be sized based on building loads calculated in accordance with ACCA Manual J or other approved heating and cooling calculation methodologies.



"I know of no more encouraging fact than the
unquestioned ability of a man to elevate his
life by conscious endeavor." ~ Henry David Thoreau


Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector
Member, American Society of Home Inspectors (ASHI)
Vice President - Suncoast ASHI

Square-One Inspection "Assurance begins here"

Reply With Quote
  #6  
Old 5/24/06, 8:10 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Rule of Thumb A/C sizing question from Practice Exam

Quote:
Originally Posted by Gary Reecher
Rules of thumb are dumb.

Using Air Conditioning Contractors of America (ACCA) Manual J heat loss/gain calculation method is more precise with less chance of oversizing equipment and reducing comfort.
Doesn't negate the fact that it's on the NHIE...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #7  
Old 5/24/06, 8:33 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 476
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Rule of Thumb A/C sizing question from Practice Exam

Rules of thumb may be dumb but if I inspect a house that's a ton undersized based on that rule and we are here in hot Texas then I will call for a HVAC guy to be consulted so he can do those calcs and tell the buyer if the AC is properly sized. I won't say it is not properly sized but I will say that it should be looked into.
Reply With Quote
  #8  
Old 5/24/06, 10:56 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Rule of Thumb A/C sizing question from Practice Exam

What Ronald said!



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #9  
Old 5/25/06, 2:36 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 483
Default Re: Rule of Thumb A/C sizing question from Practice Exam

I also agree that one should defer if they cannot give the client the best decsion. That still doesn't take away the facts of the question on the exam.
Reply With Quote
  #10  
Old 5/25/06, 2:38 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 483
Default Re: Rule of Thumb A/C sizing question from Practice Exam

Thanks Mike! That's my point exactly...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Sizing & Neutral Question? thejnicki Electrical 18 2/15/07 8:00 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 9:42 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts