#1
|
||||
|
||||
|
I never see them in Colorado, so I'm not very familiar with them. With gas-fired combustion appliances, there's the risk of explosion and fire from pre-ignition. What are the danger associated with oil-fired appliances like furnaces, boilers, and water heaters? Do they make oil-fired water heaters?
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
| Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Excellent questions Kenton - I have to inspect my first one in the AM here in CO. Not sure what to look for other than have it insepcted by a qualified HVAC tech. Any help guys?
|
|
#3
|
|||
|
|||
|
Please Note:
An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
http://oee.nrcan.gc.ca/equipment/heating/13082 http://www.granbyindustries.com/en/p.../3/paradigm/94 Carson and Dunlop's report appendix has a bit on oil-fired heating equipment. And, yes, there are oil-fired hot water heaters. |
|
#4
|
||||
|
||||
|
Kenton
Less danger the gas fired IMO Problems Oil leaks Things not to do do not reset more the twice if flame is not present Check for excessive soot. Keep in mind it will not be clean as a gas fired unit Check flame Check flue pipe check limits / fan control Check damper Look for condensation if it is a high efficiency type going into old brick chimney And one word do not stick your tongue on the electrodes lol Wayne Wilson East TN Home Inspections LLC Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-1490 http://site.myhomeinspection.net |
|
#5
|
||||
|
||||
|
I didn't even know anyone could buy heating oil here, Greg.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#6
|
||||
|
||||
|
Quote:
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#7
|
||||
|
||||
|
Kenton if you reset ( furnace didn't fire) It pumps oil into the chamber . two many times floods the fire box and you will have a uncontrollable fire.
Wayne Wilson East TN Home Inspections LLC Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-1490 http://site.myhomeinspection.net |
|
#8
|
||||
|
||||
|
For fear of being shot down by the three stooges. The red button is a reset and should never be pressed more than twice. You will not need to touch this button in your inspection. You should also not view the flame unless you know what to look for.
Inspection of an oil-fired system is not anything like natural gas. The lines are also different colors and must be installed according to proper guidelines. The guidelines are the CSA B 149-09 I would recommend you find the equivalent in USA. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 Last edited by kwood; 12/22/11 at 10:33 PM.. |
|
#9
|
||||
|
||||
|
Just a different name for diesel different grades
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#10
|
||||
|
||||
|
Kenton - I was surprised too - but Wayne called me and gave me some hints on what to look for - will try my best and will let you know how it went. I HATE first time stuff.
|
|
#11
|
||||
|
||||
|
Trying to remember my CD course material, one thing I do remember is the reset button info that others have already informed you of. I will drag out the binder tomorrow at some point and see what, if anything I can add for you Kenton.
when you have eliminated the impossible, whatever remains, however improbable, must be the truth. Sir Arthur Conan Doyle. If you have ten thousand regulations you destroy all respect for the law. Winston Churchill |
|
#12
|
||||
|
||||
|
I have taken
Practical Guide to Safe Oil Installation Codes for Furnaces and Boilers Installation of Oil Burning Equipment B149 Codes update Safe Inspection of Oil tanks Installed Oil tanks and furnaces Monitors and wood stoves Wett site basic Natural Gas and Propane Installation code Carson Dunlop heating one and two (Teacher) HRAI Installation and designer Advanced HVAC And countless CE hours on HVAC THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#13
|
|||
|
|||
|
Please Note:
An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
FINICKY F'D UP BOARD HERE!
By clicking on "go advanced", just lost a post that took me 15 minutes on a long list of "things to check" POS!!! |
| Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
Plus i have stayed in a Holiday Inn lolol Wayne Wilson East TN Home Inspections LLC Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-1490 http://site.myhomeinspection.net |
|
#15
|
||||
|
||||
|
DANGER: Don't listen to Linus and pee on the transformer ignition to test it (10,000 volts)!
There are about 46 parts in an oil burner gun, any one could cause failure. The motor should run quietly and smoothly. The squirrel cage blower assembly should not be rotted out. Must be cleaned periodically. The oil pump should not leak. Pop the transformer and examine the electrodes for arcing. The nozzle should be clean and not drip oil. The nozzle should be changed yearly and must be the appropriate size. It must be the proper orifice size, spray angle and could be hollow or solid clone design. The igniter probes discharge against the nozzle and must be properly adjusted (special tools required). The electrode gap should be no more than 1/8 of an inch apart and no more than one half of an inch above and forward of the nozzle. Porcelain insulators must be kept clean or they will short out. The spark should jump across at least a 1 inch gap with the blower turned off. Adjustment per equipment manufacturer. The throat of the gun should be intact (not burned out). There should be no discoloration or build up. The nozzle of the gun should not extend past the refractory insulation inside the furnace. The cadmium cell above the burner must be clean and able to see the fire adequately. The tank filter should be changed yearly. Barometric damper operation should be free moving. Check for delayed ignition at start up. Should fire right off and not pop or blowback during ignition. Pulsation noted during operation is caused by positive pressure in the combustion chamber indicating there's not enough draft. The draft should be .02 inches of water gate. Positive pressure may be caused by having the air shutter open too much, the chimney is too small or partially blocked or not high enough. If anyone made any changes to where the tank is located, the type of pump may not be compatible if it is a single stage operating in vacuums at or above 15 inches of mercury. This causes the oil to foam before it reaches the nozzle to be atomized. A faulty nozzle has an irregular flame pattern. The flame tips should be sharp (but not excessively). If you see oil on the floor of the furnace room it is a serious condition. An air leak in the oil suction line causes the nozzle to drip. It can be from loose connections or fittings or from a bad pump seal. Unusual sounds during operation indicate worn and broken parts which should be immediately replaced as failure may cause a significant breakdown which could be avoided. Noises come from loose fans, loose shutter, worn pumps, dirty strainer, air in the oil, motor coupling is worn, motor and pump are not properly aligned, relay contacts not seating, restricted oil lines, Any indoor tank should be at least 7 feet away from the furnace. The oil storage tank should be tilted away from the outlet pipe to collect moisture and crap. Any black soot observed in the furnace room is an indication of blowback and improper ignition current or in the past. I taught air conditioning installation to the oil burner technicians at the American Fuel Institute. This is what they taught me! "Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein Clarksville - Nashville Home Inspector Lic#40 http://www.midtninspections.com ITC Level III Thermographer Cert#1958 Building Science Thermographer Cert#33784 http://www.thermalimagingscan.com HVAC Certification EPA Cert#2046620 Link to my Website at: http://www.midtninspections.com/link-submission Last edited by dandersen; 12/23/11 at 9:53 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Vacation Resort Inspectors in Coeur d’Alene, ID 83815 | rspriggs | Ancillary Inspection Services & Additional Topics | 0 | 1/9/09 3:40 AM |
| Property Management Inspectors in Coeur d’Alene, ID 83815 | rspriggs | Ancillary Inspection Services & Additional Topics | 0 | 1/9/09 3:21 AM |
| BC is acting on the new bill | jkoong | Canadian Inspectors | 21 | 2/19/08 7:38 AM |
| Another reason to recommend CO testers | rnewman1 | Interior Inspections | 2 | 10/12/06 7:47 AM |