Default Secondary condensate ports

Around here the new homes have several different methods of piping the secondary condensate drains.

The most noticeable difference is this:

Cheap house: secondary port is left plugged up with the factory plug.
(Pan and switch present also)

Mid to expensive house: secondary port is piped to the exterior over a window or to a pan with a float switch.

I always write up the plugged secondary port as an issue and state that the manuf. recommends it be used.

I looked yesterday in the installers manual for a new Rheem attic unit and found nothing about the condensate drains. It even had a checklist for the installer to use for determining proper installation and nothing there about the condensate lines. The portion of the unit that has the ports had a label that indicated ADP as the manuf. but no manual was there for it.


I have seen units with a clogged main with water ooozing out of the metal joints around the unit. Also remember the humidity that gets blown back into the house when the unit has excess water for prolonged periods.

Is there any code for this except for the catch all that requires the installer to follow the manuf's specs? It's hard to use that argument when the manuf's document is not complete or unavailable on site.
Reply With Quote
  #2  
Old 9/13/06, 2:53 PM
Raymond N. Newman Raymond N. Newman is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Avondale, AZ
Posts: 128
Send a message via Skype™ to rnewman1
Default Re: Secondary condensate ports

Why always code? How about defending it with common sense? We are making recommendations to serve the best interest of our clients.
Reply With Quote
  #3  
Old 9/13/06, 3:17 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Secondary condensate ports

I agree but tell that to the house flippers, builders and agents and they still refuse to fix it.

Some agents tell their client "it meets code so you can not ask the seller to change this"

You can take the time to explain issues like these to some people and they only act like they are listening. It could be that it is over their heads and they are embarrassed to ask questions. Builders are starting to refuse repairs around here because they will just sell the house to the next one in line. One large builder told me that only 10 percent of buyers get an inspection!!!!

Its time for the state to require private home inspections and let the govt. employee inspectors just do the zoning, tree population and regulate the point of occupancy.

Last edited by bking; 9/13/06 at 3:27 PM..
Reply With Quote
  #4  
Old 9/13/06, 3:25 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Secondary condensate ports

Also, on many of the newer units, the two ports are level with each other.
There is a baffle hidden inside the unit that determines which one is the primary and secondary. Without the documentation you can not tell if the primary drain is really the primary.

If it is backwards and the other is plugged you get excess humidity back into the house.

We have many builders around here, national and local so we see many different types of units, no way to keep up with all of the porting specifics.
Reply With Quote
  #5  
Old 9/14/06, 1:07 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Secondary condensate ports

Quote:
Originally Posted by bking
Some agents tell their client "it meets code so you can not ask the seller to change this"
When I hear a Realtor say that, I always tell my Clients that they can ask for anything they want to ask for and, if the Realtor is telling them that they can't, perhaps the Realtor is not working in their best interest. That gets my Client's attention.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 9/14/06, 1:19 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Secondary condensate ports

Is this what you're looking for, Bruce?

M1411.3.1 Auxiliary and secondary drain systems. In addition to the requirements of Section M1411.3, a secondary drain or auxiliary drain pan shall be required for each cooling or evaporator coil where damage to any building components will occur as a result of overflow from the equipment drain pan or stoppage in the condensate drain piping.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 9/14/06, 9:45 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Secondary condensate ports

You are required to have a secondary drain, or float switch. You often see both, which is best. You are not required by code to have a secondary drain if a float switch is present. (I don't have time to read manufacturer's installation instructions for every unit.)

IRC M1411.3.1.3 "An auxiliary drain pan without a separate drain line shall be installed under the coils on which condensate will occur. This pan shall be equipped with a water level detection device conforming to UL 508 that will shut off the equipment served prior to overflow of the pan."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 9/14/06, 9:54 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Secondary condensate ports

Since the code leaves the installer a gray area....

Put another way for the sake of discussion:

When you do have a pan with a switch present:
How do you get the condensate to the pan?
I think the secondary port is required to be piped to the pan.
Many installers leave it plugged and think they have met code.

The code is written badly and actually is missing the detail for the secondary port/piping.
Reply With Quote
  #9  
Old 9/14/06, 10:02 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Secondary condensate ports

If I see a pan with a float switch present, its acceptable to me. Even if the 2nd port is plugged at the evaporator coil. The water will find a way out and into the pan. You may be correct, but I don't focus on whether the port is plugged at the coil.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 9/14/06, 10:08 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Secondary condensate ports

With the secondary plugged, the water level will rise and only seep out of metal joints that are fairly well sealed. The excess water gets blown around inside the airhandler and onto the coil where the humidity gets blown into the duct (mold) and into the house (condensation around windows/mold)

When a major problem is found later by a subcontractor they change their tune and say "didn't you have this inspected?"

I suggest everyone report plugged secondaries, the port is there for a reason.
Reply With Quote
  #11  
Old 9/14/06, 10:10 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Secondary condensate ports

I may change my tune. Let's see what others say about it.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 9/14/06, 10:25 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Secondary condensate ports

There are other similar threads but everyone kept drifting towards code or pan/pipe vs pan/switch.

***** This one is about getting the water out of the cabinet and off the coil when the primary is clogged.

What you do with the water when it is out of the cabinet is where code and personal preference come into play.
Reply With Quote
  #13  
Old 9/14/06, 11:31 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Secondary condensate ports

Most of the furnaces I see are in the attics here, but about half of them have no cooling condenser. However, when there is a cooling system present, this is what I like to see (notwithstanding the lack of a trap on the main drain). But even when I find this, I'll go as far as recommending that my Clients have a float switch installed. I've seen the results of water damage to the ceilings when everything gets clogged. And the wasps love to create their mud homes in the exterior openings of these drain lines. Also recommend regular homeowner and monitoring to ensure that those wasps don't block the drain pipes during cooling season.
Attached Thumbnails
secondary-condensate-ports-faudrain.jpg  



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 9/14/06, 11:45 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Secondary condensate ports

RR, regarding maintenance, pour bleach down the opening on the primary once a year to help keep the drain open.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 9/14/06, 11:55 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Secondary condensate ports

Quote:
Originally Posted by jfunderburk
RR, regarding maintenance, pour bleach down the opening on the primary once a year to help keep the drain open.
I have heard of that, but with the size of these mud dauber nests, all I would have is a drain pipe full of bleach. And since chlorine is naturally a gas, it dissipates into the atmosphere quite quickly. Perhaps more often might do the trick, but I've found a power nozzle on the hose works quite effectively.

The cliff swallows like to start their homes around the drain pipes, as well, eventually having a whole colony of nests with the drain pipe nowhere to be seen.

Note that in California, it is illegal to disturb nesting cliff swallows, so if you see active nesting, wait until the little babies have flown the nest before destroying the nests. I did make such a recommendation to a Client up in Poway. He had a few billion active nests. He thought I was kidding. Unfortunately, his neighbor was an active bird watcher and turned him in. Granted, it's only a $50 misdemeanor fine, but I can do a lot of marketing with $50. Or make Ms Margarita and Dr Cuervo quite happy.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year

Last edited by rray; 9/14/06 at 12:00 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
1 condensate line...... Scott Schultz HVAC 2 11/4/07 7:18 AM
Condensate piping dmacy HVAC 15 3/13/07 1:17 AM
TPRV line and condensate line marriage ccarrington Plumbing 3 4/29/06 8:59 AM


All times are GMT -4. The time now is 9:12 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts